07/17/2013 7:15 AM

We have 315KVA transformer with 120KW of lighting load, 62KW of UPS load and one 20HP motor load. The maximum demand is 220KW. The power factor is poor 0.75. Please suggest how to select a capacitor bank?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: How to select Capacitor Bank?

07/17/2013 7:26 AM

Er, how about discussing the need with various capacitor bank suppliers, and go from there?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#2

Re: How to Select Capacitor Bank?

07/17/2013 11:03 AM

Rule of thumb for a quick estimate or worst case (general industrial loads):-

Incoming supply switch - in this case say 400A

1/2 for supply to PFC = 200A

1/2 for KVAr fitted = 100KVAr

This is no substitute for proper measurements etc, but it is surprising how often it is not far off.

__________________
rogerggbr
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: How to Select Capacitor Bank?

07/17/2013 8:13 PM

In giving you this information, we are assuming that you know what happens when harmonics and capacitors meet.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: How to Select Capacitor Bank?

07/17/2013 10:44 PM

Contact a capacitor bank installer to fix a power analyzer/recorder at the main switchboard and record I,V,pf,harmonics,max demand,KW,kVA,kVAr,Hz etc for 24 hour period and recommend suitable solution including protection from harmonics.

__________________
pnaban
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#5

Re: How to Select Capacitor Bank?

07/17/2013 11:12 PM

TonyS - thank you excellant link