VFD Over Current Trip

04/01/2013 11:22 PM

Hello,We have a small trouble working with VACON vfd which is installed at our power station and thought of getting an solution from support team available online.We have a NXP 0385 Model vacon drive to run a ABB motor rated 180 kw.Motor is used for pump application and cable length is nearly 300m from the o/p of drive to motor terminals.The problem is VFD getting frequently over current trip with the fault code F1 and this trip is occuring even when the motor is in OFF state. The drive suddenly shows up trip during off state too.The motor current from fault history is noted as 5A and DC link voltage is 570v. Rest of all are recorded as zero as motor is not running.The drive has input choke and no output choke. Drive is being run in V/F open loop mode and no brake resistor is being used. We checked all possible parameters which might be able to cause this trip 1. Current limit scaling
2.Brake current during off
All were found normal and none of them were enabled.Vacon engineer visited the site and said the igbt module in the inverter might be malfunctioning.As much as i know..the igbt module wouldnt be functioning unless the start command is given to the drive but the drive here is showing the fault indication even when the motor is off state ie drive is idle. Pls suggest some solution fot this..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: VFD Over current trip

04/01/2013 11:54 PM

It sounds like a reflective wave issue because of the long cable run.If you have a local isolator near the motor, try switching off that isolator and note the amps on the drive.It should be close to zero but if its high then thats the problem.You can try decreasing the switching frequency to prove this as well.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#4
In reply to #1

Re: VFD Over current trip

04/02/2013 11:16 AM

A good answer from an AP? Eh? Why would one do that?

Register to Reply Score 1 for Off Topic
Anonymous Poster #2
#9
In reply to #4

Re: VFD Over current trip

04/02/2013 3:52 PM

Hello Cuba Pete

Many of us started as AP's, earning many GA's, until we thought it wouldn't hurt to have a record too.

Regards

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#15
In reply to #9

Re: VFD Over current trip

04/04/2013 10:51 AM

I am the one who gave the AP a GA doofus!

Cheers!

Register to Reply
Member

Join Date: Mar 2013
Posts: 6
#7
In reply to #1

Re: VFD Over current trip

04/02/2013 2:02 PM

Hello,

The drive trips during motor OFF state too..Load current during OFF trip was recorded as 5 A..Let us consider the 5 A is due to capacitive effec of cable and still 5 A is too less for tripping..Would you pls suggest regarding swithching freq modification its presently at 3.5KHz

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: VFD Over current trip

04/02/2013 6:13 AM

Presumably the cable to the motor has been 'meggered' recently, and passed the test?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Mar 2013
Posts: 6
#5
In reply to #2

Re: VFD Over current trip

04/02/2013 1:54 PM

Heelloo..

The motor and its cable both have been meggered and found normal,they are working normal with another standby drive

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#3

Re: VFD Over Current Trip

04/02/2013 10:01 AM

we have this same scenario from my previous employer, i am sure that the igbt's are all fine..the problem lies in your triggering circuit.

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Member

Join Date: Mar 2013
Posts: 6
#6
In reply to #3

Re: VFD Over Current Trip

04/02/2013 1:56 PM

Hello..

Would you pls what steps have you taken in your previous plant to solve dis one..

We r planning to change the entire igbt module on the suggestion of service engineer and is costing almost 90% of drive cost

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: VFD Over Current Trip

04/02/2013 3:07 PM

If it is tripping when the drive is in the OFF state, it will typically trip on ANY amount of current flow, because the expected amount is zero. So it CANNOT be anything associated with the load wiring, motor windings etc., it can ONLY be an internal issue in the drive. If one of your IGBT modules is cracked and failing, it could be leaking current to ground (the heat sink itself) across a carbon trace left over from a previous catastrophic failure of the device. A reflected wave issue may have contributed to that failure, but that is not what you are seeing now.

Your drive is toast. Most of the time, the cost to disassemble it to get to the bad IGBT module and replace it might exceed the value of the drive. In addition you most likely will need to replace them all, because if something stressed one of them enough to cause this, the others were stressed as well. This was just the weakest link.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Member

Join Date: Mar 2013
Posts: 6
#10
In reply to #8

Re: VFD Over Current Trip

04/03/2013 2:38 AM

Thanks for the reply. But in your case as u said the drive would trip continuously if a IGBT is shorted through heat sink..Here the drive runs fine for some time and then shows up suddenly over current trip..It runs fine for hours to even days some times with outa trip..and some time trips even when drive is idle not running!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: VFD Over Current Trip

04/03/2013 3:20 AM

Swap it for the strategic spare in the stores, and either send it away for repair or buy a replacement.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14
In reply to #10

Re: VFD Over Current Trip

04/03/2013 2:51 PM
  • "... But in your case as u said the drive would trip continuously ..."

