355Kw Ind. MoTOR 415V, AC Creating Problem in Starting

03/07/2013 9:19 AM

I have 355KW motor 415V AC Induction Control with Soft startor Siemens, Motor Couplled with Air Compressor 30Kg Pressor When we start the motor Voltage LT Goes down 415 to 330 and HT 11000V to 9800V. The Same motor Run properly On 2MVA DG Set. 200KVAR Capacitor also Connected with Startor. HT. line Span is 9 Kilo Mtrs. with 10no. Conductor.

I Want Solution Please Suggest. P. F. Gose Down Up to .53. Pl. Pl. Suggest.

Transformer running smoothly on another Inductoin load 2000Amp Properly.

Register to Reply
Pathfinder Tags: L. MAURYA 9811678182
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: 355Kw Ind. MoTOR 415V, AC Creating Problem in Starting

03/07/2013 10:57 AM

Triplicate thread.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4
In reply to #1

Re: 355Kw Ind. MoTOR 415V, AC Creating Problem in Starting

03/08/2013 6:51 AM

He never feeds back any info (on the same 3 threads!!)

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: 355Kw Ind. MoTOR 415V, AC Creating Problem in Starting

03/07/2013 2:55 PM
Register to Reply
Member

Join Date: Apr 2009
Location: At SAARC country site.
Posts: 6
#3

Re: 355Kw Ind. MoTOR 415V, AC Creating Problem in Starting

03/07/2013 10:47 PM

Dear Mr. Luxmi Mourya,

It appears that its motor is taking very high current at the time of starting. A big starting voltage drop is observed, may be conductor size is not suitable/enough for such a long distance. what is the size of conductor/HT cable. May increase the number of parallel cables to avoid the voltage drop.

Ensure when starting the drive, compressor is in Unload condition.

Running o.k in DG means, if DG is nearby load, then no voltage drop and hence enable to take the starting load.

If DG is at distance source, then where is your capacitor installed!!, try connecting the suitable size capacitor at load end. check no other big inductive load is connected or running in the same panel at the time of starting this drive, or ensure capacitor bank for the source end panel.

Regards,

V R Rao

__________________
Keep smiling and be happy.
Register to Reply
Associate

Join Date: Dec 2007
Location: Dubai
Posts: 32
Good Answers: 1
#5
In reply to #3

Re: 355Kw Ind. MoTOR 415V, AC Creating Problem in Starting

03/08/2013 11:58 PM

Check the capacity of DG - it happens to me with York medium voltage chiller rated at 2500 tons, We double the capacity of Genset and working fine.

__________________
nlp