UPS Input Connection Without Neutral

05/20/2013 9:18 AM

220V UPS input is mentioned as Line & neutral connection,But our system voltage is 3Ph,220Vac, so is it ok to connect L1 and L2 on UPS without neutral connection.

can expert give us some comments.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: UPS input connection without neutral

05/20/2013 9:20 AM

What does it say in the Manual that came with it?

What did the UPS manufacturer have to say during the telephone call to its technical helpline?

Is the output galvanically isolated from the input and what does the downstream wiring do in terms of earthing and the provision of an IT earth system?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: UPS Input Connection Without Neutral

05/20/2013 11:20 AM

If the UPS's case is electrically connected to the designated neutral input, hooking it up to your 220/3 supply will energize the case to ~127V, which is dangerous. Discuss with the mfr how this unit is grounded/earthed, and what modifications may be needed.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2012
Posts: 142
Good Answers: 14
#4
In reply to #2

Re: UPS Input Connection Without Neutral

05/20/2013 10:57 PM

Whilst I am not particularly au fait with US wiring rules, here in Australia it is expressely forbidden (and highly dangerous) to have any connection between the neutral and appliance casings at any point, or the neutral and earthing conductors at any point other than the main distribution board.

I would have thought that this would also be the situation over there, and as such there would be no appliances with a neutral connected to their cases on purpose.

I also question the assertion that the case would be energised even if the neutral were to be connected to the case, do you not have functioning earth connections that would immediately cause the CB/RCD to operate and so disconnect the supply if this were to occur? I assume that if the case is metallic (and the appliance not of class 2 configuration), then an earth connection to it would be a legal pre-requisite

I would have expected that a 220v single phase appliance such as a UPS would perform OK across two phases of the same RMS voltage (a motorised appliance would present a different situation), again, I am not up to scratch with your electrical system, so a bit of clarification would be appreciated.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: UPS Input Connection Without Neutral

05/20/2013 11:11 PM

The case ground connects to ground at the the distribution panel. The neutral connects to a neutral bar, to which ground wiring is also connected. Thus, indirectly at least, the neutral is connected to the appliance casing. If, in the OP's situation, an ungrounded L2 phase is connected to the appliance neutral, there will be a ground fault. If there are protection devices, the appliance case may be energized only momentarily. But still....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2012
Posts: 142
Good Answers: 14
#7
In reply to #5

Re: UPS Input Connection Without Neutral

05/20/2013 11:36 PM

I would expect that if the OP were to connect the 2 phases to the UPS rather than 1 phase and neutral, then a neutral connection back to the neutral bar from said UPS would not be made. How then can the case become energised at all?

Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: UPS Input Connection Without Neutral

05/20/2013 11:46 PM

Why not? If there is a case ground back to the distribution panel, and if there is a neutral also grounded there....

My main point was to be sure of what grounding provisions may (or may not) be on the UPS, and to be sure there are no conflicts.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #5

Re: UPS Input Connection Without Neutral

05/21/2013 3:24 AM

Only the OP knows whether the casing is metal or non-conductive. Only the OP knows whether a metal case is grounded or whether it is a double-insulated piece of equipment that doesn't need a ground. Only the OP can answer the questions raised so far.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#25
In reply to #5

Re: UPS Input Connection Without Neutral

05/30/2013 1:12 PM

The neutral at the input or output of the UPS?

Surely the source neutral is not bonded to the output. That would defeat the power factor correction, harmonic balancing, and isolation features for the UPS.

And would be a violation, to boot. There shouldn't even be a place to bring the neutral into the system and bond it to the output.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#18
In reply to #2

Re: UPS Input Connection Without Neutral

05/21/2013 8:28 AM

That should never, ever be true......but buying stuff from China means that it might be a good idea to check.

But even if you don't, it should drop off the breaker for that circuit....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Commentator

Join Date: May 2011
Posts: 61
Good Answers: 1
#3

Re: UPS Input Connection Without Neutral

05/20/2013 10:31 PM

Measure the voltage between L1 and L2, if it is 220 V +/- 10% then connect them to UPS.

Be insure that your system voltage is 3 ph 220 V ac.

In most of the contries, the system voltage is 3 ph 415 v ac. In this case, the voltage between L1 and L2 will be 415 v and your UPS may got damaged.

If you have 3 ph 415 V ac, connect one phase and neutral to UPS.

Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #3

Re: UPS Input Connection Without Neutral

05/21/2013 6:10 AM

...and what about the neutral connection from the N inlet terminal to the N outlet terminal? If they are connected through the UPS, then the outlet N terminal becomes live with no downstream circuit protection!

