Generator Issue Continued...

06/24/2013 6:10 PM

Hi Guys, I was wondering if anyone could give me some useful input here. I am still having an issue with the generator I mentioned in an earlier post and my guys are stumped. Please see their report below, any advice here is appreciated. Thank you in advance for your time and effort.

Interim report on the generator The initial problem on this unit was "under frequency shut down fault'. Preliminary investigation revealed that there was water in the fuel system. This was caused by someone removing the two-inch plug from the main bulk tank man- hole cover, thus causing rain water to enter the fuel tank. Three (3) inches on water found in the bottom of the tank when a test was carried out. After the use of the bulk tank was discontinued, the fuel delivery pipes were redirect from the other building daily service tank. This did not solve the problem. The electrical systems and wiring were checked and no abnormalities were found.

A Cummins engineer was contacted and he recommended that we conduct a series of tests, these tests include, Fuel pressure at no load and full load. Actuator DC voltage monitoring while unit was on load. Fuel solenoid was monitored for voltage loss during operation on load Fuel inlet restriction and return pressure. With all this tests, everything was checked top be in order, yet we could not get more than one to two hours run from the unit on load.

Then Kimble Company was called in to assist. All tests that were already conducted on the unit were redone. A full load dump test was conducted, this involve switching off the unit while running on line , then restarting to check if the unit regain control of the load. The engine failed twice on this test. Kimble then recommended that we change the high pressure fuel pump, the mechanical fuel pump and the actuator. In addition, they also change all the electrical boards in the Power Command control panel. These include; Engine interface board Customer interface board Digital board Analog board The Governor control and the PT/ CT module were also changed. A load test was performed on the unit and the same failure occurred after one hour. After several months of trial and error, the unit would run and stop on the same fault. We installed a new DST tank with all new delivery pipes to the standby. Several on line test produced four (4) and five (5) hours runs from the unit.

After the unit was deemed ok, it was only after GEBE had a failure we would know that this problem still exists. Then it was notice while working one day on the generator that vibration was affecting the Power Command Control that sits on the alternator panel. The control was relocated and some of the pins connectors at the back of the panel were repaired. We then got four (4) and five (5) hours run from the unit on load. But the problem was still there. We had numerous shut down on many different occasions on the same fault.

Then Electec Company was called in to assist. All the electrical connection were checked, they thought the problem was the 'MPU' magnetic pick-up. This component was check by us and Kimble many times. After several on line tests with Electec supervising, the unit failed every time after one (1) hour. Then Mr. Vincent Commock was called in to assist. All tests and checks, both mechanical and electrical were re-conducted on the unit. The fuel solenoid was changed. A number of on line test was conducted on the unit, but did not yield any success, Commock narrow down the problem to be the governor control after some more electrical checks. Commock then incorporated a second governor control from a NTTA-855 - G generator. He connected the actuator and fuel solenoid valve to the second governor and also tapped in to the MPU. With this second governor added, the unit ran for six (6) hours and then eleven (11) hours respectively. Commock made recommended in his report that we should replace the original governor on the unit. A new governor was installed and the second governor disconnected. We then conduct an online test on the generator which revealed that the problem is still there even with a new governor installed. The second governor was reconnected.

The problem needs further investigation. The unit was not designed to run on two governors. The side effects when running on two governors are still not known. We do know that start up fuel pressure is very high; the second governor does not ramp up in speed. We also discover lately that on two occasions, the unit did not transfer when there was a GEBE failure; instead, the engine hunts in speed and does not reach sixty (60) hertz.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Generator Issue Continued.......

06/24/2013 6:30 PM

zzzzzzz...synopsis please..

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #1

Re: Generator Issue Continued.......

06/24/2013 7:40 PM

It still doesn't work right.

He's desperate and I don't blame him. New gen sets are expensive.

No clue here. (Does that surprise anyone)

Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#4
In reply to #3

Re: Generator Issue Continued.......

06/24/2013 7:46 PM

LMAO, I really am Lyn! Not winning here with what we have tried so far....

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Generator Issue Continued.......

06/24/2013 7:50 PM

Sorry, I really hope you get it solved, and that it doesn't cost a bazillion dollars.

Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#6
In reply to #5

Re: Generator Issue Continued.......

06/24/2013 8:07 PM

Yes indeed! Put it this way, if we don't sort this out soon and we get nailed by a tropical depression, we are going to find ourselves up the creek with no paddle lol!

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10
In reply to #6

Re: Generator Issue Continued.......

06/25/2013 2:19 AM

Sounds like you need a better troubleshooting technique.....as a passing comment.FWIW

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User
Hobbies - Musician - New Member Technical Fields - Technical Writing - New Member

Join Date: May 2010
Location: Upstate NY
Posts: 278
Good Answers: 5
#2

Re: Generator Issue Continued.......

06/24/2013 7:17 PM
__________________
LakeGrl
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#7

Re: Generator Issue Continued.......

06/24/2013 10:17 PM

Rip out all the expensive electronics and go back to a good old fashioned all mechanical governing system.

