Fault Duration For Ground Conductor Sizing

05/07/2013 2:18 AM

IEEE 80: 2000 caluse 11.3.3 b) suggests taking fault duration as 3s for smaller S/S and 1s for larger S/S.

1) What is the definition of smaller and larger S/S? Can it be defined in terms of voltage ?

IEEE 80 also suggests to take shock duration equal to fault duration for calculation of Step and Touch voltage.

2) If we consider 3s as shock duration it will be difficult if not impossible to design a ground grid system.

3) Some consultants specify 3s as fault duration for ground conductor sizing (as the conductor will be burried in soil and will be non-accessible in future for checking) and 1s as shock duration for step and touch voltage calculation.

Can somebody clarify the above with reference to international standards?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Fault Duration for Ground Conductor sizing

05/07/2013 3:19 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Member

Join Date: May 2013
Posts: 7
#2
In reply to #1

Re: Fault Duration for Ground Conductor sizing

05/07/2013 5:26 AM

Sorry PWSlack. I was looking for some concrete answer. Please do not give any reference to any standard. However, you may elaborate what BS 7671 specifies. I do not have access to BS.

Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Fault Duration for Ground Conductor sizing

05/07/2013 5:55 AM

Everyone has access to British Standards, as they are available for purchase from the British Standards Institute's outlets on-line.

At this moment, the forum does not know the country for which the installation is intended. Each country has its own electrical standards, which encompass the varying supply parameters and installation practices prevailing in each. The applicable standard is always the starting point. Without it, one is relying on opinions from anonymous postings in an international forum without the wherewithall to evaluate them, which exposes one to the possibility of interminable wrath if an installation hurts, maims or kills someone. Don't go there.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #2

Re: Fault Duration for Ground Conductor sizing

05/07/2013 11:40 PM

According to Bs7671,for sizing earth conductor in the adiabatic equation K^2S^2=I^2t

t is normally considered as 1sec.

__________________
pnaban
Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: Fault Duration for Ground Conductor sizing

05/07/2013 8:23 AM

To answer your last question first, IEEE 80-2000 is the principal international standard for grounding system design. Some additional time spent familiarizing yourself with more of the body of the standard should answer your questions.

The first reference you bring up relates to the selection of ground grid conductor size based on thermal damage to the conductors caused by fault current in the grid. The tables in 11.3.2.2 give you information on how much current can be carried by different size conductors for how long before they fuse / melt. The times you quote (3 and 1 sec.) are not referring at this point to safety of a person or proposed fault clearing times, but how long the grid can withstand the damaging effects of fault current before the conductors burn up.

Therefore "smaller" and "larger" substations in that section don't have an absolute definition - they're just relative descriptors. It's up to the designer to determine whether you have enough copper in the ground for the fault currents, the soil conditions, and the protection schemes to keep your system physically intact and your people safe.

Section 5 gives details on the effects of various levels of current in the human body, and concludes by recommending that maximum design fault clearing time be limited to 0.5 sec. or less. Most people designing ground grids work based on that limit. Using 0.5s and modifying the design as needed to achieve acceptable step and touch potentials and ground potential rise is usually possible, but may require more copper in the ground or a larger (in area) ground grid than you originally planned for. This is part of the "art & science" of ground grid design.

You would do well to do another careful read-through of IEEE 80 and make sure you grasp all the parts together.

__________________
To get the right answers, first you need to ask the right questions.
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Fault Duration for Ground Conductor sizing

05/07/2013 9:18 AM

You are right: the fault clearing time of 3 sec it is only for conductor sizing. See IEEE-80/2000 :

CH.11.3.3 Additional conductor sizing factors

"a) Relay malfunctions can result in fault duration in excess of primary clearing times. The backup clearing time is usually adequate for sizing the conductor. For smaller substations, this may approach 3 s or longer. However, because large substations usually have complex or redundant protection schemes, the fault will generally be cleared in 1 s or less."

It is still not a compulsory requirement but a "usual" consideration.

That depends on protection fault clearing time-mainly for backup protection.

For instance: if the first step could be 6 cycles[100 msec] the backup could be 1 sec.

However, there is not a recommendation to calculate Etouch or Estep for more then first step taken into consideration that statistically it occurs very seldom [almost never]: a man could be in danger of touch- or step- and in the same time the first protection would fail.

See: 16.2.2 Fault duration (tf) and shock duration (ts)

"Typical values for tf and ts range from 0.25 s to 1.0 s."

The British Standard is not connected to IEEE-80, I agree. By the way, BS7430 Code of practice for Earthing [ch.19-20] it is more suitable for Substation Grounding, I am afraid.

__________________
Julius
Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#7

Re: Fault Duration For Ground Conductor Sizing

05/08/2013 9:12 AM

PW Slacks answer was correct.

Unfortunately too many people want someone else to do their work, buy standards, etc.

So gentlemen please first of all buy the proper and applicable standards.

Next if you are not an engineer or designer, then hire a specialist.

Otherwise the answers they will give you can be costly and could even cause damages to people and installations.

Reply
Member

Join Date: May 2013
Posts: 7
#8
In reply to #7

Re: Fault Duration For Ground Conductor Sizing

05/09/2013 2:55 AM

I think then there is no need of existence of CR4 at the first place. I thought this and similar type of forum are for sharing knowledge. No professional and sensible engineer will design as per the feedback from this forum unless and until he is sure about the source and reference.

Sorry PW Slack and vargaalex this is not the right place for you.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9

Re: Fault Duration For Ground Conductor Sizing

05/14/2013 12:00 AM

What is it for? Is it for relay setting or for ground conductor sizing or for earth mat design?

Reply
Anonymous Poster #1
#10
In reply to #9

Re: Fault Duration For Ground Conductor Sizing

05/14/2013 4:53 AM

It is for ground conductor sizing and earth mat design. Please go thru the question properly.

Reply
Reply to Forum Thread 10 comments

"Almost" Good Answers: