Fire Rated Wall Between Transformers

04/25/2013 2:12 AM

Kindly brief me the purpose of fire rated wall between the transformers and which standard/code guide the electrical designer to construct in the substation?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Fire rated wall between transformers

04/25/2013 3:21 AM

A1) It is to prevent a fire in one transformer affecting the operation of another.

A2) It is likely to be a Civil Engineering code, as Electrical Engineers don't build walls. Which country, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2012
Posts: 115
#2

Re: Fire rated wall between transformers

04/25/2013 4:47 AM

For indian projects only.

I am not sure that it is described in civil code. It may be a technical requirement for transformer.Because that fire rated wall is requested by the electrical engineer not by the civil engineer.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Fire rated wall between transformers

04/25/2013 7:26 AM

According to : NFPA-850 Recommended Practice for Fire Protection for Electric Generating Plants and High Voltage Direct Current Converter Stations

Ch. 5.2.4.4 "Unless consideration of the factors in 5.2.4.2 indicates otherwise, it is recommended that adjacent oil-insulated containing 500 gal (1890 L) or more of oil be separated from each other by a 2-hour-rated firewall or by spatialseparation in accordance with Table 5.2.4.3."

__________________
Julius
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Fire rated wall between transformers

04/25/2013 8:02 AM

...so it's whatever the Indian equivalent of NFPA-850 is, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Fire rated wall between transformers

04/25/2013 10:27 AM
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Fire Rated Wall Between Transformers

04/25/2013 11:08 PM

Whether there is firewall or not if recommended/proper fire detection/ extinguishing measures are not taken fire will cause damage to anything.

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Fire Rated Wall Between Transformers

04/26/2013 7:53 AM

It is very clearly mentioned in the Indian Electricity Rules, 1956, Rule No. 64 (2) (e) (i) that "(e) Where a sub-station or a switch station with apparatus having more than 2000 litres of oil is installed, whether indoor or out-doors, the following measures shall be taken namely:-

(i) The baffle walls 2[of 4 Hours fire rating] shall be provided between the apparatus in the following cases:-

A. single phase banks in the switch-yards of generating stations and sub-stations;

B. on the consumer premises;

C. where adequate clearance between the units is not available".

Hope the above is clear.

Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); electricalexpert65 (1); lyn (1); Muthuvel (1); pnaban (1); PWSlack (2)