Merlin Gerin (MG) Main Circuit Breaker Faulty

03/12/2013 5:09 AM

Dear All,

We have a diesel genset of Caterpillar -725 kVA model 2412. The main circiut breaker got faulty.

MG - C1251N 1250 Amp

Please advise the possible causes of faulty breaker.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Merlin Gerin (MG) main circiut breaker faulty

03/12/2013 5:24 AM
  1. The first possibility is overload.
  2. The next is water ingress.
  3. A third would be mechanical damage.
  4. Overheating from outside.
  5. Etc., etc.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Merlin Gerin (MG) main circiut breaker faulty

03/12/2013 5:55 AM

6. Ingress of foreign objects...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Merlin Gerin (MG) Main Circuit Breaker Faulty

03/12/2013 7:27 AM

7. Lack of maintenance: cleaning, lubrication, etc...

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#4

Re: Merlin Gerin (MG) Main Circuit Breaker Faulty

03/12/2013 8:58 AM

8.- Loose conections causing overheating and metal erosion.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Merlin Gerin (MG) Main Circuit Breaker Faulty

03/12/2013 10:21 AM

What's the prize for getting it right? Only, Del the cat wants to know...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#6

Re: Merlin Gerin (MG) Main Circuit Breaker Faulty

03/12/2013 10:44 AM

Main infos needed :

  • ref of the breaker
  • type of network, installation
  • type of failure : "faulty" is a bit vague.

Then I would advise to call the Schneider service center ...if Caterpillar does not answer.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#7

Re: Merlin Gerin (MG) Main Circuit Breaker Faulty

03/13/2013 12:00 PM

You did not state what type of breaker is in question.

If it is a molded-case type breaker:

Most molded-case circuit breakers are not designed to operate/trip/open more than once under fault conditions.

If this breaker has operated more than once in/under fault condition(s) it must be removed from the application and tested using a certified tester and following the breaker tester IOM instructions.

Not knowing if or how many times the breaker has been "tripped" in/under a fault condition nor the operating environment nor whether it has been properly maintained it is not reasonable nor logical to determine or assume the "Root-Cause" of failure.

All of the posts are excellent information and should be considered.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply