MPCB for Star Delta Starters

06/06/2013 4:26 AM

Dear Experts,

While using the Siemens Type 2 Coordiantion chart for selecting MPCB for star delta starter, it was found that no MPCB ranges are given for star delta starting.
It shows a circuit breaker and a conventional Bi-relay combination.

Is it not advisable to use MPCB's for star-delta starting.of motors.

Does anybody know what is the reason...?

Thanks

Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#1

Re: MPCB for Star Delta Starters

06/06/2013 5:44 AM

It is very likely because the price to develop a digitally controlled starter for such arrangement is way too big, compared with the traditional starting methods.

And, depending on the power of the engine and application, likely very unnecessary.

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Reply Score 1 for Off Topic
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: MPCB for Star Delta Starters

06/06/2013 9:38 AM

This has nothing whatsoever to do with electronic controls.

An IEC style MPCB (Motor Protection Circuit Breaker) which incorporates the disconnect, short circuit and adjustable thermal overload protection in one unit, is intended to feed the motor starter as the first device from the line source. So the motor thermal overload setting must be for the motor nameplate Full Load Amps.

But when you use Star Delta starting where you take advantage of using 6 leads to the motor, you typically place the thermal overload protection in only one part of the windings going through just 3 of the leads, set to 58% of the nameplate FLA of the motor, because that current flows to it the same whether it is in Star or Delta mode. This way, the overload protection sees and reacts to both the true starting current and the running current on a cumulative basis.

If you use an MPCB ahead of the entire stating/running contactor set, the starting current is not being correctly tracked, it is only going to see starting current (Star) as a fraction of the total current, yet the trip settings will be based only on the full current (Delta). The true cumulative heating effects of the starting current then are not properly included in the trip curve of the overload protection.

So for example, if the motor was turned off when it was over loaded (but not yet tripped), when you restart it, the added thermal stress of starting is not properly tracked and may allow the motor to be restarted when it should have tripped, resulting in it being damaged, which is exactly what the thermal overload is supposed to prevent.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 5)
Anonymous Poster #1
#3

Re: MPCB for Star Delta Starters

06/07/2013 3:28 AM

Thank you all...

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: MPCB for Star Delta Starters

06/30/2013 7:25 PM

Because it might spuriously trip during transition from star to delta.

Reply
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); electronick (1); JRaef (1)