Help required on selecting Underground cable

06/02/2007 3:39 AM

My house is about 110 meters from the Electrical Supply point. It is connected by a 50Sq mm Underground 3 1/2 Core Aluminum Cable. The Line Voltage is 220 - 230 V. The Full load would be about 40 KVA. How much Voltage Drop is expected ? Do I need to strengthen the existing cable by another one of 35 Sq mm ??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Dec 2006
Location: Randburg, South Africa
Posts: 10
#1

Re: Help required on selecting Underground cable

06/03/2007 3:42 AM

40kVA at 220V gives about 182A. If you have the specific resisteance of Al you can do your own voltdrop calc.

I would suggest you use a 400/380V 3-phase supply and take some trouble to balace the load at the Distribution Board. This means you have 105A per phase. You may need a single core neutral in addition to the existing cable to cover for unbalanced load.

__________________
Wessel Pieters
Reply
Active Contributor

Join Date: May 2007
Posts: 10
#2

Re: Help required on selecting Underground cable

06/03/2007 7:39 AM

If you want to continue with 220V, 1-PH supply atleast another 2x35 sq.mm Al. cable is required for 40KVA load. The voltage drop in this case will be about 14V at 182A (40 KVA). Alternatively. if a 2x50 Sq.mm Al. cable is laid the voltage drop will be about 12V.

For all good reasons, it is better to go for a 400V, 3-PH supply with the existing load almost equally balanced (in each phase). In such case, the existing 3 1/2 core cable is enough and the voltage drop will be only about 4V at full load.

Reply
Anonymous Poster
#3

Re: Help required on selecting Underground cable

06/03/2007 3:59 PM

In your case you will have no drop unless the transformer is very old and connected to two other residences in you immediate area as a transformer willl usually deliver 100 to 200 AMP loading to up to three homes at a time.

Reply
Active Contributor

Join Date: May 2007
Location: Vermont and Alaska
Posts: 24
Good Answers: 3
#4

Re: Help required on selecting Underground cable

06/03/2007 5:03 PM

-You will definitely need 2x50 Sq mm aluminum cables with that kind of load. As near as I can tell 50 Sq mm AL cable is only rated for 115A. Running 2ea 50Sq mm cables in parallel will allow you to "pull" up to 230A.

As noted previously you will also reduce the voltage drop by 50%.

Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#5

Re: Help required on selecting Underground cable

06/03/2007 8:32 PM

Are you sure it is 40KVA? If really so, (hard to believe) you will need additional cable. Instead of investing in more Aluminum cable, throw it away go for Copper, and three phase system. You would be much better off.

Wangito.

__________________
Never trade luck for skill.
Reply
Participant

Join Date: May 2007
Location: Dubai
Posts: 2
#6

Re: Help required on selecting Underground cable

06/04/2007 4:34 AM

Hi;

I had checked the BICC data table for 4 Cores Aluminium (Sorry I do not have it on any web site, it is an old copy) and the voltage drop for the 50 sqmm is 1.4 mV, so this is OK.

Mustafa

Reply
Anonymous Poster
#7

Re: Help required on selecting Underground cable

06/04/2007 8:37 AM

Thank you very much for all your postings and Help. For safety sake I am installing an additional 50Sq mm Cable. Now the 2 cables will run side by side and in future if any one of the cable has a problem I can still survive with the other cable.

Mine is a 3 Phase supply. I mention 40 KVA - that is because I have ordered a 40 KVA Diesel generator and they calculated the full load of my house to be about that. Even though all the load will not be "On" at the same time.

If I have a problem in future, will dump the Aluminium for Copper.

Cheers

Jay

Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#8
In reply to #7

Re: Help required on selecting Underground cable

06/04/2007 8:57 AM

Conclusions,

I wish I had the same house...

Wangito.

__________________
Never trade luck for skill.