Arc Flash calculations give thermal energy, with the empirical statement that over 40cal/cm2 is "dangerous" because of the blast pressure. I think this assumes the arc flash energy is all released in a very short time duration such as 0.05 sec. But if the clearing curve for a fuse or breaker puts the time duration past 0.5 sec. or longer, I suspect there is a point where the correlation between thermal energy and blast pressure is no longer linear. In this case it may be possible to survive an arc flash with >40cal/cm2 energy even though conventional thinking says NO. Suits are available up to 100cal/cm2. Is there any research on this correlation between thermal energy and blast pressure for arc flashes where the duration is not very short? If not, perhaps this would be a good research topic for an EE student.
--John Mueller
Pathfinder Tags: Arc Blast arc flash
Good Answers: 181
Re: Research Idea: Thermal Energy and Blast Pressure
04/02/2013 7:14 PM
The only way to find out if you're supposition is correct is put it to the test.
You wear the suit, if you survive you can publish the findings.
Good Answers: 128
04/04/2013 8:21 PM
TonyS,
I assume your post was "tongue-in cheek". I unintentionally did such a test but on a lower energy circuit and found the calculations to be valid. No injury, but some metal vapor was deposited on my leather glove protectors. (This was when I turned on a disconnect for a small motor, tapped from parallel 3x500mcm with an 800A breaker set to the lowest IT setting; I was pushed off balance by the force of the closed door as it was blown open.)
--JMM
Register to Reply 2 comments