Hi Guys,
I was wondering if anyone could give me some useful input here. I am still having an issue with the generator I mentioned in an earlier post and my guys are stumped. Please see their report below, any advice here is appreciated. Thank you in advance for your time and effort.
Interim report on the generator
The initial problem on this unit was "under frequency shut down fault'. Preliminary investigation revealed that there was water in the fuel system. This was caused by someone removing the two-inch plug from the main bulk tank man- hole cover, thus causing rain water to enter the fuel tank. Three (3) inches on water found in the bottom of the tank when a test was carried out. After the use of the bulk tank was discontinued, the fuel delivery pipes were redirect from the other building daily service tank. This did not solve the problem. The electrical systems and wiring were checked and no abnormalities were found.
A Cummins engineer was contacted and he recommended that we conduct a series of tests, these tests include, Fuel pressure at no load and full load. Actuator DC voltage monitoring while unit was on load. Fuel solenoid was monitored for voltage loss during operation on load Fuel inlet restriction and return pressure. With all this tests, everything was checked top be in order, yet we could not get more than one to two hours run from the unit on load.
Then Kimble Company was called in to assist. All tests that were already conducted on the unit were redone. A full load dump test was conducted, this involve switching off the unit while running on line , then restarting to check if the unit regain control of the load. The engine failed twice on this test. Kimble then recommended that we change the high pressure fuel pump, the mechanical fuel pump and the actuator. In addition, they also change all the electrical boards in the Power Command control panel. These include; Engine interface board Customer interface board Digital board Analog board The Governor control and the PT/ CT module were also changed. A load test was performed on the unit and the same failure occurred after one hour. After several months of trial and error, the unit would run and stop on the same fault. We installed a new DST tank with all new delivery pipes to the standby. Several on line test produced four (4) and five (5) hours runs from the unit.
After the unit was deemed ok, it was only after GEBE had a failure we would know that this problem still exists. Then it was notice while working one day on the generator that vibration was affecting the Power Command Control that sits on the alternator panel. The control was relocated and some of the pins connectors at the back of the panel were repaired. We then got four (4) and five (5) hours run from the unit on load. But the problem was still there. We had numerous shut down on many different occasions on the same fault.
Then Electec Company was called in to assist. All the electrical connection were checked, they thought the problem was the 'MPU' magnetic pick-up. This component was check by us and Kimble many times. After several on line tests with Electec supervising, the unit failed every time after one (1) hour. Then Mr. Vincent Commock was called in to assist. All tests and checks, both mechanical and electrical were re-conducted on the unit. The fuel solenoid was changed. A number of on line test was conducted on the unit, but did not yield any success, Commock narrow down the problem to be the governor control after some more electrical checks. Commock then incorporated a second governor control from a NTTA-855 - G generator. He connected the actuator and fuel solenoid valve to the second governor and also tapped in to the MPU. With this second governor added, the unit ran for six (6) hours and then eleven (11) hours respectively. Commock made recommended in his report that we should replace the original governor on the unit. A new governor was installed and the second governor disconnected. We then conduct an online test on the generator which revealed that the problem is still there even with a new governor installed. The second governor was reconnected.
The problem needs further investigation. The unit was not designed to run on two governors. The side effects when running on two governors are still not known. We do know that start up fuel pressure is very high; the second governor does not ramp up in speed. We also discover lately that on two occasions, the unit did not transfer when there was a GEBE failure; instead, the engine hunts in speed and does not reach sixty (60) hertz.
Good Answers: