Captive Transformer

05/24/2013 12:23 PM

Now I'm in doubt about how to feed a new installed 2500 KW, 6 KV, 60 Hz, 3600 rpm DOL start motor from existing switchboard connected to 12.5 MVA 115/6.3 Kv main transformer.

The plant running load now is about 8 MW, hence my worrying about possible disturbance during starting of this motor which will drive a process flow flouid which require DOL starting due to process requirements, therefore no soft start system is allwed.

I had been persuaded by some consultant to use a captive transformer with the secodary connected direct to motor terminal as good method to reduce the distribution circuit disturbance.

your comments about it should be gratefull

Bye

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Captive Transformer

05/24/2013 2:09 PM

Working with the incomplete information that you have provided yields the following "back of the envelope" scenario:

Your 12.5 MVA transformer can supply 1145 Amps at full load (a 0.8 pf is assumed for all calculations, and voltage drops are ignored),

Your present loading of 8 MW is about 915 Amps,

Your 2.5 MW motor draws about 300 Amps at full load.

Your other posts have indicated that the grid is unreliable, unstable, and results in severe disturbances to your processes because of switching transients and voltage sags. Now you want to know if it is ok to add 300 Amps of running current to a transformer that will be asked to handle 100 Amps above its rating under running conditions, and nearly 3 times its rating when this large motor is started.

For a much more structured answer you need to look at the one-line diagram, relevant parameters regarding the grid, transformers, loads, this new motor, and how and when your local generation is going to be used for voltage support; things that only you know.

I can only assume that the cost of the dedicated transformer is at issue, when in fact you should be concerned about the effect of this new motor on the overall plant electrical system regardless of how or where it is connected.

Perhaps you can share with us what your doubts are about the consultant's recommendations, then we'll have something to comment on.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#2
In reply to #1

Re: Captive Transformer

05/24/2013 11:19 PM

I will agree with RAMConsult about what he said, but will add that the reason for the dedicated transformer is to provide some isolation for transient protection but mainly to add impeadance to reduce inrush which will in effect produce a slightly softer start than across the line starting. I have had experience with motors around 30000 HP using isolation transformers but nothing as small as what you propose. It sounds like you have a very weak system. When I dealt with weak systems, I noted that the large motors always started better when everything else was running, particularly large inertia rotary loads. The other motors acted as generators during the voltage sag. This has nothing to due with the question but you need to analyze the loads connected and running when the motor is started. You also need to get full information about the power coming into the facility and do a complete system study. I have another question, is the 12.5 MVA the base rating and does that transformer have Fan (FA) or more rating? You have not mentioned what the transformer impeadances are.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jan 2013
Posts: 70
#6
In reply to #2

Re: Captive Transformer

05/27/2013 2:34 PM

4Wsilver

Thanks for your comments

Very interesting for me your information about your experience regarding large motors with large inertial constribution to reduce the effect of the voltage sag.

The 12.5 transformer are ONAN type, off-load tap changer (old version) 11% SC impedance.

Bye

Register to Reply
Commentator

Join Date: Jan 2013
Posts: 70
#5
In reply to #1

Re: Captive Transformer

05/27/2013 2:19 PM

Hi RAMConsult

It result very pleasant for me getting your comments.

The Captive transformer issue is another industry which are located far from the one of my former Post. In this case there are an strong system and the disturbance are such common for every grid in the world. Also no on-site generation exist because there are a 600 MW utility 5 KM far from the plant.

My doubts regading consultans recommendation was the cost-effective of captive transformer invesment and that after the 2500 KW motor installation the load is dangerously close to the transformer top capacities.

Thank a lot

Bye

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Captive Transformer

05/25/2013 8:13 AM

As RAMConsult said, here is a lack of lot of data:

System short-circuit power. I'll take it 1000 MVA

Transformer short-circuit impedance. I'll take it 11%

Motor p.f. and efficiency. I'll take these 0.85 and 90%

Motor p.f. at start. I'll take it 0.3

Motor Istart/Irat. I'll take it 6

Load p.f. I'll take it 0.85

In this case the steady state transformer overload will be only 30 A.

However, at start-when transformer is 8 MW loaded-and the supply voltage will be 6.3 kV[by reducing 115 kV to 6.3 kV at the source] and total current at transformer terminals is 2600 A[2.26 times the rating] the voltage at transformer terminal does not drop to less than 6.124 kV[even more than 6 kV rated.]

If the motor is supplied from the transformer with 3*120 sqr.mm 10/6 kV copper conductor 500 m length the voltage at motor terminal at start will be 5860 V[97.6% from motor rated voltage].

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Captive Transformer

05/25/2013 2:03 PM

I am curious as to why the process requirements would require DOL starting versus other methods.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Jan 2013
Posts: 70
#7
In reply to #4

Re: Captive Transformer

05/27/2013 2:52 PM

The reasons for not allowed soft start switches is because in continuous process is a common practice to have available one main pump in operation and other in reserve (spare) so in case of the main pump failure, the reserve shall start as fast as possible to maintain the process parameter in term of flow, pressure etc and so avoid plant trip

Bye

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: Captive Transformer

05/27/2013 2:59 PM

That rationale makes precious little sense.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: