Big Area Air Conditioning

06/24/2013 6:36 PM

Hi Friends,

We are going to transfer a former bowling alley into a factory for small gadgets.

So far no big problems except everything that could be carried away has been stolen. Yes, even the High and low voltage 500 MCM cables have been cut from the transformer and been pulled out of the pipes.

I need your advice about the HVAC.

Should we go with a chilled water system or just regular AC unit(s). Even these have been stolen and nobody knows even what tonnage was designated to this building.

The climate is like South Florida. We look for the most economic solution, but chilled water systems are not tested here yet.

The building is one box, the roof has torch on roofing on top of P.U panels.

About 25 % has 9 Ft ceilings (Offices)

Dimensions are 180 X 180 Feet by 20 Feet high. When fully occupied there will be 100 persons doing light work in clean room environment.

Thank you for all the help. D

__________________
Plenty of room here
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Big area Airconditioning

06/24/2013 6:54 PM

Well the first thing I would get is.....

I would go with 20 ton package units, chilled water would work but be expensive and if it breaks down, nobody has air....You would need about 10 units...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#6
In reply to #1

Re: Big area Airconditioning

06/24/2013 11:46 PM

Hi SE,

For the dogs it is too late now. And they poisoned one of my shepherds. G.A.

Do you think 10 unit of 20 tons are necessary? I was hoping to clean it up with maximal 50 tons for everything. What has Costco and Walmart (small store)on the roofs?

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: Big area Airconditioning

06/25/2013 1:42 AM

You could lower the heat load considerably by putting a dropped ceiling in(8'), with insulation 4" above tiles....The 20 ton units are 2-stage units which enable the units to be able to recover quickly in the mornings after being off all night....It also provides some back-up if a compressor should fail in one of the units, you can just just switch 1st stage to good compressor....With minimal machinery and activity you could cut heat load to around 80 tons...In this case I would go with 5 ea 20 ton 2-stage cooling....This is the strategy of most large stores...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#20
In reply to #7

Re: Big area Airconditioning

06/25/2013 9:21 PM

Any idea of the costs of operation in terms of kW or tons per area? Most HVAC systems I have seems are oversized. There are some weird thumb rules like the 400 and 600 SQFt per ton. Tks. D

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Big area Airconditioning

06/24/2013 6:59 PM

There are on-line calculators you can use, or go to the site below for a complete rundown.

F28 Residential Cooling and Heating Load Calculations

Never been a fan of chilled water, myself.

Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: Big Area Air Conditioning

06/24/2013 9:06 PM

put my vote on 410A package units I'd use Lennox and give each one an address and it could be monitored anywhere in the world through a pc

Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#4
In reply to #3

Re: Big Area Air Conditioning

06/24/2013 10:53 PM

I checked the website and these guys come with 20,5 seer. Seems to be very good?

Thank you Fredski.

__________________
Plenty of room here
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#5
In reply to #4

Re: Big Area Air Conditioning

06/24/2013 11:40 PM

The 20.5 was probably a commercial stunt from one of the vendors. In the catalogs I only found 16 as best number until now. (In the 1,5- 5 ton series)

I found that they also have bigger units.

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#8
In reply to #4

Re: Big Area Air Conditioning

06/25/2013 8:18 AM

they have a line that's rated closer to 18 Seer I would recommend before the 20. these machines are outstanding and have a proven track record for reliability and parts are more abundant than the

Strategos line

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9

Re: Big Area Air Conditioning

06/25/2013 8:21 AM

a couple of things. you said a "clean room environment". clean rooms are a specialty that require a lot of planning and more than a few bucks to build and maintain, are you sure this was the phrasing you intended?

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#13
In reply to #9

Re: Big Area Air Conditioning

06/25/2013 6:17 PM

Well, that's how they prefer to call it here.

The reality is that it will be a class 7. (a little bit better than your kitchen)

This part, will be bought prefab, probably in the USA and assembled here. The HEPA filter inlets will be connected to a duct system and 7.5 HP blower- air-handler per clean room (25 X 70 X 9 Ft). Initially 2 rooms, extendable to 4.

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#16
In reply to #13

Re: Big Area Air Conditioning

06/25/2013 7:16 PM

you mean in place of a ceiling tile like these?....using the ceiling as a charged plenum?http://www.cleanroomspecialists.com/products/documents/MicroSoundFilter.pdf

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#17
In reply to #16

Re: Big Area Air Conditioning

06/25/2013 9:08 PM

Hi Fredski,

This is about what one clean room supplier offers. It is from the company "clean room supply" or supplies. Some come with fan motor, others don't. These have a inlet collar

that connects to ducts, (for no fan types) under higher pressure to overcome the filter resistance, or when a fan is in the unit regular duct work, because the fan does the job.

