Damage to Single Core Cables

03/17/2013 11:56 AM

Installation - Three Phase 5 kv Service installation. Three ug 4 in. pvc duct runs, and three runs of 750 mcm, single conductor teck 90 xlpe with ft4 rating. Cable had aluminum armour, and also a concentric ground. 4/0 ground also ran in trench. All ducts encased in 3000 psi cement. Length of runs approx. 400 ft. from pole to switchgear.

Line side - Alumium armour and concentric ground connected to ground grid

Load side - Swichgear had zero sensing ct. Alumium plate installed on top of switchgear for cable glands. Cables with their outside pvc jackets and concentric grounds were passed through zero sensing ct window. 5kv terminating kits were used to terminate cables. Grounding flex straps which are part of kit were used to attach to concentric grounds by use of spring tension springs supplied with kit. Flex straps were connected together at this point and returned back up through sensing ct, and ground wire was taped off and isolated from ground.

Each flex strap should have been brought up through ct indepentant from each other, and isolated from ground.

Hy pot testing was conducted - phase to ground at 28kv,with good results. System engergized, everything ok.

Two months later,during routine checks, it was noticed that one of the flex straps had burned off.This is when flex straps were seperated to prevent current flow.We are about to do further tests in near future shutdown for cable damage.

Has anyone had experience with this kind of situation and if so what were end results. Please add your comments and what value of current do you think that was flowing in sheath. Load current varied at 400 amps. Voltage at 4.16 kv. We appreciate your comment.

Thankyou in Advance !

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Damage to Single Core Cables

03/17/2013 6:19 PM

If you bond together the flex straps at both ends, a current will circulate as if they are bonded and grounded at both ends. Imagine the armor as a winding and if the three windings are connected together at the ends three_ phase currents will flow and the sum of these currents will be zero only at the connection point.

You have to isolate each strap from the ground and from each other at the not_grounded end.

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#2

Re: Damage to Single Core Cables

03/18/2013 3:24 AM

If you have both ends of the cable earthed, and they are single cores, as stated, remove/disconnect the far end earths and this will reduce the circulating earth fault currents you have created in the XLPE cable.

Separate the earths from the terminations to thier own earths, Do not connect them together then take them to earth. Make sure the termiation kit is an 11/6.6kV(7.5 kit) and that the constant force springs, (tension springs) and securely wound around the core and that the heat shrink, I think you have used, has been shrunk properly, smoothly, equally. Even wall thickness.

Your end result will be that the cable burns at the stress cone edge, it will go straight to earth via the semi con and pop to earth. Also, check you earth fault currents and check the cross section of what you call the concentric neutral, against the cross section of the earth straps. Normally the earth straps vary fromn 35mm2 to 70mm2. You may have to install bigger earth starps or two to suit the cable earthing/screening tapes and wire. Also check to make sure the outer sheath is not graphite coated, if it is it is a semi conductor and the earthing is poor along the cable. And make sure you use Brundy paste on the ali/copper connections. If your cable is rated at 6.6/11kV, you Hi Pot test is too high. 18.6Kv is your test voltage, if DC and 11kV if AC. You may have created a problem, on over voltage testing at the earth point of the termination. Your sheath fault current was varying due to load and it was highest at the termination earth point, where it should be, due to poor earthing, right at the termiantion. Cheers

Register to Reply
Anonymous Poster #1
#3

Re: Damage to Single Core Cables

03/18/2013 4:04 AM

We assumed you are connected grounding flex straps both end of the cables termination to the ground ,this facilitate the circulating current path to circulate through the armour, This circulating current creates heating effect at the glands & even may become red hot and damage the cable.

Action: Terminate both end of the cables on nonmagnetic gland plate preferably AL plate.

& ISOLATE earthing flex straps on both side of the terminals this will solve your problems.

you mentioned you have tested HI pot of cables with 28KV,YOU HAVE INJECTED VERY HIGH VOLTAGE there is a chances of damaging the cable,maximum you can use DC 8.5KV test voltage during hi pot.

Register to Reply Off Topic (Score 4)
Member

Join Date: Mar 2013
Posts: 5
#4

Re: Damage to Single Core Cables

03/18/2013 10:41 AM

Flex Straps have been seperated from each other, and ground.Burnt flex strap has been repaired for now.We are waiting for a shutdown to do more tests and investigation.

Questions-

1 - If load current was 400amps on each conductor. What was valve of sheath currents flowing in each phase and at connection point of flex straps that were connected and not grounded.

2 - Do you think we may have cable damage anywhere ?

3 - What type of tests should we be doing during shutdown ?

*Note - Cable Glands on Line ( Pole ) side were in free air and armour/ concentric neutral were grouned on this end only.

