Generator 200kva Cummins/Stamford Alternator

07/03/2013 10:29 AM

This generator runs fine with a small load of lighting and some small 3 phase motors up to 20 amps, when we load it with other equipment of not more than 30 to 50 amps, we encounter high revs and the generator cuts off on an alarm, over load. I have changed the Smartgen controller checked all electrics what I can. But revs up and cuts out on alarm

Register to Reply
Pathfinder Tags: generators
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: generator 200kva cummins/stamford alternator

07/03/2013 10:36 AM

Sounds like it's time to phone Cummins/Stamford and arrange for a Service Technician to call in.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: Generator 200kva Cummins/Stamford Alternator

07/03/2013 11:36 PM

200kVA set should not run at 20 A load.Consult manufacturers regarding recommended minimum load for it.

__________________
pnaban
Register to Reply Score 1 for Off Topic
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: Generator 200kva Cummins/Stamford Alternator

07/04/2013 10:39 AM

New machine or in service for awhile?

New problem or there from the beginning?

If it is a new problem on a machine that has been is service for awhile; Has there been any faults/failures or maintenance performed on the machine recently?

The generator engine should not be increasing the speed if the overload is real rather an overload would cause the engine to slow down due to the mechanical loading.

I would check the engine speed control as higher revs result in increased power frequency which will in turn will cause the Volts/Hertz ratio to be out of limit hence the generator protection circuitry will see an overload condition and trip.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Participant

Join Date: Jul 2013
Posts: 4
#4
In reply to #3

Re: Generator 200kva Cummins/Stamford Alternator

07/05/2013 1:53 AM

machine been in service for a while(190 run hours)

New problem, no others prior to this one

machine never been touched for maint or other faults, recently prior to fault.

Replaced the speed control and Smartgen control unit

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5
In reply to #4

Re: Generator 200kva Cummins/Stamford Alternator

07/05/2013 3:47 AM

Speed control = Governor:

- What type: mechanical or Electronic?

It looks like the loop gain has gone wrong: When there is load demand, the fuel is increased by the governor to maintain the rpm constant as set. if the Gain is too high, the reaction will be too fast and too much for a small increase in load ( This is for both types). Check the Governor setting manual for any gain adjustment that might be available on the model. This needs some knowledge of the subject on servo mechanism and the particular governor.

Register to Reply
Participant

Join Date: Jul 2013
Posts: 4
#7
In reply to #5

Re: Generator 200kva Cummins/Stamford Alternator

07/30/2013 4:53 AM

managed to get another governor and replaced old one , sorted problem out, thanks for advise

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: Generator 200kva Cummins/Stamford Alternator

07/30/2013 4:22 AM

Check also that the new unit is programmed the same way as the original. If it is set to reverse acting and the original is direct acting, for example, that feature alone would produce the behaviour indicated in the original post.

Find the manual and/or call the manufacturer for advice.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jul 2013
Posts: 4
#8
In reply to #6

Re: Generator 200kva Cummins/Stamford Alternator

07/30/2013 4:55 AM

settings set the same as old controller, changed the governor as an option and by doing so, this sorted out the problem. thanks

Register to Reply