In the first example all the ducts receive the air - most from recirculation - through the air handler again and boosted with the 7.5 HP turbine to feed 12 to 16 of these ceiling fixture filters.

We try to not expose the HEPA to air with too many impurities (dust), because of the maintenance work and cost.

The ceiling is a hard panel version that is completely sealed in a aluminum framework, designed for that purpose.

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#19
In reply to #17

Re: Big Area Air Conditioning

06/25/2013 9:19 PM

"We try to not expose the HEPA to air with too many impurities"

Pre-filter the air upstream of the HEPA filter. You probably knew that.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#21
In reply to #17

Re: Big Area Air Conditioning

06/25/2013 9:56 PM

I've worked clean rooms for many years, from the lab at Loctite to manufactures of hard drives, and even balloon catheters for the medical world. there is no "rule of thumb for sizing one of these specialty rooms. usually only a smaller room is dedicated to actual "clean room duties". a bowling alley is a huge room! these rooms have special needs, problems, certifications. besides your ultra high local humidity and temperature, maintaining a positive room pressure at all times will be critical to keep foreign particles from entering you room. I hope you're working closely with an expert on your room so you don't flush good money down the drain.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#10

Re: Big Area Air Conditioning

06/25/2013 8:27 AM

I like the idea of cutting the heat load on the building with drop celings, just be sure to add some sort of venting for the dead air space. There are many new and repurposed buildings that are using layers to shield the building from the sun.

Some use solar sheilding to reduce heat on the sides because it makes your insulation (or lack of) work better.

Others use ivy and trellis for a green look, I also like green roofs but with a drop celing it would be less benefit (you can get away with using a white surface).

Drew K

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#14
In reply to #10

Re: Big Area Air Conditioning

06/25/2013 6:39 PM

The building is a square box with walls and almost no windows. It is build with concrete blocks and has isolation on the inside.

__________________
Plenty of room here
Register to Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#24
In reply to #14

Re: Big Area Air Conditioning

06/26/2013 1:00 PM

If it seems cool compared to outside in the middle of the day it is probably ok, but you can almost always do more. In the long run reducing your heat load in the summer will save you energy. If you are in a tropic climate that doesn't ever see cool weather, you might consider extracting air from next to high temp or high wattage equipment that way you vent your heat outside.

My Dad once sealed a fridge into a door so that it blew it's heat outside instead of into the house.

Drew K

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#11

Re: Big Area Air Conditioning

06/25/2013 10:40 AM

Using a chilled water system is going to require a big outlay of cash from the get-go, but will pay off with time. If you really think you can make a go of it with your new business then it may be the way to go. I am not trying to be pessimistic, but the reality of the market may not be in your favor. (I really am pessimistic.) You have to have the space to put all of the equipment required, as well (chillers, pumps, towers, etc.) You have a pretty small building, but it still comes under consideration.

The installation of chill water piping will either require a raised floor (plenum) or a system that would really benefit from a drop ceiling. The others have mentioned this as an effective way to keep the cool where you want it.

Outside of the building envelope, you would probably benefit from a battened roof layer. These types of roof structures can be installed easily, but again, require an outlay of cash that you may not see back in savings for years. Plus, you have to consider your location. High winds can heavily damage these types of roofs.

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#18
In reply to #11

Re: Big Area Air Conditioning

06/25/2013 9:16 PM

Thank you.

Can the cooling towers be made of PVC or PE tube? How can I prevent the chilled pipes inside the building from gathering condensate and dripping down? I had an idea when chilling to 4 degrees Celsius, this will happen?

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#25
In reply to #18

Re: Big Area Air Conditioning

06/26/2013 2:00 PM

Cooling towers made of pipe? I don't follow...

The "chilled' water doesn't have to be all that cold, especially with the temperature ranges you posted. 4 Celsius is pretty cold! You should only need about 8 or 9 C, but this is going to vary dependent on the dynamic load (work hours vs. non-work hours).

Insulation/cladding for the pipes. Drip pans and drain lines (evap pans) are usually necessary for those just in case events (say you open the place to outside air/humidity to move goods/equipment in and out). Breakout points in the runs will also develop condensate.

Register to Reply
Commentator

Join Date: Aug 2010
Location: Austin, TX
Posts: 80
Good Answers: 8
#12

Re: Big Area Air Conditioning

06/25/2013 11:31 AM

If you are going to build a cleanroom environment, you will most likely need to control for humidity as well, which will most likley require a system of 100% outside air or make-up units and a combination of interior recirculation units that only perform sensible cooling (I'm assuming thre will be some exhaust). Using 20 ton DX units to maintain humidity control, especially in a high humidity environment like the Bahamas, will be very difficult. I think you should not rule out chilled water.

Can you tell us more about the process that will occur within the building? It is important for understanding your AC needs.

