Active Contributor

Join Date: Jan 2013
Posts: 11

Panel Earthing check

03/11/2013 2:51 AM

Dear all,

How to check the panel earthing is okay.after connecting the earth strips/cables properly.?
Any common practice is available?
Please share....

Thanks in advance..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Panel Earthing check

03/11/2013 4:43 AM

A continuity check would be a good start.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#2

Re: Panel Earthing check

03/11/2013 11:39 AM


http://www.gcl.in/tsd/doc/26_earthing_concepts.pdf
http://www.test-meter.co.uk/17th-edition-test-equipment/earth-testers/
http://www.weschler.com/_upload/sitepdfs/techref/gettingdowntoearth.pdf
http://www.testequipmentdepot.com/newequipment/groundresistancetesters.htm

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Panel Earthing check

03/11/2013 3:09 PM

Don't forget the visual check and a torque tightness check of the connections.

Further information (and torque values) can be found in your applicable local electrical standards that the panel is being built and tested to.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Panel Earthing check

03/13/2013 12:11 PM

This poster songsaah is a DANGER TO HIMSELF AND OTHERS.

If he really is handling 400AMPS, he will kill somebody.

Register to Reply Score 1 for Off Topic
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

jack of all trades (1); lyn (1); PWSlack (1); soebfatehi (1)