Grounding control loops

06/02/2007 8:58 AM

OK, we all know that you should only ground one end to eliminate noise(ground loops). Speaking 4-20 ma. here. Now, say for instance you have a system that uses gas detection. From the instrument remote unit to the main control are 4-20 ma. From there(the main unit is a sourcing 4-20ma. run to a DCS for monitoring. Are each of these separate loops and ground one end of each, say from the remote and ground the end at the main unit, and then and then ground the output at the DCS as another loop? or treat it as one control loop and only ground the final landing out at the DCS? Hope this makes sense.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Apr 2006
Location: USA
Posts: 252
Good Answers: 6
#1

Re: Grounding control loops

06/02/2007 10:34 AM

Hard to say without a drawing. If I understand your circuit, the "main unit" is in the middle, remote sensor at one end and DCS at other. If so then the main unit has a 4-20ma input (from remote) and a 4-20ma output (to DCS). Looking at the diagram or spec sheet of the main unit will tell you if the input and outputs are isolated from each other as well as isolated from ground. Typically they will be isolated; meaning none of the terminals (+/- source/return) on main unit will have continuity between them and each cable shield could then have it's own ground. I prefer twisted pairs, and no grounded shields.

Register to Reply
Anonymous Poster
#2

Re: Grounding control loops

06/03/2007 12:13 AM

It is clear that you are talking about two seperate current loops one starts from gas deterctor and ends up with main control unit, the second loop is to retransmit the 4-20 ma to the DCS. you have to treat them as two different loops.

Register to Reply
Active Contributor

Join Date: Dec 2006
Location: Randburg, South Africa
Posts: 10
#3

Re: Grounding control loops

06/03/2007 3:33 AM

I stuck to the same philisophy.

Ground at central point and use galvanic isolating apmlifiers to disconnect all problem areas or wrong way round earths.

Ground loops are too difficult to find and once they are there you can pick up noise that is in the ground if the electrical earthing is suspect.

__________________
Wessel Pieters
Register to Reply
Associate

Join Date: Feb 2007
Posts: 43
#4

Re: Grounding control loops

06/03/2007 8:44 AM

I cannot speak to your specific installation because I've learned the hard way that rules of thumb and generalities are only starting points. You must have detailed knowledge of all your components, the degree and type of isolation and how they use the earth ground and for what purpose. It's common to have a variety of components in the same cabinet that have adverse affects on one another with respect to a common earth ground. It is often the cause of erratic and intermittent faults.

In large factories the typical earth ground loop is about the last place you want to connect anything to. "Dirty" does not do justice. Use your own grounding rods or points.

Register to Reply
Participant

Join Date: Nov 2010
Posts: 3
#5

Re: Grounding control loops

11/25/2010 8:07 AM

Hey..you are looking for signal conditioners, signal conditioners are great device. You can use those, I can recommend you one company that manufacturers signal conditioners. The company name is PJ Boner and you can find this on

http://www.pjboner.com/ .