How to Adjust Power Factor When Two Generators Are Running Parallel

06/26/2013 10:21 AM

how to adjust power factor when two generator are running parallel

one generator is showing .6 other generator is showing 0.99, load is same ,voltage is same,ampere is different on both generator depends on load

Register to Reply
Pathfinder Tags: Power Factor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: how to adjust power factor when two generator are running parallel

06/26/2013 10:41 AM

One at a time.

Register to Reply
Power-User
Engineering Fields - Petroleum Engineering - Rig Electrician United States - Member - the Oil Patch Engineering Fields - Power Engineering - Drives & Gen's Engineering Fields - Instrumentation Engineering - Drive Control Popular Science - Cosmology -

Join Date: Jan 2010
Location: Houston off/on-shore @ Oil Patch
Posts: 223
Good Answers: 2
#2

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/26/2013 12:46 PM

whats your KVAR meter say? nevermind, turn up the voltage on the generator that's got the lowest amp untill the amps are =. or turn down the voltage on the one that's high, whatever it takes to keep the volts near where you want them

__________________
Why do they make manhole covers round? so they won't fall in [before asking "Who is John Galt?"]
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#3

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/26/2013 12:56 PM

If ampere [sic] is different then load is not the same. That is why your PF is different for each generator.

Either the voltage needs adjustment, control and/or sense circuitry is out of whack, you have a load difference being seen by one of the generators, or your generators are not manufactured to a very close tolerance.

There are many other reasons, but these are easy to check.

Are your meters calibrated?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/26/2013 2:06 PM

You haven't told us if you're operating in "Island" or "Grid connected" mode, the size of the machines, and the nature of the load. As you have discovered, raising the voltage/power factor/reactive power on one machine causes an equal and opposite reaction on the other, typical when you have two controllers trying to regulate one variable without any coordination between them.

The first thing you need to do is RTFM (Read The Fine Manual), then enable "Paralleling" or "Cross Current Compensation" in your AVRs (Automatic Voltage Regulator), and adjust the settings accordingly.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#5

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/26/2013 11:21 PM

Greetings -

RAMConsult's comments are good.

In the questions about your system.

1. Is this a new installation ?

2. Was one of the generators added to an existing installation ?

If so, the existing generator voltage regulator may not have paralleling provision.

3. Is this running in parallel with the grid ?

4. A generator runs at it's lowest amp's (coolest) when at Unity Power Factor, it is best to have both generator voltage regulators connected together (cross current compensation) when run in parallel, especially if the load is changing. It is also best to regulate Power Factor vs Vars, if the load is changing, a wrong Var setting as you see will cause the amps to be off.

5. Sometimes the generators are run by a controller independent of either generator, the controller determines load and vars from each generator, and can cycle gens to equalize operating hours.

6. NEVER switch modes with the generator running and under load unless the manual approves of this. NEVER open the excitation to a running under load generator. NEVER open a CT circuit when the generator is running under load. Even worse - NEVER - close the excitation circuit of a generator whose breaker is closed to the grid. NOTE: Some companies have done this as a paralleling method, but it is very hard on the machinery.

7. Do you have a Sync Check relay for paralleling ?

Reverse Power relay to open the breaker if power is lost ?

Over-Under Voltage, Over-Under Current, Loss of Excitation, ... ?

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Register to Reply
Active Contributor

Join Date: Jul 2008
Location: India
Posts: 18
Good Answers: 1
#6

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/26/2013 11:32 PM

Specify whether the power factors are lagging or leading and whether the panel has auto synchronizing and auto load sharing modules. For manual sync nd load sharing machines, generally you need a proper droop adjustment for equal KVar sharing. It is always better to individually load the machine to 80% of its capacity with inductive load and adjust all the parameter including droop of both the machines equal. For this, run the machine single and adjust the no load parameters with zero droop setting. Then, load the machine individually to 80% of its capacity with inductive load and adjust the speed droop by governor nd voltage droop by AVR to 4%. Note: both the machines should be adjusted precisely to equal parameters. And most importantly, neutral breaker of only bus connected machine should be close while, neutral breakers of incoming machine should be open to avoid circulating current. Hope this article would be helpful to you. All the Best!!!

__________________
Quality is never an accident; it is always the result of high intention, sincere effort, intelligent direction and skillful execution.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2013
Posts: 3
#7

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/27/2013 6:51 AM

hi gurus

extremely sorry for late reply

observed generators running individually ,found one generator is taking 150ampers more than other two generators and also the generator which is taking more amper

Register to Reply
Participant

Join Date: Jun 2013
Posts: 3
#8

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/27/2013 6:58 AM

and one more thing....

the ACB removed and checked the terminals at bus bar side having black carbon deposit.is it possible due to which it is taking more ampere, pls adivise

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #8

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/27/2013 1:05 PM

Now you are talking about 3 generators?!

