Transformer Oil

07/09/2013 4:51 AM

50 kv bdv for oil suitable for 220 kv transformer?

or at what rate does bdv of oil increases with rating of transformer?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: transformer oil

07/09/2013 6:06 AM

A1) Why would it be suitable if its bdv is less than 25% of what is required (rhetorical question - NNTR)?

A2) Ask the oil and transformer manufacturers.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Transformer Oil

07/11/2013 3:08 PM

Yes, 50kV dielectric breakdown voltage should be acceptable for use in a 220kV transformer, assuming other characteristics of the oil are acceptable (including specific gravity, acidity, interfacial tension, moisture content, dissolved combustible gases). The BDV is usually a measure of the moisture and other contaminants in the oil, and 50kV is well above the ASTM D-1816 and D-877 test limits.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3
In reply to #2

Re: Transformer Oil

07/11/2013 10:59 PM

Is there a chart to read the BDV strength of oil for various voltage levels (6.6,11.33,66,132,275,400,500,750kV) of transformer.

__________________
pnaban
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #3

Re: Transformer Oil

07/12/2013 8:16 AM

Breakdown strength doesn't necessarily relate directly to transformer voltages. It relates to the electrode type and gap used in the BDV test apparatus. ASTM D-877 is the older test method, using flat, coin-shaped electrodes spaced 2.54mm (0.1") apart, and "passing" BDV is 30kV. The newer D-1816 uses electrodes with rounded surfaces, at a 1mm or 2mm gap. There are differences in the acceptable values of BDV for different voltage ranges (for NEW oil), and also depends on the electrode gap used. See the following link for more explanation. However, although the BDV value is part of the equation, the rest is in the "thickness" of oil (it's more than 1 or 2mm !) the transformer manufacturer has designed for when he located the energized components in the transformer tank.

Based on a D-877 test, the OP's BDV is quite acceptable. Based on D-1816, the OP's BDV is acceptable if this is in-service oil. Overall, I would probably accept this oil test value for use, unless it were brand new oil (fresh from manufacturer) and the test was the D-1816 @ 2mm. Then I would expect the BDV to be better.

http://sdmyers.com/techcorner/tech-2009-12-18-dbvt.html

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply