Panel Sizing Query

04/27/2013 6:38 AM

Dear Engineers,

I came across an electrical SLD in last day. In the SLD there is one panel with the following feeders

2 Nos of 14.9 kw load
2 Nos of 29.8 kw load
1 no of 48.6 kw load
2 no of 100 A spare
1 no of 250 A spare


The design consultant has assumed the demand factor as 1
so the connected load and maximum demand load is the same and it comes to 138 kW

So the current will be 240 Amps

So the main breaker can be of 400 so as the busbar of the panel.

But they have mentioned in the SLD as 630 A busbar.
Another panel with the same connected load of 138 kw is provided with 400 A breaker and bus bar in the SLD.

The out going feeders are same except that instead of 1 no 250 A spare they have provided 1 no 100 A spare.

Why this difference since the maximum demand is the same...?

If any one knows how it is done please share the valuable suggestion


Note: This project is not handled by me but by one of colleagues I asked him about this he also don't know and he is least bothered in how they have determined all these. He is the in charge of project he can only raise queries to the design consultant. So I cannot ask them directly. I am asking this because of my curiosity to know. So kindly don't reply like " Ask them" etc....

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Panel sizing query

04/27/2013 7:34 AM

What voltage? (Or what amperage for the kw-designated items?)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Panel sizing query

04/27/2013 9:32 AM

3 phase 415 V

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Panel sizing query

04/27/2013 10:29 AM

There's more to sizing than just looking at the total load per feeder.

Somewhere there may exist a design document that may detail criteria that does not show up on the SLD, things like allowance for future load growth, critical loads with tight voltage drop criteria, high and/or simultaneous motor starts with high torque/inertia mechanical loads, etc., etc. Or it could be something as simple as a company-wide philosophy such as "...always choose the next size up from what the calculations dictate..." or "...we've always done it that way..."

Welcome to the real world of engineering where not every answer makes sense or is found in the back of the book.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Anonymous Poster #1
#6
In reply to #3

Re: Panel sizing query

04/28/2013 3:57 AM

Thank you for the answer

But why for the same load ratings different incomer ratings.?

The loads on both panels are of same type and power rating .

The only difference is the no of spare feeders.

Can you please tell me what is the normal philosophy you will use when you include spares along with the maximum demand in calculating the incomer size as well as the busbar..?

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7
In reply to #6

Re: Panel sizing query

04/28/2013 3:30 PM

Busbar sizing and design also has to take into account prospective short circuit current, which may mean a different busbar sizing or arrangement/support for two panels that are supplying the same load.

Are these two panels on two different sites or different sections of the site where short circuit currents could be quite different?

__________________
jack of all trades
Reply
Anonymous Poster #1
#8
In reply to #7

Re: Panel sizing query

04/29/2013 5:51 AM

Thanks,


So if the panel is located near the source (ie the main distribution panel which is fed from the transformer) the short circuit current available will be more (approximately) because of the lesser cable length. And the panel which is located far from the source will have less. (I am neglecting the types of loads because in this case loads are same)

Please correct me if my understanding is wrong..

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11
In reply to #8

Re: Panel sizing query

04/29/2013 3:06 PM

Generally yes.

Consider going back to real simple basics and imagining the cables as different sized resistors and the transformer as the source if this helps you picture what's happening in a real world system (which is obviously more complicated than this).

__________________
jack of all trades
Reply
Anonymous Poster #1
#12
In reply to #11

Re: Panel sizing query

05/02/2013 2:05 PM

But in the SLD along with the busbar amperage they have mentioned the SC value as 50 kA for both the panels..

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#13
In reply to #12

Re: Panel sizing query

05/02/2013 3:06 PM

Well then perhaps the second panel has some additional expansion built it to its design, in that additional or larger sized circuit breakers could be added or replace the existing ones later. There may not be enough information on the SLD alone to ever know for sure.

It could also be a mistake (consultants aren't perfect).

__________________
jack of all trades
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Panel Sizing Query

04/27/2013 11:37 AM

Since you don't bother to inform us of your location, there's no way to know what codes and regulations are in play.

Ask the consultant to enlighten you.

Or consult the code books.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Panel Sizing Query

04/27/2013 11:57 PM

For busbar sizing you should consider SC level and tripping time of CB too.

__________________
pnaban
Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#9

Re: Panel Sizing Query

04/29/2013 8:28 AM

While sizing the panel, especially for motor loads following two things are important:-

(a) starting sequence of all these motors

(b) number of restarts per hour

In the second case (where 400 A Incoming feeder is provided), we can only assume that the very few motors start simultaneously.

The exact answer can be arrived by knowing the correct starting sequence.

Loads involving motor have high diversity. Diversity factor can be taken as 1.4

Wherever two motors of equal ratings are provided; one is usually stand-by.

Hence check for these factors to arrive at the answer.

I am 100% sure that you are from India.

Prashanth

Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#10

Re: Panel Sizing Query

04/29/2013 8:53 AM

I forgot to add one more point :-

Sizing of incoming breaker for a panel (supplying motor loads) also depends on co-ordination with upstream breaker.

if the selected breaker size is too less (improper co-ordination) & in case of fault, upstream breaker may trip.

Hence this may be one of the reasons for selecting (630A feeder) in your case.

Prashanth

Reply