Tan Delta Test Of 250MW Generator

04/16/2013 11:33 PM

Dear friends i have recently performed tan delta test on 250MW generator and the values in GST mode obtained were well within limit.But UST mode tan delta (PF)values were negative. Kindly give some explanation regarding the negative values and what its significance ,Whether anything to worry ? The tests were performed at 2kv ,4kv,6kv and 8kv.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Tan delta test of 250MW generator

04/17/2013 3:26 AM

One route to the answer is to make a telephone call to the technical helpline of the generator's manufacturer. It would certainly be faster than waiting for someone on CR4 who can be bothered to type in the correct response, and safer than risking mis-evaluating CR4 responses.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Tan Delta Test Of 250MW Generator

04/17/2013 9:49 AM

I have seen similar results when doing Doble Insulation Power Factor tests (essentially the same as tan delta) on generators. If I remember correctly, the sign is not significant, and you evaluate based on the magnitudes of the test results. Do you or your client have past test results for this generator for comparison? Usually this sort of thing is specific to a particular unit, so you will see it happen repeatedly.

You might also query the tech support people at the manufacturer of your tan delta tester. They should have some experience interpreting its output and be able to tell you what causes the polarity reversal.

Don't base your evaluation of the generator on what I say, but I believe if the results (based on magnitudes) are acceptable, the stator insulation should be good. Are the tip-up values good? Did you also take radio interference voltage (RIV) measurements while testing, and if so, are they acceptable (< 1000 μV at highest test voltage)? Is there any significant change from previous tests? These are the questions you have to ask.

__________________