MRI, CT Scan Acceptable Frequency Tolerance

02/25/2013 11:46 PM

Dose anyone know about the frequency tolerance that MRI, CT scan can acceptable ?

Now i under the offering the dynamic ups for the hospital.

and my dymanic ups have 2 frequency tolerance as +,- 1% and +,- 5%

They(hospital) wondering the dynamic ups can not match the power supply of MRI, CT Scan

ps. i can not ask the hospital about this question because they have not buy a MRI, CT scan yet. it's just their plan in the future.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Power-User

Join Date: Nov 2012
Posts: 183
Good Answers: 6
#1

Re: Dose anyone know about the frequency tolerance that MRI, CT scan can acceptable

02/26/2013 4:23 AM

Ask teh manufacturer of the MRI, CT scan

Gajanan Phadte

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Nov 2012
Posts: 17
#5
In reply to #1

Re: Dose anyone know about the frequency tolerance that MRI, CT scan can acceptable

02/27/2013 9:56 AM

Thank you for your answer.

while i'm asking in this forum, i do contacing with the CT, MRI Scan manufacturer also but have not get the answer yet.

Register to Reply
Commentator

Join Date: Dec 2012
Posts: 65
Good Answers: 3
#2

Re: MRI, CT Scan Acceptable Frequency Tolerance

02/27/2013 1:38 AM

The MRI & CT scanners both will not care about freq tolerance. They both use internal power systems that are designed to be impervious to anything but the most egregious power fluctuations. However, that said, three are a multitude of other loads in any hospital that absolutely MUST be kept within tight tolerances. If any surgical our life signs monitoring equipment will be on this generator then it will need to be 1% tolerance. One question, why on earth would you need or want to run an MRI or CT during a power outage?! These are not considered critical functions and are not required by any standard that I know of to be supplied power from a gen set. You would need a separate gen set just to run them and it would be about the largest standard order set you could buy!

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#3

Re: MRI, CT Scan Acceptable Frequency Tolerance

02/27/2013 1:58 AM

Re:#2

Why are MRI and CT mentioned together at all?

CT is a very fancy X ray machine with a set of computers. Not particularly sensitive to anything.

The MRI on the other hand, is so sensitive to electromagnetic interference, that it is normally housed in a separate, shielded building to reduce interference from other equipment. It has excessive power filtering requirement for sure. But none against a PURE SINUSOIDAL UPS.

I think the frequency requirements are make-believe.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#4
In reply to #3

Re: MRI, CT Scan Acceptable Frequency Tolerance

02/27/2013 6:55 AM

The reason why MRI and CT are mentioned together is that they both belong to the radiology department, and, as in my hospital, can be in adjacent suites.

I agree, though, that they are not critically dependent on the frequency of the mains supply.

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

DogOfWar (1); gmphadte (1); leveles (1); phph001 (1); soolloos (1)

Previous in Forum: Surge Arrestors   Next in Forum: CPD Heaters vs Induction Heat for PWHT

Advertisement