Will There Be a Separate Protection for Tie Breaker
03/11/2013 10:49 AM
In a switchyard of 400KV, one and half breaker scheme,Will the tie-breaker(breaker connecting two feeders/lines)have separate protection?In my switchyard only Local breaker backup is given.
__________________
Experience is what you got by not having it when you need it
Re: Will There Be a Separate Protection for Tie Breaker
03/11/2013 11:18 AM
Normally in a breaker-and-a-half scheme, each line/feeder will have its own protection, and each breaker (including the tie) will have its own breaker backup / breaker failure protection. If your transmission system regulations require it, you may need redundant protection schemes for reliability.