Slip Ring Induction Motor- VFD Starting

07/05/2013 4:51 AM

In a plant there is a Induction motor, earlier it was started using liquid rotor starter for three years and it was running successfully but before three months the starter has been changed to VFD. And in the course of three months only the stator has burnt!

I want to know what could be the possibilities that has caused this.

suggestions are most welcome.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 6:47 AM

One of the possibilities is that the overload protection device was set incorrectly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Associate

Join Date: Jul 2007
Location: São Mamede Coronado - Portugal
Posts: 27
Good Answers: 3
#2

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 7:23 AM

Check if the motor was designed for converter supply. If not, this is the reason for the failure.

The insulation system of the motor is subjected to higher dielectric stress when converter fed than in the case of a pure AC sinusoidal source. The voltage stress level exceeded the insulation system voltage stress level at the motor terminal.

Beware when rewinding the motor, the new stator winding insulation must be redesigned, special care should be taken about the conductor and inter-turn insulation.

__________________
Best regards, SMCTR
Register to Reply Good Answer (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 7:34 AM

It sounds like it would be better to junk the motor and purchase a replacement rated for inverter duty.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jul 2007
Location: São Mamede Coronado - Portugal
Posts: 27
Good Answers: 3
#4
In reply to #3

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 7:47 AM

Depending on the motor power, purchase a newone designed for converter supply might be the better solution...

__________________
Best regards, SMCTR
Register to Reply
2
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#12
In reply to #2

Re: Slip Ring Induction Motor- VFD Starting

07/08/2013 12:42 AM

Friends,

I believe that SMCTR has given the answer closest to the reason. In the past, I worked for a city's water/wastewater utility department. We put VFD's on at least 6 slip-ring motors with liquid resistors--"flow matcher" brand. We had zero problems with them because we always included 3% load reactors between the VFD and the motor.

Because VFD's operate with a high-frequency (called the carrier frequency) to do the switching of the output IGBT's, there is a high-frequency signal embedded into the output waveform. When the wires carrying this signal meet the motor's windings, the significant difference in wire impedance causes the voltage to reflect back. This doubles the effective voltage seen at the motor and is the source of premature motor winding insulation failure. Such failures are almost always in the first few turns of the winding in the stator. "Inverter Duty" motors are designed and built with stator winding insulation capable of handling this higher effective voltage.

Solutions to this problem include

  1. Buying an inverter-duty motor,
  2. Buying and installing a load reactor (probably 3%, but 5% may be needed),
  3. Buying and installing an active filter for the carrier frequency,
  4. Buying and installing an impedance matching transformer sized for the voltage and current.

Of these, #2 is usually the most cost-effective.
As others have mentioned, make sure that your shorting of the motor's rotor occurs at the slip rings on the rotor, so the brushes are removed.--John M.

Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#15
In reply to #12

Re: Slip Ring Induction Motor- VFD Starting

07/09/2013 8:53 PM

"...We put VFD's on at least 6 slip-ring motors with liquid resistors--"flow matcher" brand....."

Heh, Flomatcher. They are still around believe it or not. I went in there a few years ago to try to talk to them about soft starters for their stator power, I don't think there was any technical person in that building that was under 70 years old. Those guys make a good product, but they are milkling the limits of that technology to the bitter end.

And they continue to insist that VFDs are an abomination!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#16
In reply to #15

Re: Slip Ring Induction Motor- VFD Starting

07/09/2013 10:05 PM

Jraef,

Good evening to you. Those flomatchers had a lot of mechanical components that all had to work together for the drives to run. However, they are the quietest variable speed drive that I have ever seen and they are infinitely variable in speed.

Mechanical components, let me count the ways--

  1. slip rings, brush holders, and brushes (3 sets each),
  2. salt solution tank with three electrodes,
  3. air compressor and bubbler for measuring liquid level,
  4. salt solution in sealed storage tank, pressurized by the air going to the bubbler,
  5. radiator and pump to keep the salt solution from boiling, and
  6. piping and filters for all the above--had to resist the salt solution corrosion.

Plus the normal electrical components for all of this, including safeties, starters, etc. And don't forget, mandatory regular maintenance (at least 1x per month if not weekly or daily).--John M.