__________________
Some standards are like the North Pole and some are like Mecca. People use both to get their sense of direction, however, only one is a preferred destination. - P.E. Scheibmeir
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#15
In reply to #12

Re: Big Area Air Conditioning

06/25/2013 6:44 PM

We need 50%- 60% relative humidity and 72 - 78 degrees Fahrenheit.

__________________
Plenty of room here
Register to Reply
Power-User

Join Date: Sep 2007
Location: I am located in Mumbai,India.
Posts: 125
Good Answers: 2
#22

Re: Big Area Air Conditioning

06/26/2013 1:57 AM

The HVAC designing needs with proper professional input.

The process needs to be studied for requirements of fresh air and any pollutants being generated. Requirements of clean room needs to be satisfied.

You need to follow standards like ASHRAE 55 for comfort conditioning, AsHRAE 62.1 for indoor air quality and ASHRAE90 for energy standards.

Proper design will ensure good and healthy working conditions. This will result in increased productivity, and save money in operation of the system by reduced energy consumption.

__________________
Rajesh
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#23
In reply to #22

Re: Big Area Air Conditioning

06/26/2013 9:00 AM

he\s in the Bahamas, I doubt he's bound by AHRAE but he could certainly use their recommendations as a guideline depending on what product he intends to assemble/produce.

Register to Reply
Power-User

Join Date: Sep 2007
Location: I am located in Mumbai,India.
Posts: 125
Good Answers: 2
#26
In reply to #23

Re: Big Area Air Conditioning

06/27/2013 1:11 AM

The ASHRAE guidelines will ensure proper and healthy working conditions as well as energy saving. Any problem solving after the systems are designed improperly and implemented would be very costly affair.

__________________
Rajesh
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#28
In reply to #26

Re: Big Area Air Conditioning

06/27/2013 11:49 AM

Thank you for the good advice.

The facilities and procedures will be all with ISO certificate and also FDA inspected and approved. All regulations will be respected, since productivity and sales can not be compromised.

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#29
In reply to #28

Re: Big Area Air Conditioning

06/27/2013 2:58 PM

FDA?? what are you planning on making??

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#31
In reply to #29

Re: Big Area Air Conditioning

06/27/2013 4:20 PM

artificial body parts?

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Sep 2007
Location: I am located in Mumbai,India.
Posts: 125
Good Answers: 2
#34
In reply to #31

Re: Big Area Air Conditioning

07/25/2013 9:35 PM

I have recently qualified as "Accredited professional" with Indian Green Building Council.

Presently I am involved in the commissioning of a 5 star hotel here in India.

It would be of interest to me to follow/contribute in this project of yours. I have also experience of designing FDA approved air conditioning facilities for Johnson & Johnson India where I was working for 27 years in engineering maintenance and projects.

__________________
Rajesh
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2009
Location: Kansas, USA
Posts: 748
Good Answers: 64
#27

Re: Big Area Air Conditioning

06/27/2013 11:11 AM

I would also add an Alarm System to the Systems that is tied to your security monitoring program. If the units are moved or the power is cut to them the alarm sounds, immediate vicinity horns as well as to police or security services.

There are a number of them on the market that work well and it may at least limit your loss. Also post signs letting people know the facility and the equipment is security monitored.

__________________
One of the greatest discoveries a man makes, one of his great surprises, is to find he can do what he was afraid he couldn't do. Ford, Henry
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#30
In reply to #27

Re: Big Area Air Conditioning

06/27/2013 3:05 PM

good advice. several years ago a group of meth-heads were working the Orange county area stealing every inch of copper drain line they cut rip out, a couple of months later they came back and had taken a Sawzall and took out all the condenser coils., so at first I was bombed with water leak calls, then no cool calls. a lot of monitoring systems were installed after the second hit.

Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#32

Re: Big Area Air Conditioning

07/25/2013 6:47 PM

I think you would be best to do a dropped ceiling with insulation. I calculated about 95 tons of cooling needed before the dropped ceiling. You will save money in the long run with a dropped ceiling, and also probably pay for it with the savings from not having to purchase 5 - 20 ton units. I would still have an HVAC contractor give you a bid on both with and without a dropped ceiling.

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#33
In reply to #32

Re: Big Area Air Conditioning

07/25/2013 7:12 PM

Thank you,

Your input is very much appreciated. D

__________________
Plenty of room here
Register to Reply
Register to Reply 34 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cuba_pete (2); Drew K (2); dvmdsc (12); facilitiesmgr (1); Fredski (8); lyn (2); MrGeneRall (1); Original_Macgyver (1); rsalaskar (3); SolarEagle (2)

Previous in Forum: Pipe Pressure Withstand   Next in Forum: Blower Air Pressure at Open Area

Advertisement