1.2 MW Generator

06/05/2013 9:12 AM

Hi Guys,

We have a team of guys that service our generators, every time we need to use it though there is something wrong with it or something fails. We are on a small island in the Caribbean so good help is hard to find. Please can someone help me with a detailed checklist for monthly inspections, checklist for offline and online tests, etc. We are approaching hurricane season and this is becoming quite a concern for us. Please could you also guide me in what checks I could do to make sure we are good to go in the event of a power failure. Your help here is greatly appreciated as usual. Thank you in advance.

-Rob.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: 1.2 MW Generator

06/05/2013 9:35 AM

The maker of the generator, unknown to the forum is the best source of this information.

Since you give no useful information, guessing is the next step.

Contact the maker, or go on line and look at their web site.

They should have all that on their site.

Register to Reply Good Answer (Score 4)
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#2
In reply to #1

Re: 1.2 MW Generator

06/05/2013 9:58 AM

Hi Lyn,

The generator is a Cummins Onan KTA-50-G3 480/60 1250KW Maranthon. I have tried to reach out to the manufacturer but have had no response as yet. I was hoping that there was a general check list that I could follow and one that the service guys could follow. Like when a car is inspected. I cannot even get a service or operators manual on this, I have searched everywhere.

Any help here is appreciated. Thanks.

-Rob.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: 1.2 MW Generator

06/05/2013 10:03 AM

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #2

Re: 1.2 MW Generator

06/05/2013 10:21 AM

TType the name and model # into a search engine and you will be able to download manuals maintenance, and trouble shooting guides.

I'm on a phone, or I'd do it for you.

Virtually anything you need to know can be found, if you just search.

If you have a teenager around, just ask them to do it for you. They'll have all the information you need in no time at all!

Good luck.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#5
In reply to #4

Re: 1.2 MW Generator

06/05/2013 10:29 AM

Thanks Lyn and PWSlack, I will try this again. I hope you are all well.

-Rob.

Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#6

Re: 1.2 MW Generator

06/05/2013 10:36 AM

There is a good company out of the BVI, PM me if you'd like. I suggest you team up with other users with similar issues and hire a tech. You may have to send him to a factory school for training. In general, diesel gensets should be tested at least monthly. Critical systems, servers, computers, electronics, should be on battery or UPS. Fuel contamination both deliberate and "natural" is a big issue.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7

Re: 1.2 MW Generator

06/05/2013 1:13 PM

Did you keep a log of what failed and how it was fixed? Have you tried starting this generator periodically regardless of need or do you test if it works only when power has been lost. You have to put in some effort to maintain this backup machine.

I would start by running this generator once a month with at least a 10kW load on the generator with your coolant at operating temperature for 15 minutes. Only once you've done this six months in a row without a start up failure would I consider extending this testing cycle to six weeks, two months, six months and finally yearly. If this generator fails only when needed but operates fine when tested, you have to consider what is different between your monthly tests and your "in need" operation.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#8
In reply to #7

Re: 1.2 MW Generator

06/05/2013 2:25 PM

Hi Redfred,

I have only been in my new position here for two months now. This generator was down for 5 months before it was finally fixed a month ago (Limping along in my books). They are running two governors on the unit as the one has failed, the #5 fuel injector is leaking, the silencer needs welding, the ATS batteries need replacing, and I am sure there are more issues. I have just recently had a master mechanic flown down which costed about $10k for the whole trip, he got it running to where it is now and I will get the parts needed to fix the rest, however once it is fixed I would like it to stay that way, hence the urgent need for a detailed check sheet. Does anyone reading CR4 have such a list that they check monthly?

Thank you everyone for your time here, it is much appreciated.

-Rob.

Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#9

Re: 1.2 MW Generator

06/05/2013 11:49 PM

Where I used to work, the generator was a necessity for ventilation primarily. One lab got full lighting. The card access system got put on the generator and a few items of convenience until we ran out of capacity.

20 minute no load tests were run daily. The only no start conditions were because a mouse got hungry and ate a PC board and no fuel.

Full load testing does add a power glitch so it wasn't done.

Register to Reply
2
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#10

Re: 1.2 MW Generator

06/06/2013 8:37 AM

I searched for - Diesel Generator Operation and Maintenance - came up with this...

http://cumminspower.com/www/literature/technicalpapers/PT-7004-Maintenance-en.pdf

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11
In reply to #10

Re: 1.2 MW Generator

06/06/2013 9:29 AM

Nice find and a GA.

Who would've thought that a search engine could find such a document. I wonder how likely it is that it would also be found among the manufacturer's technical pages.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#12

Re: 1.2 MW Generator

06/06/2013 3:53 PM

Thank you everyone for your input here, it has helped tremendously! I hope you are all well.

-Rob.

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JWthetech (1); KeepItSimpleStupid (1); lyn (2); PWSlack (1); redfred (2); Robotech (4); Tom_Consulting (1)

Previous in Forum: IT System Dedicated Transformer   Next in Forum: 69kV:12.47kV Dy1 Transformer Paralleling

Advertisement