Hello Electrical Gurus

I have a question about star delta calculation. I will try and write all the information I have related to my question along with my calculations. But before I proceed I will like to make it clear that I will not be doing any installation or designing and this is just primarily for my own understanding.

Main Supply Voltage = 400V/3Phase/50Hz

Motor Power = 18.5KW (Condenser Pump) (Continuous Duty)

Ambient Temperature = 40C

Starting Method = Star Delta

Cable Installation Method = Conduit

Distance from the panel to starter = 1meter

Distance from the starter to motor = 20meter

I want to calculate the following,

a. MCCB

b. Cable size from main supply panel to starter and from starter to motor

c. Size of Main contactor, Delta Contactor and Star Contactor

d. Size of overload

My calculation

Full Load Current = 18.5KW/1.732*400*0.85*0.94 (0.85 = p.f and 0.94 = efficiency)

FLC = 33.42A (FLC I have obtained from ABB Motor Catalogue is 34A)

MCCB = 1.5*FLC = 1.5*33.42A = 50.13A

(I am confused on how to select the best MCCB rating. I mean like NEC states, if I am right to select MCCB at 2.5*FLC. What about IEC or BS7671?) I am trying to follow the BS7671

Cable size

From Panel to starter.

Cable size = 16mm (Table 4D2A 16mm cable ampere rating = 62A)

Applying derating factor at 40C we have 62*0.87 = 53.94A This is sufficient in my opinion. Keeping in mind I have a 50A MCCB installed.

Voltage drop

Starting current in star delta = 3*FLC = 3*33.42 = 100.26

Vd (Running) = 2.4*1*33.42/1000 = 0.08V (OK)

Vd (Starting) = 2.4*1*100.26/1000 = 0.24V (OK)

Cable Size from starter to motor

I will have 6 cables going from the starter to motor. Each set of cable need to be rated at 58% of the FLC. Therefore

Cable size = 0.58*33.42 = 19.38A ( From table 4D2A I have selected 4mm which has a 27A rated capacity)

Applying derating factor at 40C = 23.49A which is good

Voltage drop

Vd = 9.5*20*33.42/1000=3.68V (Which is good)

Main Contactor = 0.58*FLC = 0.58*33.42 = 19.38

Delta contactor = 0.58*FLC = 0.58*33.42 = 19.38

Star Contactor = 0.33*FLC = 0.33*33.42 = 11.02A

Overload = 0.58*FLC = 0.58*33.42 = 19.38A

I know there are a lot of calculations but can someone check them for me. Are they right? If not can you please highlight my mistakes and if its totally wrong can you please explain the calculation or point me to a good literature.

Many thanks

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Star Delta Calculation

05/20/2013 3:18 PM

Asking strangers to check these things is probably not a good idea. If someone gets hurt, you will be liable for your actions.

Wiring Regulations - BS 7671 - IET Electrical

Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: Star Delta Calculation

05/21/2013 12:21 AM

Do not confuse NEC with Bs or IEC,stick to one of them. For selection of contactor refer catalog of reputed manufacturer like Telemecanique or similar. CB selection should be done considering starting current and its duration as well as spike during changeover from star to delta,refer tripping curves(OL/SC).For sizing cable from starter to motor consider grouping factor and number of circuits enclosed in a conduit(BS7671)

__________________
pnaban
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Star Delta Calculation

05/21/2013 12:36 AM

Have you considered the magnetic release setting in the MCCB? If not, it might spuriously trip either during starting or during transition.

Also, if MCCB is the back-up device, your contactor ratings have to be reviewed as the short circuit I2t would be more with MCCB.

Why don't you simply follow the Type-2 Co-ordination based switchgear selection charts published by leading switchgear manufacturers like L & T, Siemens, ABB, etc.

Reply
Active Contributor

Join Date: Jan 2013
Posts: 11
#4

Re: Star Delta Calculation

05/21/2013 1:17 AM

NEC 430.52 mentions that the maximum rating of the Inverse time breaker should be 250%. So you can choose a breaker rating whose rating is less than 250% and more than 100% of the motor rated current.The breaker is there to provide protection against Short circuits.To protect the motor from over load Over load relays are provided

The breaker selected should be able to withstand the current developed during the change over from star to delta which is about 300 % for a few seconds.

It is better to go through the selection charts of a good manufacturers in Switching devices as they will provide the details for selecting contactors and breakers for different ratings of motors.

Reply
Member

Join Date: Jun 2013
Posts: 5
#5

Re: Star Delta Calculation

06/12/2013 9:27 PM

Based on your calculation of the Star Delta Starting Current you have used 3 times which is not correct. As it should used 4 time at 15 Sec.

Reply Off Topic (Score 6)
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); Lek (1); lyn (1); pnaban (1); songsaah (1)

Previous in Forum: UPS Input Connection Without Neutral   Next in Forum: Does This Circuit Make Sense for Variable Voltage to Constant Voltage?

Advertisement