Add New Drive to an Existing PLC

03/15/2013 10:26 PM

Automation -Siemens we are using a siemens drive which can operate with plc.but it was damage due to some problem.after that we are using an abb drive.Abb drive only run in local mode.what can be the procedure to run it with existing automation in plc mode? please reply ...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Add New Drive to an Existing PLC

03/16/2013 12:19 AM

What does tha ABB drive literature say about external interface possibilities?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#2

Re: Add New Drive to an Existing PLC

03/16/2013 11:27 PM

That you have to ask this question, worries me that you aren't qualified to work on this unit. That said, I will give you a brief outline of how most drives & plc/dcs interact. Your drive generally has a power source dedicated for control function. The drive will have inputs that when 'open' will 'Stop' the drive and when 'closed' will 'Start' the drive. Your plc will have either a dedicated output or relay type output, that will utilize the power source from the drive, to control whether the drive sees power at the appropriate terminal, for the desired function. Those along with whatever safety or process interlocks and or other input signals such as a 4-20 mA or voltage input to control such things as the drives speed control, will also come into play. Please check with your ABB rep and your plc rep or your local qualified engineer/technician to access exactly what your system requirements are. Without knowing exactly what drive, plc, process interlocks and other control functions you have, it really is impossible to answer your question specfically. Be careful.

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Register to Reply
2
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#3

Re: Add New Drive to an Existing PLC

03/17/2013 2:36 AM

Atish09,

ABB drives, like virtually all others, supply their own internal power to operate their control terminals. That means that any switches or other controls that are attached to them must not impose an external source of power on these terminals. This is a fairly low voltage DC, which means that it must be kept away from electrically-noisy and line-voltage wires also, as well as be insulated for the maximum voltage on any wire within the cabinet (or box or raceway) these control wires are in. This is basic stuff that any industrial electrician should know and do.

You say that the drive can "run in local mode"--I interpret this to be that it can run from the keypad. Therefore, the drive's input and output sections are still good. You probably have a damaged control board.

Two steps to take:

  1. Check and ensure that the drive's control wiring to the PLC and all other controls does not interconnect with any source of power other than the drive. While doing this, also check the ABB wiring diagram to make sure the control inputs are correctly wired, so they are receiving their voltage from the proper terminal of the ABB drive. Use a decent multimeter set on DC ranges to do this.
  2. Contact a qualified person to then service/repair the drive.

Always, remember to properly protect yourself from any shock or arc flash hazard while doing this work. You are near live terminals, and depending on the supply circuit there usually is a potentially fatal amount of power present. Use tools that are insulated for the voltage present, use voltage-rated gloves, use a meter rated for at least 600V (and with a recognized testing agency's listing). Depending on the overcurrent protection on the input circuit and the other characteristics of this circuit, there can be enough energy present on the input terminals to do anything from making a bright light and loud noise to physically blowing you backward and sending you to the hospital for 2 months IF YOU ARE NOT WEARING PROPER PROTECTIVE CLOTHING.

-John M.

Register to Reply Good Answer (Score 2)