At least then you have real screws to turn that make it 'better or worse'.

Now for the system you have has anyone ever checked the sensor that measures the actual RPM's or line frequency to see if it is getting any interference or drift that shows up after running for a while?

Register to Reply
3
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#8

Re: Generator Issue Continued.......

06/24/2013 11:41 PM

Obviously, the motor and generator set are capable of running and typically operate for around an hour before the cumulative impact of the "fault" causes shutdown.

Thus we can conclude the motor, generator and control gear are probably in reasonable order.

I suspect that it is something to do with total load versus nameplate versus expected load.

I would sugges that if possible you partition the system into BALANCED quarters of the total load and run the generator supplying only one of those segments while the grid is used to operate the balance of the facility. Do this for a prolonged time (a few days). Purpose: To confirm system stability, fuel pumps, motor cooling and all that stuff.

Once that is proven, add another 25% of the system load and run for a couple of days. Purpose: To verify the capability of the motor/generator set and also confirm no load anomally in that section.

Then add another 25% of the system load and then incrementally move to full load condition.

I truly suspect that peak load of the system and the dynamic capacity of the generator is not matched and at those random moments when every A/C unit, motor, clutch and conveyor just happen to turn on simultaneously it's just too much and the protection systems do their job.

Just a guess!!! from JAE.

__________________
Just an Engineer from the land down under.
Register to Reply Good Answer (Score 3)
5
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9

Re: Generator Issue Continued.......

06/25/2013 12:05 AM

Good story but nobody seems to have taken advantage of all the features of the PCC (Power Command Control) and the Amp Sentry. I'd be interested in utilizing the logging function to see the pre- and post-fault status indications, and I'd be looking really closely at the settings on the Amp Sentry, especially the Under Frequency Shutdown (81u) settings. It's adjustable from 0-10 Hz below nominal governor setpoint, for a 0-20 second time delay, default is 6 Hz, 10 seconds, though it sounds to me that it's set way too tightly, like 0 Hz and 0 seconds. With settings like that any burp in the speed is going to take you out.

You also skirt the issue of the ATS and if it plays a part in the problem. Regarding the two governor "solution"; it may have bypassed the Amp Sentry trip because it was probably connected outside of the PCC, so it wasn't "influenced" by all the magic going on in the electronics there.

What started as a mechanical/fuel problem should have been solved by flushing out the entire fuel system from tanks to injectors, I think at this point you should be looking at what initiates the trip function; is it truly an under frequency trip, if so, then what are the conditions that lead to it. Time for an electrical engineer with a Transient Data Recorder on-site, the parts swappers have had their turn.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 5)
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#13
In reply to #9

Re: Generator Issue Continued.......

06/25/2013 10:48 AM

I made a mental assumption that they were monitoring the output/load.

That should be day-one stuff for any contractor (in-house electricians/engineers for that matter). How would they know the whole story if they don't know the demand? (rhetorical)

Part swappers....haha...good one (we call them 'black-box-technicians').

Register to Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#11

Re: Generator Issue Continued.......

06/25/2013 4:31 AM

Have you added any bulk load recently (like fire hydrant pump) or high capacity DOL operated compressor etc. These bulk loads could even be 1/5th the capacity of the DG set but on starting these loads, the D.G may not have the capacity to maintain the starting current requirements until the load achieve the full speed. Is the D.G rated for prime duty or standby duty? Please consult with the D.G manufacturer regarding performance of D.G with these high inertial loads if such a situation is present at site.

Otherwise I will go with RAMConsult answer.

Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#12

Re: Generator Issue Continued.......

06/25/2013 8:41 AM

Hi Guys,

You have all given me some very interesting and useful information here, I am going to hand this over to our Chief Electrician and see if he has checked the points mentioned and try what you have suggested.

Thank you all for you time and responses. I hope you are all well.

-Rob

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#14

Re: Generator Issue Continued...

06/25/2013 11:24 AM

The question to be clarified here is the generator protection system prematurely or properly trying to prevent the generator from being damaged? Under frequency conditions imply to me that the engine cannot provide enough energy for the mechanical load applied to it. There are engine related things (water in fuel, sticking throttle, dirty air cleaner) that might be a mechanical problem here but tracking the electric load will quickly clarify which side of the equation is the problem.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#15

Re: Generator Issue Continued...

06/25/2013 5:43 PM

Troubleshooting can be a b*tch. Without some kind of logging capability that you can revert to and examine data for a periodic or random failure it can be a whole lot bigger b*tch. You don't need too much time resolution or detail, you just have to determine between two events every time, which happens (or starts happening) first. That's more likely to be the cause, or a step closer to cause. Finding an obvious or not so obvious pattern of events that triggers the failure is also a good hint. Exchanging parts can help ONLY if you are certain that any adjustments are correct. My two (euro) cents. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 62
Good Answers: 5
#16

Re: Generator Issue Continued...

06/25/2013 10:45 PM

The reason the Cummins engineer told you to do a fuel pressure reading at two different speeds was for a very good reason.