Thankyou All for Comments so far. Just wandering what we might expect to find during shut down.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#5
In reply to #4

Re: Damage to Single Core Cables

03/18/2013 2:19 PM

The value is around 200Amp on the shield wire, (concentric neutral), The wires can take a higher KAmp, but the time is reduced tremendously i.e 10kA for 0.1 second. Make sure the earth strap used is of the same cross section as the copper tapes in the cable. If possible, use the next cross section earth braid up, or double the braid over and securely bind in or use a constant force spring to secure the doubled-over braid, to the shield wires. Over wrap the constant force spring with 3M,No 23 tape. (self fusing tape) just to smooth the spring edges and secure the braid connection to the copper tapes. On the earth braid one needs a damned good connection to the cable tapes/wires as there is a great deal of stress and force at the connection point. Make sure the XLPE is clean, no scuffs and scratches, make sure their is no carbon building up on the insulation and pay particular attention for treeing/ferning on the insulation. (You will need to strip down the termination to see this on the XLPE). Don't be applying pressure test, (Hi Pot), at over voltage, just stick to the service voltage used. You could try doing a sheath test at 10KV for 1 minute, but I doubt this will provide you with any evidence of a fault. I would expect on a pressure test, (Hi Pot), the leakage current should not be higher than 5ma on each cable. If you want to check further for Pd, take a radio, put it slightly off station and while the cable is under test, you will hear the Pd on the radio as interference, and you will hear the termination discharging both on the radio and on the termination. (Not a super test but, It works if you don't have Partial Discharge tester). NB, MAKE SURE YOU EARTH THE CABLE BEFORE WORKING WITH IT AND KEEP IT EARTHED. XLPE builds up a capacitance charge and it bites 24 hrs later. To get your sheath fault amps one needs more details than 400amp! need Tfx amps, etc etc. Cable damage may only be within the crutch area of the termination, and it will be carbon you will look for, If there is carbon, you can try cleaning it with a non conductive cleaner and lint free cleaning pads. DONT WIPE the semi-con then wipe the xLPE with the same pad, you will transfer semi-con to the XLPE. I have found it pointless and quicker, cheaper and more sensible to replace the cable. (Long term). The pole side was earthed and the switchgear side was also earthed via a CT. You said? Disconnect the pole side earth from earth. Leave the armour and tapes earthed together only and keep the earthing at the sub station side so circulating to one side only, not both sides, and not taking in your line currents as well as your cable currents. Hope this all makes sense to you, and I hope it helps you. Sometimes it is just a bad/weak earth connection and the braid being to small to handle the load. You could try the radio as above now, if the cables are energised, you should hear any discharge taking place, even a walkie-talkie works to hear discharge. !!!!!This is only indicative and not a proper test or test method!!!!! Have fun.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#6
In reply to #4

Re: Damage to Single Core Cables

03/18/2013 2:22 PM

This site crams my paragraphs together and changes the spacing. Sorry if it is difficult to read, I can safely blame the SYSTEM and not me. Cheers

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #6

Re: Damage to Single Core Cables

03/18/2013 2:43 PM

You can throw a <br> to separate your own paragraphs manually.

I have to do that on my iPad for some forums.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#8
In reply to #7

Re: Damage to Single Core Cables

03/18/2013 3:51 PM

I sometimes throw a wobbly and give up with computers. But, I shall try the <br>. I hope the info is helping the lads with these cables. Hope it is also helping others, so if I am loosing folks, they must tell me. Far easier to speak than type instruction and advice. Mayhap's I need to do a common terminology list for people and then there is less confusion when typing i.e. OPGW, is referred to as 'fibre optic ground wire (FOGW)'. The real acronym is OPGW, Optical Power Ground Wire. But, THANK YOU for your kindly advice and help, its appreciated. Cheers.

Register to Reply
Member

Join Date: Mar 2013
Posts: 5
#9
In reply to #8

Re: Damage to Single Core Cables

03/18/2013 4:24 PM

Thankyou IQ for your detailed comments.

Just to let you know cable is non shielded, has no semi con, has a concentric wire shield of 2/0, wire shield was connected to ground on pole side only,not at switchgear. They were connected together but isolated from ground at this end.

Cable Structure - PVC Jacket - Aluminum Interlocking Armour - Inner PVC Jacket - Concentric Copper Ground Wires - XLP Insulation - Conductor Shield - ( Not Semi Conductive) - and 750 MCM Copper Conductor.

What would be approx. sum of currents flowing in this case

We do have some slack in cables and could do new terminations. Also this being a non shielded cable we can remove concentric ground wires back closer to top of gland entry point, bend concentric wires back, cut & tape for isolation. Cable can be terminated with out stress cones.

Please Comment. Again Thanks for all comments

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: Damage to Single Core Cables

03/21/2013 9:41 AM

The armor and grounding total circulating currents-all three phases connected together both ends-calculated as per IEEE-525 could be about 40A -if the main conductor current would be 400 A. But in short-circuit case for 15 KA per phase the circulating current could be 1400 A. If the fault clearing time will be 0.5 sec a 4 awg copper conductor will melt down.

__________________
Julius
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); Anonymous Poster (1); cuba_pete (1); electron (2); IQ (4)

Previous in Forum: Can Amps Going to Ground Make My Bill Higher   Next in Forum: Inductor for AC to DC Welder Conversion

Advertisement