MCCB Trip by Emergency Stop Button

03/12/2013 7:51 AM

Hi Friends, I have 250Amp. MCCB and i want to tripp that by the emergency stop button can we do that,any one have idea pls. tell me. Regards, Hariom Tomar

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MCCB tripp by emergency stop button.

03/12/2013 7:59 AM

It depends upon what the Instruction Manual that was supplied with it says. It cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Feb 2012
Posts: 28
#2

Re: MCCB Trip by Emergency Stop Button

03/12/2013 10:02 AM

in mccb testing point are there.. if any emergency cases used by this testing switch.

Register to Reply Score 1 for Off Topic
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#3

Re: MCCB Trip by Emergency Stop Button

03/12/2013 10:39 AM

MCCB make and part number is the main needed info to give a valid answer ....

Register to Reply
Member

Join Date: Aug 2012
Location: Pune in Maharashtra
Posts: 5
#11
In reply to #3

Re: MCCB Trip by Emergency Stop Button

03/12/2013 11:47 PM

MCCB make- Scheider Model no.- CVS 250F

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #11

Re: MCCB Trip by Emergency Stop Button

06/16/2023 9:31 AM
  • So what does it say in the manual that came with it?
  • If the manual has been lost then has a search been done on the internet to find another one?
  • Has a call been put in to <...Schneider...> to ask the question?

Sheesh.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: MCCB Trip by Emergency Stop Button

03/12/2013 11:19 AM

In general though, MCCBs can be remotely tripped in two ways: Shunt Trip (ST) or Under Voltage Release (UVR). But rather than focus on whether or not you can, start with whether or not you SHOULD. Using remote tripping of a protective devie is not considered best Practice in most engineering circles, here is why.

Using the ST option is not "fail safe". If you are relying on this for emergency shut down (ESD) as a safety function, you must consider what happens if a wire is broken or disconnected. In the case of a Shunt Trip coil that must be ENERGIZED to make the MCCB trip open, a broken wire results in NO SAFETY OPERATION and is therefor contraindicated.

Using the UVR for ESD is more fail safe, but comes with another nasty side effect. EVERY time you lose power, the MCCB goes into a tripped state. This can result in unwanted resetting procedures that can result in frustration that leads to tampering. it can also cause the MCCB to wear out prematurely, they are not really designed to be used as a contactor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#5
In reply to #4

Re: MCCB Trip by Emergency Stop Button

03/12/2013 12:11 PM

There are some MCCBs with a coil, which trips the device whenever it looses power (I've seen 'em for 24VAC) you can use this coil to interlock the breaker, either to safety guards, control cabinet doors, or emergency stops. It works the opposite way to the one you describe as Shunt Trip.

They are fast and reliable and don't interfere with the thermo-magnetic trip function.

They have been around for a while.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: MCCB Trip by Emergency Stop Button

03/12/2013 12:27 PM
  • "There are some MCCBs with a coil, which trips the device whenever it looses power (I've seen 'em for 24VAC)"

Yes, that is the Under Voltage Release (UVR) I described above. But like I said, it trips EVERY time power is lost.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#7
In reply to #6

Re: MCCB Trip by Emergency Stop Button

03/12/2013 12:37 PM

No, the one I say is not monitoring the supply line voltage (thats the UVR option) it is just a 24VAC coil that trips the breaker when de-energized.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#8
In reply to #6

Re: MCCB Trip by Emergency Stop Button

03/12/2013 1:06 PM

I checked another document besides the one I provided a link for earlier, the manufacturers seem to describe their function in different ways, maybe the device performs the same but the text is a bit confusing.

Anyway, the ones I've seen don't leave you unprotected when a wire (of the coil) is broken, on the contrary they trip right away. I just can't remember the brand and model, but is a little late for that, the OP has already purchased the breaker...

By the way, we should ask the OP the brand and model.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Member

Join Date: Aug 2012
Location: Pune in Maharashtra
Posts: 5
#10
In reply to #8

Re: MCCB Trip by Emergency Stop Button

03/12/2013 11:42 PM

MCCB make- Scheider Model no.- CVS 250F

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9

Re: MCCB Trip by Emergency Stop Button

03/12/2013 3:00 PM

If it is fitted with or has an option for a remote trip function (or similar) you can. If not then the only way is some sort of crowbar circuit, but this is not recommended due to the assumed distribution class high fault current level (so much so that i am not supplying a link on what a crowbar circuit is).

What does the MCCB manual say?

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#12

Re: MCCB Trip by Emergency Stop Button

03/13/2013 6:48 AM

use a motorised MCCB.

__________________
pnaban
Register to Reply
Power-User

Join Date: Nov 2012
Posts: 183
Good Answers: 6
#13

Re: MCCB Trip by Emergency Stop Button

03/14/2013 7:16 AM

Use an RCCB and create an imbalance by adding a load using the Emergency stop switch. You can use as many Emergency Stop switches and don't need any additional wiring. Use earth connection on the other end of the load used to create the imbalance.

You can also lay a separate single return wire(neutral) bypassing the RCCB for creating the imbalance and tripping the RCCB.

Gajanan Phadte

Register to Reply
Anonymous Poster #1
#14

Re: MCCB Trip by Emergency Stop Button

12/08/2018 12:21 AM

Use UV coil, and connect NC Emergency stop switch in Series of its supply. You can also providing single phasing, reverse phasing protection by using UV coil