Anonymous Poster #1

Blocked Capillary

03/06/2013 3:01 PM

How to when an A/C capillary is clocked or blocked

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2012
Location: Iowa, USA
Posts: 577
Good Answers: 50
#1

Re: Blocked Capillary

03/06/2013 4:16 PM

There's no simple answer. If it's totally blocked, then the compressor will run, and do no work, so the condenser discharge line will be at room ambient (assuming steady state, where compressor has been running a long time), and as there is no refrigeration flowing through the system the evaporator and suction line will be at room ambient. The compressor housing may be hot/warm as the motor has operating losses, and will conduct the heat from motor/compressor to the housing.

If partially blocked, it depends on how much, and how long it's been running in this state, as you could have a partially frosted evaporator closest to where the capillary is connected. This assumes that there is no large heat load or insulation losses that keeps provide more heat to the evaporator then the partially plugged capillary allows of refrigerant flow and heat removal. This is similar to a slightly undercharged capillary system, where the relative pressures on both the condensing and evaporator sides are reduced, allowing a portion of the evaporator to operate below it's normal temperature relative to the saturated pressure enthalpy curves for the refrigerant working fluid.

I hope I worded this in an intelligible fashion.

__________________
ignator -
Reply Score 1 for Good Answer
Active Contributor

Join Date: Mar 2013
Location: Nigeria
Posts: 10
#4
In reply to #1

Re: Blocked Capillary

03/09/2013 11:31 AM

Thank u sir

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Blocked Capillary

03/06/2013 4:18 PM
Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Blocked Capillary

03/06/2013 5:37 PM

This can be one of the most difficult problems to diagnose, fortunately it's rare in a/c systems.....Usually do to some condition that starves the return to the compressor and results in the oil being pumped out and basically oil logging the cap tubes....There can also be a piece of trash in the system, such as a small chunk of solder that has dripped into the system from a joint being over soldered, this is usually easier to spot as it results in the icing of the cap tube, when the system has a full charge....Also if it's a system using a mineral based lubricant, overheating or moisture contamination can result in the accumulation of a waxy buildup....I found one once that was the result of a previous repair that had blocked the cap tube completely with solder....The first question I would ask is why do you suspect a capillary tube blockage...? In any case I would try a few things such as pumping the system down, heating the cap tubes up with a hot air gun, changing the refrigerant and filter driers....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Good Answer (Score 2)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#5

Re: Blocked Capillary

03/09/2013 3:31 PM

How many capillaries are feeding the evaporator?

Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Icarus (1); ignator (1); lyn (1); SolarEagle (1); Viquo (1)

Previous in Forum: I.R.Port in Digital Energy Meter   Next in Forum: Firefighting Package Logic Control

Advertisement