Register to Reply
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 7:50 AM

Read this, particularly the section on soft starters and slip ring motors http://www.lmphotonics.com/slipring.htm

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 9:44 AM

looks like someone with enough knowledge to be dangerous decided to adapt the wrong control in the wrong application. your slip ring is a very high torque motor that requires specific resistances to start and run properly, a VFD simply is the wrong choice for this application, you were offered an excellent link in another response I suggest you read and UNDERSTAND it before throwing away more money and burning up a perfectly good motor due to ignorance

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#14
In reply to #6

Re: Slip Ring Induction Motor- VFD Starting

07/09/2013 6:51 PM

Fredski,

On this one, I have to strongly disagree with your concern. Although you raise a very valid point regarding loads that are of high torque and/or high inertia (at least for soft starters, but not so much with VFD's), the application that is being discussed in this thread is a pumping application which is neither high starting torque nor high inertia. I read many (most) of the references posted in this thread and in them the application of a VFD for booster pumping to constant pressure or lift station pumping is considered a very good VFD conversion from a wound-rotor motor with liquid resistor speed control on the secondary. As I noted in another post, I have done this very application with zero difficulties a number of times.

Thanks--JMM

Register to Reply
Participant

Join Date: Jun 2013
Location: Philippines
Posts: 4
#7

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 11:56 AM

If your motor is an inverter duty it can withstand the new challenges presented by a vfd, but if it is not, it may fail both electrical and mechanical in nature. Regarding insulation, because of the type of output generated by vfd, temperature rise in the winding may increased which causes great stress upon insulation. For every 10degree celsius rise, the insulation is Reduced to half and if it rises too high, the motor will overload and burned-up in a short time . What have actually burned-up your stator is the positive harmonics which rotates in the direction of the rotor.

Register to Reply
Associate

Join Date: Jul 2007
Location: São Mamede Coronado - Portugal
Posts: 27
Good Answers: 3
#8
In reply to #7

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 12:10 PM

Acceptable reply in general, but some confusion bringing the insulation resistance concept to this discussion.. it is not helpful for evaluate the real problem...

__________________
Best regards, SMCTR
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 1:45 PM

The most common problem in applying VFDs to older motors is that whoever considered this concept got cheap at the last minute and decided to ignore the issue of voltage stresses added to the winding insulation. Newer motors now take this into account, but it was never a concern on older ones. It could have been effectively mitigated at the time of the initial installation, but would have cost more money.

For some reason people do this a lot. It's like buying a classic car that needs Premium gas, but you get cheap and put in Regular, then the engine burns up. It's not the fault of the engine or the gas, it's the person at the pump.

If you are having the motor rewound, insist that they use inverter rated magnet wire, that is a minimum first step now. I would also recommend purchase of a sine wave filter on the output of the VFD, or at least a motor terminator to absorb any voltage spikes.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#10
In reply to #9

Re: Slip Ring Induction Motor- VFD Starting

07/05/2013 4:09 PM

agreed. This might help those that would ike a more detailed explaination explainationhttp://www1.eere.energy.gov/manufacturing/tech_assistance/pdfs/motor_tip_sheet14.pdf

Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2013
Posts: 8
#17
In reply to #10

Re: Slip Ring Induction Motor- VFD Starting

04/23/2014 11:26 AM

We have had problems from 3 phase, slip ring motors recently (stator/rotor winding damage) switching to Inverter duty motors is probably not an option. We have also damaged at leas one drive, possibly a second. Motors are 270kw, 480V, 3phase. Line reactors used @ motor circuit disconnect sw. Any thoughts would be appreciated. Im no way a master on this subject. Thanks.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#18
In reply to #17

Re: Slip Ring Induction Motor- VFD Starting

04/23/2014 5:05 PM

Many people ignore old threads like this, you should start a fresh one, and in it, describe the damage you speak of in more detail both to the motors and the VFDs, and describe the application. Give us some clues to work with.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Member

Join Date: Oct 2013
Posts: 8
#19
In reply to #18

Re: Slip Ring Induction Motor- VFD Starting

04/23/2014 5:50 PM

Thanks for the reply. I figured on that, and I attempted to start a new thread, chock-full of details, data, info, and such. Either the server was having problems or maybe I was doing something wrong, either way I couldnt post the thread. I will try again later.

Register to Reply
Commentator

Join Date: Aug 2008
Posts: 82
#11

Re: Slip Ring Induction Motor- VFD Starting

07/06/2013 11:08 AM

Inverter Duty motors - how are they mentioned in name plate ? As I don't know , request for assistance , please .

Register to Reply
Active Contributor

Join Date: Jul 2013
Posts: 11
#13

Re: Slip Ring Induction Motor- VFD Starting

07/09/2013 2:21 AM

What is the application and rating of motor and VFD? Slip ring secondary is shorted or what?

I also implemented VFD in slip ring motor for crane application

Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Fredski (2); jmueller (3); JRaef (3); Nono (1); PWSlack (2); Ritz11 (1); sivaa (1); SMCTR (3); steeler1 (2); TonyS (1)

Previous in Forum: Electrical Saving Equipment   Next in Forum: PSM, PMS, and TMS

Advertisement