Installation - Three Phase 5 kv Service installation. Three ug 4 in. pvc duct runs, and three runs of 750 mcm, single conductor teck 90 xlpe with ft4 rating. Cable had aluminum armour, and also a concentric ground. 4/0 ground also ran in trench. All ducts encased in 3000 psi cement. Length of runs approx. 400 ft. from pole to switchgear.
Line side - Alumium armour and concentric ground connected to ground grid
Load side - Swichgear had zero sensing ct. Alumium plate installed on top of switchgear for cable glands. Cables with their outside pvc jackets and concentric grounds were passed through zero sensing ct window. 5kv terminating kits were used to terminate cables. Grounding flex straps which are part of kit were used to attach to concentric grounds by use of spring tension springs supplied with kit. Flex straps were connected together at this point and returned back up through sensing ct, and ground wire was taped off and isolated from ground.
Each flex strap should have been brought up through ct indepentant from each other, and isolated from ground.
Hy pot testing was conducted - phase to ground at 28kv,with good results. System engergized, everything ok.
Two months later,during routine checks, it was noticed that one of the flex straps had burned off.This is when flex straps were seperated to prevent current flow.We are about to do further tests in near future shutdown for cable damage.
Has anyone had experience with this kind of situation and if so what were end results. Please add your comments and what value of current do you think that was flowing in sheath. Load current varied at 400 amps. Voltage at 4.16 kv. We appreciate your comment.
Thankyou in Advance !