Dear all
Is there a difference between surge arrestor for line and surge arrestor for transformer
Regards
Pathfinder Tags: Surge Arrestor
Re: surge arrestor
02/25/2013 2:15 PM
Good Answers: 444
Re: surge arrestor
02/25/2013 4:15 PM
There may be, it depends upon where in the overall system the arrestor is going to be installed, so simply substituting an identical looking arrestor can be a formula for disaster. Two of the key parameters are the amount of energy available and its duration.
A lightning strike in the middle of a radial transmission line might be less severe because the major source of energy is that contributed by the lightning bolt, which is of very short duration (relatively speaking). On the other hand a strike on a transformer that is located in a switchyard with multiple transmission lines, or worse, fed by multiple generators, has many times more available energy and of longer duration, meaning that the amount of power that the arrestor has to dissipate is much greater.
Grounding in the latter case is also much better (of lower impedance) so that the current has a shorter path and is much higher than it would be when faced with the combined impedance of the tower, its footings, and the local earth loop return path in the case of an isolated line line strike.
See the flowchart on page 8 of this ABB product brochure for info on how to make the proper selection
Re: surge arrestor
02/25/2013 4:33 PM
Have you considered taking some courses in electricity?
Re: surge arrestor
02/25/2013 4:57 PM
Yes and no.
No, there is no difference in the type of function these devices perform. Both will protect downstream components from a surge. Often they will sacrifice themselves to protect things downstream.
Yes, there is a significant difference in the amount of power each will allow to flow downstream, the amount of energy they will successfully stop without any damage and the amount of energy they will stop with damage.
Re: Surge Arrestors
02/26/2013 6:19 AM
This info may help you
Surge Arrestors
Re: Surge Arrestors
02/27/2013 11:05 AM
All do the same solution. How it is done varies significantly.
An ABB example of how all surge protection works:
http://www05.abb.com/global/scot/scot245.nsf/veritydisplay/abe7dffae47234f7c125736e0021458c/$File/pexlink.wmv