I never said that, you read something into what I said. I said IF it is leaking any current, it will trip. It could be leaking current via a carbon trace left behind from a more catastrophic failure. But that does not mean it is leaking continuously. There may be a myriad of environmental and situational contributing factors involved in it, so sometimes it happens, sometimes it doesn't.

Bottom line, the signs point to a either a malfunctioning IGBT, or magical thinking about ghosts in the machine. You take your pick

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster #1
#12

Re: VFD Over Current Trip

04/03/2013 3:57 AM

What type of cable are you using? If its not XLPE does vacon recommend a filter on the load side.Try dropping your switching frequency to 2KHz and see if the problem goes away.Note,a lower switching frequency can cause other issues but it may prove that this a classic case of reflective wave form.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#13

Re: VFD Over Current Trip

04/03/2013 5:01 AM

Check the cable run (300m !) and make sure it is screened properly and that the screen is grounded at the VFD side. The 5A when OFF is possibly enough to trip the drive because it expects a zero current at that stage. Where is the 5A current coming from? Either the igbt is fulty, or its drive circuit is faulty or the cable is picking stray voltage enough to drive a 5A current ???

Register to Reply
Member

Join Date: Mar 2013
Posts: 6
#16

Re: VFD Over Current Trip

04/25/2013 1:56 PM

Hello Everyone,,

I have observed few things which i felt sharing,,

As we felt the excess cable length of nearly 300m was a concern here,,We isolated the cable from drive and found drive still tripping with Over current fault ( Under same condition of drive being in OFF state, ie IDLE State)

While the cable was isoalated, the drive output voltage was found 50V, and after connecting cable with motor back drive output voltage dropped to 6v), These were observed during drive OFF state.It takes a current of 0.5 A

My doubt is why is drive producing a ouput voltage of 50v even when it is off?

The drive runs fine for some time and suddenly trips showing over current both the times when it is running and stopped time.

The fault history data shows a normal current but still trips,,

Service engineer suggested IGBT module is malfunctioning and needs to be replaced which equals the cost of a new drive,

We procured a new drive instead of a module and trying to find the cause for this,

Suggestions pls,

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#17
In reply to #16

Re: VFD Over Current Trip

04/25/2013 6:09 PM

well, since you have procured a new drive and going to try it, then if the new drive operates correctly without tripping as before, under the same conditions, this would have prouved that the old unit was faulty!

If the fault persist, then ??

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#18
In reply to #16

Re: VFD Over Current Trip

04/25/2013 8:21 PM

Quoting myself earlier:

  • "If it is tripping when the drive is in the OFF state, it will typically trip on ANY amount of current flow, because the expected amount is zero. So it CANNOT be anything associated with the load wiring, motor windings etc., it can ONLY be an internal issue in the drive. If one of your IGBT modules is cracked and failing, it could be leaking current to ground (the heat sink itself) across a carbon trace left over from a previous catastrophic failure of the device. A reflected wave issue may have contributed to that failure, but that is not what you are seeing now.

    Your drive is toast. Most of the time, the cost to disassemble it to get to the bad IGBT module and replace it might exceed the value of the drive. In addition you most likely will need to replace them all, because if something stressed one of them enough to cause this, the others were stressed as well. This was just the weakest link."

Quoting your recent post:

  • "Service engineer suggested IGBT module is malfunctioning and needs to be replaced which equals the cost of a new drive,"

So, you doubted me, now you paid someone to look at it in person and he confirmed what I said, now you are still doubting him? Man, you are a tough sell my friend...

You had a damaged transistor. It was not a complete meltdown, so it only caused a fault under certain conditions, most likely related to heat and stress. If you have thoroughly tested the motor circuit components, i.e. the conductors, the connections, the motor windings, and I do me THOROUGHLY, as in using a megger, not just a multimeter, and you are confident that it was not a reflected wave issue, then you can safely assume it was a random component failure in the drive and get on with your life.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Feb 2015
Posts: 1
#19
In reply to #18

Re: VFD Over Current Trip

02/19/2015 10:59 PM

Hello Raef. I read it a long time ago Vacon frequency inverter overcurrent error occurred with the engine as well. Now I have the same situation, but unfortunately for me the inverter should fix it. You may not remember what the transistor was wrong? I suspected from the IC. Thank you in advance for your help. Sorry for the mistakes, I'm Hungarian. Welcome to WordPress. Gabor

Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); cuba_pete (2); gabo7600 (1); gowrivsp (5); JRaef (3); LAA_Lucke (2); PWSlack (2); rockraiden (1)

Previous in Forum: Research Idea: Thermal Energy and Blast Pressure   Next in Forum: Dead Time Constant of IGBT

Advertisement