Diesel fuel acts as a sort of lubricant. In consistency, it is more oily than gasoline, although it does act as a sort of mild solvent.

Diesel engines more often than not operate on compression of the fuel/ air mixture, rather than combustion from a spark.

This requires a very, very high fuel pressure, in *all* of the cylinders.

Water inherently makes a poor lubricant.

This is why water in the crankcase can lead to a seized engine (I have seen it before).

Water in a modern, sophisticated high pressure diesel fuel pump will do the same thing. If it seizes due to lack of lubricity, or even rust, the starter motor will break it free- but it will forever be down on much needed fuel pressure. Which is why diesel engineers are so careful to put water seperators in their fuel systems.

If your high pressure fuel pump was damaged by the water/fuel mixture, the engine is going to have a hell of a time getting up to proper speed, or staying there under load.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#17

Re: Generator Issue Continued...

06/25/2013 11:06 PM

Write to agents/manufacturers to rectify,if they refuse/fail sue them.

__________________
pnaban
Register to Reply
Power-User

Join Date: Jan 2010
Location: Atchison Village
Posts: 383
Good Answers: 39
#18

Re: Generator Issue Continued...

06/25/2013 11:55 PM

Emulsified water in the injection pump.

__________________
Align culture with nature...
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#19

Re: Generator Issue Continued...

06/26/2013 2:02 AM

Sorry to say, that the notes since Ramconsult have all a likelihood of validity.

If ever there was a need to break out sensors and do longer term recording of events, this is it. From experience, in hindsight, the recordings are all logical.

Otherwise, we all keep wild guessing. THAT is then expensive.

Register to Reply
Member

Join Date: Jul 2008
Posts: 5
#20

Re: Generator Issue Continued...

06/26/2013 2:10 AM

Hi Robotech,

We had a similar experience, which we overcame.

I tried to post a response but it seems I am blocked for some reason. maybe my reply was too long!

Owen

Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#21
In reply to #20

Re: Generator Issue Continued...

06/26/2013 10:12 AM

Hi Owen,

Thanks for the reply, I have sent you a message with my email. Your help is greatly appreciated.

Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#22

Re: Generator Issue Continued...

06/26/2013 10:19 AM

Hi Everyone,

One of our guys just found a wire that was disconnected, our ATS is now functioning properly, however the genset is still not able to run for prolonged periods of time.

Thanks once again for all your help guys.

Register to Reply
Participant

Join Date: Jun 2013
Posts: 1
#23

Re: Generator Issue Continued...

06/26/2013 10:27 AM

My experience is in the automotive repair industry for 33 years as Master ASE certified Tech, shop owner and manager. The most wierd and difficult electrical problems to diagnose and repair were poor continuity on clustered ground wires connecting computers, sensors and power systems. I would recommend checking resistance on all your ground circuits. Any high resistance causes sensor readings to go off scale and trigger shutdown events, phantom fault codes and erattic performance. Hope this helps. E. Green.

Register to Reply
Power-User

Join Date: Nov 2011
Location: St Maarten, Netherlands Antilles
Posts: 126
Good Answers: 1
#24
In reply to #23

Re: Generator Issue Continued...

06/26/2013 11:00 AM

Thanks Mr. Green, I will check that out.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#25

Re: Generator Issue Continued...

06/26/2013 4:23 PM

My vote goes with "Just an Engineer" - system overload, protection kicks in.

(1) make sure all groundings are done properly, we seem to get these so-called labelled "ground faults" on some of our gas turbine gensets, and they can induce a trip condition.

(2) verify that all equipment connected to this is designed for the output of the generator as to frequency, voltage, etc.

(3) you need to have enough monitoring equipment on this to be able to see average and instanteous load, and try running a test with various sectors in the plant on shut-down.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 11
Good Answers: 1
#26

Re: Generator Issue Continued...

06/26/2013 5:07 PM

If the generator always indicates an under frequency fault after all the work you have done so far, I would suspect the devices that are used to determine frequency i.e. a tach or circuit board monitoring the generators sine wave to be at fault. Perhaps it is temperature related as you seem to experience many different run times.

Good Luck !

Register to Reply
Member

Join Date: Jul 2011
Posts: 6
#27

Re: Generator Issue Continued...

06/27/2013 2:34 AM

Don't know if this would help...we had a similar problem..small diesel generator. Experts stripped the engine and put it back together..three times. Until I noticed the exhaust stack outside above the generator room. There was hardly any smoke. The muffler and extended pipe were choked with soot. The moment they were disconnected the engine was back to running normal. Perhaps back pressure. regards.

Register to Reply
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

CEG (1); cuba_pete (1); James Stewart (1); JB of NM (1); Just an Engineer (1); LakeGrl (1); leveles (1); lyn (2); Mntho24 (1); ormondotvos (1); OwenSmart (1); Pattabhiraman (1); pnaban (1); RAMConsult (1); redfred (1); Robotech (6); SimpleMind (1); SolarEagle (2); tcmtech (1); tundrawolf (1)

Previous in Forum: Motor Current   Next in Forum: Responsibility of Main Intake Substation

Advertisement