03/28/2013 7:30 AM
i have a siemens micromaster drive in our plant which has an analogue input control of 0-20mA but the existing analogue control on the plant is a 4-20mA. without changing the existing control signal of 4-20mA, how do i use the 0-20mA drive on an analogue input control of 4-20mA.
Will appreciate greatly if i can be assisted.
Good Answers: 11
Re: How to Use 0 - 20mA Drive on a 4-20mA System
03/28/2013 8:37 AM
Suggest one of these or similar:-
ASC230 - Signal Converter / Transmitter
http://www.amelec-uk.com/products/ASC230-%252d-Signal-Converter-%7B47%7D-Transmitter.html
rogerggbr
04/02/2013 7:04 PM
Also check the drive manual and application notes (check the Siemens website) to see if it can be reconfigured or programmed to accept a 4-20mA input.
If it can it is much cheaper than buying the necessary signal converter.