Your observational report is not helpful. If you run each generator on its own, with the same exact load attached, you will notice the same power output!! The amps reading by themselves do not help us to understand your problem. You need to make a table where each generator's data are logged in, (volts, Amps, P.factor: Volts and amps for each phase, and the rpm of the genset or the frequency as read).

In any case, you need to adjust each genset voltage output separately before trying to synchronise them (in pairs I presume, from your 1st input). Then you must check what type of load sharing equipment you have and how to set them. If the 3 gensets are of the same capacity each, then they will be set to share the load equally.

Depending on the precision of the equipments, you might have to live with some circulating current (imbalance).

Better stil, get an expert to do the job at least once for you to learn the procedure for your setup.

Register to Reply
Participant

Join Date: Jun 2013
Posts: 2
#9

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/27/2013 12:00 PM

depending on how the power is generated, transmissioned and distributed...

with digital energy, you would have modules like those in object oriented programming...

these physical models would have to be speced and schematiced to work under various inputs, transformations and processes, and outputs...

increase amperes velocity and storage capabilities would increase the power factor...

perhaps techniques such as proton core amperes injections, geometric infinity loops capacitors black holes and superconductivity materials would help...

Register to Reply Score 1 for Off Topic
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#11
In reply to #9

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/27/2013 3:03 PM

I'll have some of what this guy is drinking!

Digital energy? Does that come in fits and bursts?

Speced and Schematiced...? Wouldn't that be Schematified? [sic...really sic]

If I increase the amperes velocity, does the retro-encabulator decrease the velocities of the voltages in direct inverse proportions? Especially when taking into account the storage capacities of greater electron densities?

I mean, with proton core injection...it kind of goes without saying here, but, infinity loop capacitors, ball bearings, and some 3-in-1 oil...everything should smooth out.

Right?

Hurry up, I need to turn in my homeworks!!!

Register to Reply Score 1 for Good Answer
3
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#12

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/28/2013 12:22 AM

Hi,

Assuming that the problem still persists..

SESHA REDDY - Please note that the Power Factor is governed by the Characteristics of te Load ( Resistive, Inductive and Capacitive Loads), and it has nothing to do with the generators when operated in solo mode.

But In the Synchronised Mode of Operation the PF or KVAR shows the Load Sharing between the Alternators, hence becomes very Improtant.

As a Thumb Rule - The gensets in Synchronised conditions should be loaded to the equal % of their Capacity, this is irrespective of the rating of the Alternator / Generators. i.e say you are synchronising two gensets of 1000 kVA and 500 kVA, and the Load is 1200 kVA, now both the gensets should be loaded to 80 % of their Rated Capacity.

This is known as Load Sharing between the generators. The Load sharing between the Engines (kW Sharing) is achieved by adjusting the Engine Speed Droop, where as the Load Sharing Between Alternators (kVAR / PF) need to be adjusted with the Help of Voltage Droop Pot on the AVR.

The conditions for Synchronising needs to be precisely set..

Voltage of Alternators ( Measure with One Instrument)

Speed of Engines / Freq of AC Voltage

Phase Sequence

After Meeting the above conditions, you need to set the Droop Pot ( Voltage and Speed).

Load the generators is SOLO mode for atleast 80 % of the Rated Capacity with the Worst Inductive Load, Increase the Voltage Droop with the Help of Droop Pot on the AVR, this means the Voltage will Droop (Reduce) from the set value to alteast 4 %, similarly set the speed Droop to 4 %. Repeat the same with all remaining gensets to be synchronised.

Please note that the Error is setting the Voltage Droop and Terminal Voltage will lead to Different PF / kVAR of the Alternators. So set the same very carefully.

Now once the basic conditions for Synchronising is met and the Droops are adjusted correctly, Synchronise the gensets and start loading..

Causion -

1) Neutral of Mater to be Earthed and the Neutral od Slave to be kept open / Floating

2) Attenmpt No Load Synchronising, if you are attempting this for the First Time, observe the Circulating Current, This Circulting Current should not be more than 4 % of rated Current of the Lowest Rated Alternator.

Do it systematically and carefully, if in doubt stop, relook, correct & go ahead..

Take Care..

Register to Reply Good Answer (Score 3)
Anonymous Poster #1
#13
In reply to #12

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/28/2013 12:35 AM

This is exactly what Develop Service quoted. And this is the basic procedure for synchronising.

Register to Reply
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#14

Re: How to Adjust Power Factor When Two Generators Are Running Parallel

06/28/2013 9:39 AM

it may have some default from the generator´s output´s to the respective load, and you may want to check that.

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); CoronaCameraMan (1); cuba_pete (2); Develop Service (1); electronick (1); kwcharlie (1); LAA_Lucke (1); lyn (1); mostadorthsander (1); RAMConsult (1); SESHA REDDY (2); vishram lele (1)

Previous in Forum: Battery Charging in Parallel   Next in Forum: Connecting Generator and PCC

Advertisement