Substation Insulated Floor Mat

04/26/2013 10:22 PM

Sirs,

If my substation & switchboard is 33kV rated, what class & type of floor mat should I use with reflect to IEC 61111. I'm a bit confuse on nominal max working voltage definitions.

Working voltage is refers to phase-phase as working/rated voltage(33kv) or phase to ground (19kV) only (during any faults).

Appreciate any advice.

__________________
Elect & Instr
Register to Reply
Pathfinder Tags: Floor Mat
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Substation Insulated Floor Mat

04/26/2013 10:58 PM

What is your confusion? Do you need a copy of IEC 61111?

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2
In reply to #1

Re: Substation Insulated Floor Mat

04/26/2013 11:33 PM

Please show the chart for selection or give a link to download.

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Substation Insulated Floor Mat

04/27/2013 12:03 AM
Register to Reply
Active Contributor
Malaysia - Member - Master

Join Date: Mar 2008
Location: Malaysia
Posts: 21
#4

Re: Substation Insulated Floor Mat

04/27/2013 2:22 AM

Here is the difference:

1. If I consider Phase-phase Volt (33kV), I need to select Class 4 Rubber Floor Mat since the max working voltage is 36kV

2. If I consider Ground-Phase Volt (19kV), then I can select Class3 Rubber Floor Mat since the max working voltage is 26.5kV

If you can send the copy of IEC61111 is a pleasure to receive it. Thanks.

__________________
Elect & Instr
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7
In reply to #4

Re: Substation Insulated Floor Mat

04/27/2013 7:26 AM

that actually made me laugh...thanks

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#5

Re: Substation Insulated Floor Mat

04/27/2013 2:52 AM
Register to Reply Score 1 for Off Topic
Active Contributor
Malaysia - Member - Master

Join Date: Mar 2008
Location: Malaysia
Posts: 21
#6

Re: Substation Insulated Floor Mat

04/27/2013 2:53 AM

Below is the snip image of the table.Plase help to choose.

__________________
Elect & Instr
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #6

Re: Substation Insulated Floor Mat

04/27/2013 10:09 PM

"Line Voltage" in column 3 = phase-to-phase, not phase-to-ground. Thus Muditmah is correct (GA).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#8

Re: Substation Insulated Floor Mat

04/27/2013 1:04 PM

go for class 4 rubber mat...

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10

Re: Substation Insulated Floor Mat

04/28/2013 7:00 AM

If you need a rubber mat you're in serious trouble and the chances of survival with 33KV is minimal.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#11
In reply to #10

Re: Substation Insulated Floor Mat

04/29/2013 8:27 AM

This is a safety and statutory requirement. Nobody is going to touch 33 kV live part deliberately while standing on the rubber mat!

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#12

Re: Substation Insulated Floor Mat

05/15/2013 12:05 AM

How is your system earthed?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #12

Re: Substation Insulated Floor Mat

05/15/2013 12:10 AM

Let's hope it isn't via high-resistance earthing through the rubber mat.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

debata07 (1); electricalexpert65 (1); Fredski (1); lyn (2); muditmah (1); nobodysomebody47 (1); pnaban (1); TonyS (1); Tornado (2); Yasser (2)

Previous in Forum: Inrush Current and Stating Current of Motor   Next in Forum: Annuciator LCD Monitor

Advertisement