One of the station GT's tripped with 87 relay. The IR of the HV winding to earth was measured and found to be very low - 5 MOhms with a 5KV insulation tester. While performing the Tan Delta test (Chg) the tan delta test set tripped at 7.3KV and smoke came out from the Neutral Bushing of the GT. The BDV of the insulating oil is good 50KV, moisture content is low 40 ppm. Transformer was in service for the last 40 odd years. We will be carrying out further tests today to make an assessment of the condition of the transformer.