Harmonic Filters

06/04/2013 6:10 AM

Good morning

This is regarding the design aspect of harmonic filter for Arc Furnace. The filter trips due to high 5th order harmonics in smooth operation of furance. My question is , if the filter is designed to and tuned to capture a particular harmonics 3rd or 5th or 11th. So it should irrespective of harmonics generated by the furance. ?

Is it correct or no ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#1

Re: Harmonic Filters

06/04/2013 4:51 PM

How does a filter 'trip'?

One might expect a circuit breaker to trip on overcurrent, but a filter?

Methinks we need a more fulsome desription of the problem if any meaningful answers are to be given.

__________________
paulusgnome
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: Harmonic Filters

06/04/2013 6:22 PM

Maybe it's clogged and needs to be changed, or cleaned.

OK, OK.

Just stirring things.

Register to Reply
Participant

Join Date: Jun 2013
Posts: 3
#3
In reply to #2

Re: Harmonic Filters

06/04/2013 11:06 PM

the capacitors of the filter are connected to bus through circuit breaker ,which trips. again my question is ,when the filter is designed ,the worst operation of furnace is kept in mind.if I have 250Hz filter , it should supress all 250Hz frequency , irrespective of the amount/severity of 250Hz harmonic. Is it correct?

Register to Reply
Guru
Hobbies - Musician - New Member Greece - Member - New Member

Join Date: Mar 2007
Location: Greece / Athens
Posts: 722
Good Answers: 28
#6
In reply to #3

Re: Harmonic Filters

06/05/2013 3:59 AM

An ideal notch filter should cut off a specific frequency (or a specific frequency range in the case of a band-reject filter) completely, no matter how large the input signal's amplitude is. However, in practice, any filter has a specific (large but finite) attenuation (e.g. 50db). So if the input signal is really large a small but significant amount will pass on the filter's output. So, when you design a filter you should take into consideration the larger possible input signal (worst case) and the maximum accepted output signal, in order to find out the (minimum) attenuation that your filter should have.

__________________
George
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10
In reply to #3

Re: Harmonic Filters

06/05/2013 11:31 AM

It depends on the magnitude of the disruptive current created by the harmonic.

If the filter is not sized large enough to handle/dissipate the generated harmonic current by the application it will not operate correctly.

There could also be a failed or inferior component of the filter assembly that is causing the issue.

If this is a factory designed and supplied filter assembly; you would be wise to contact the manufacturer and verify the assembly is the correct one for your application.

If it is the correct unit for your application; I would suggest starting with analyzing the capacitors in the filter for proper microfarad rating/performance and verify all resistors are of the correct impedance.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#4

Re: Harmonic Filters

06/04/2013 11:27 PM

Take it easy, guys!!

The early transmitters in the 1920s or so, were driven by carbon arc. The arc has an inherently negative portion of its characteristic. It drives the generation of the Radio Frequency for the transmission.

Since it is inherently nonlinear, plenty of harmonics are generated.

SO IS IN A FURNACE. The fellow is correct, so far.

So, the question remains about the design of the filter, before further discussions are sensible.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#5

Re: Harmonic Filters

06/05/2013 2:58 AM




+



+



=

50Hz 5th Harmonic 250Hz 7th Harmonic 350Hz Distortion

If a capacitor is faulted, surely this will cause the imbalance on the busbars and cause the trip due to not filtering at the correct frequency.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Harmonic Filters

06/05/2013 6:22 AM

Well, discuss the matter with the filter manufacturer by telephone, then.

Or is that the 7th harmonic of the bleedin' obvious?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: Harmonic Filters

06/05/2013 8:11 AM

Is it a tuned filter or a de-tuned filter?

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#9

Re: Harmonic Filters

06/05/2013 9:11 AM

There are some filter basics needed to be understood.

1,. They reflect the considerable energy (20-40%) of the harmonics back into the furnace, to better efficiency.

2,. They prevent not permissible high harmonic current on the power grid.

3,. Any filter stage can do only so much dampening / reflection from harmonic to harmonic. Hence multistage filters are normal. A 90% reduction in energy (from the fundamental frequency) to the 3rd per stage is ordinary.

4,. The higher the Q quality of the stage, the higher the filtering. At the same time the voltage or current stresses are multiplied on its components by the same Q multiplier. That sets rather sharp limits on applicable Q.

5,. Components, in particular capacitors need to be protected from excessive currents, hence the OP's mention of the 5th harmonic breaker tripping. That may happen for a reason, all right. But, OP needs to make some measurements with some real test equipment, to know which way to proceed.

Harmonic filters are rather complicated in their construction and behaviour. A breaker on - light on, breaker off - light off approach to troubleshooting is wholly inadequate.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#11
In reply to #9

Re: Harmonic Filters

06/05/2013 7:55 PM

leveles, I made a comment on another question by this poster several days ago, that he should be seeking other help with his issues. Arc furnace control is an art and should be handle by those who know these systems.

Your comments were spot on!

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); fixitorelse (1); G.K. (1); IQ (1); leveles (2); lyn (1); panthripu (1); Paulusgnome (1); PWSlack (1); SHOCKHISCAN (1)

Previous in Forum: 110V ,60HZ on 220V ,50HZ Supply   Next in Forum: IT System Dedicated Transformer

Advertisement