We have 315KVA transformer with 120KW of lighting load, 62KW of UPS load and one 20HP motor load. The maximum demand is 220KW. The power factor is poor 0.75. Please suggest how to select a capacitor bank?
Re: How to select Capacitor Bank?
07/17/2013 7:26 AM
Er, how about discussing the need with various capacitor bank suppliers, and go from there?
Good Answers: 11
Re: How to Select Capacitor Bank?
07/17/2013 11:03 AM
Rule of thumb for a quick estimate or worst case (general industrial loads):-
Incoming supply switch - in this case say 400A
1/2 for supply to PFC = 200A
1/2 for KVAr fitted = 100KVAr
This is no substitute for proper measurements etc, but it is surprising how often it is not far off.
rogerggbr
07/17/2013 8:13 PM
In giving you this information, we are assuming that you know what happens when harmonics and capacitors meet.
07/17/2013 10:44 PM
Contact a capacitor bank installer to fix a power analyzer/recorder at the main switchboard and record I,V,pf,harmonics,max demand,KW,kVA,kVAr,Hz etc for 24 hour period and recommend suitable solution including protection from harmonics.
pnaban
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member
07/17/2013 11:12 PM
TonyS - thank you excellant link