Will There Be a Separate Protection for Tie Breaker

03/11/2013 10:49 AM

In a switchyard of 400KV, one and half breaker scheme,Will the tie-breaker(breaker connecting two feeders/lines)have separate protection?In my switchyard only Local breaker backup is given.

__________________
Experience is what you got by not having it when you need it
Register to Reply
Pathfinder Tags: 400kv breaker one and half
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Will There Be a Separate Protection for Tie Breaker

03/11/2013 11:18 AM

Normally in a breaker-and-a-half scheme, each line/feeder will have its own protection, and each breaker (including the tie) will have its own breaker backup / breaker failure protection. If your transmission system regulations require it, you may need redundant protection schemes for reliability.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Register to Reply

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: High Voltage Electrical Clearance   Next in Forum: Vacuum Contactor Peak Current And Motors Insulation Damages

Advertisement