The forum is still awaiting information from the original poster, and to suggest the L1 and L2 connections in its absence is premature, at best.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2012
Posts: 142
Good Answers: 14
#19
In reply to #15

Re: UPS Input Connection Without Neutral

05/21/2013 8:31 AM

I gotta say that I have never seen a UPS with through connections of the mains input to output and would be interested to see a circuit diagram of one such beast.

They normally incorporate an isolating step down transformer to feed the electronics for battery charging and switching and then feed that DC to an inverter for either backup or continuous supply depending on type. Even the switchmode UPSs have double pole isolation.

Keeping the input totally isolated from the output and using electronics to clean up the waveform is one of the primary functions of a UPS in order to prevent line distortions from affecting the load, this is especially the case with line interactive and online types.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #19

Re: UPS Input Connection Without Neutral

05/21/2013 8:39 AM

Wonderful. So what equipment disconnects a phase-to-earth fault downstream of the unit?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2012
Posts: 142
Good Answers: 14
#21
In reply to #20

Re: UPS Input Connection Without Neutral

05/21/2013 9:24 AM

Most smaller UPSs are dedicated to one piece of equipment and their outputs are normally isolated supplies in that both active conductors are above earth potential. Therefore a phase to earth fault is no danger.

Larger UPSs designed to serve multiple appliances usually incorporate their own overload device, and most often these days, a core balance unit as well where one active of the output is tied to earth to form a neutral and to allow the RCD to function on earth fault.

Some larger units are routed via their own distribution board which has all of the necessary safety functions fitted there.

There may be through connected setups out there but it seems to defeat the purpose somewhat, and I suspect they would only be used for very specific situations (which I can't envisage). Would still love to see a circuit for one.

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#23
In reply to #21

Re: UPS Input Connection Without Neutral

05/21/2013 2:18 PM

GA.

Surprisingly I was the first....you should get more.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#6

Re: UPS Input Connection Without Neutral

05/20/2013 11:28 PM

It should not be connected. The neutral and body casing will have coupling capacitor which will not be rated to do duty with this kind of voltage applied to the neutral reference bus. Best way to go ahead is to provide 2 winding step up isolation transformer and tie the secondary neutral to ground and generate 220 volts phase to neutral voltage.

Register to Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#9

Re: UPS Input Connection Without Neutral

05/21/2013 12:18 AM

Another point. What about distribution downstream of UPS. The neutral point will be live. If only SP MCB is provided for isolating during maintenance of down stream circuits it will be a huge hazard. If not anything else, the idea itself is bad engineering.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #9

Re: UPS Input Connection Without Neutral

05/21/2013 6:14 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10

Re: UPS Input Connection Without Neutral

05/21/2013 12:38 AM

Is the input neutral terminal of the UPS connected to the casing (body)?

Register to Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#11
In reply to #10

Re: UPS Input Connection Without Neutral

05/21/2013 12:44 AM

Sorry, but where do you get equipments whose neutral terminal and body casing are directly connected to each other?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #11

Re: UPS Input Connection Without Neutral

05/21/2013 2:20 AM

That has not been suggested; instead, an indirect connection has been mentioned.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#22
In reply to #11

Re: UPS Input Connection Without Neutral

05/21/2013 10:57 AM

It's not uncommon to have a three wire feed into a four wire appliance like an oven. In that case, where the house wiring is hot-hot-neutral and the oven is hot-hot-neutral-grd, the neutral and ground are tied together in the box to the house. However, the box must have a good ground as the conduit and the flex-conduit from the oven must be connected securely to both the oven case and the box.

__________________
Most people are mostly good most of the time.
Register to Reply Score 2 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#14

Re: UPS Input Connection Without Neutral

05/21/2013 4:59 AM

"can expert give us some comments."

hold up people!! In answer to your question as quoted above.. NO!

Why?

Because whatever we say is pure conjecture on our part, as 1. we can't see what you'd got or done, 2. we are not experts in that type of unit, and 3. Why didn't you try the manufacturer first.

anyone answering this question cannot be correct and give up the ultimate answer to your problem. Only the manufacturer can!

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #14

Re: UPS Input Connection Without Neutral

05/21/2013 6:12 AM

GA

...and the forum is still awaiting the original poster's answers to a number of questions with this flavour.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#24

Re: UPS Input Connection Without Neutral

05/22/2013 4:54 AM

Dear Mr.mohamedihaiah

NO. You should not connect L1 and L2 and strictly the input voltage is to be perfectly matched.

DHAYANANDHAN.S

Register to Reply
Register to Reply 25 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!