In our power Plant which is synchronised with Grid ,there was a heavy jerk in the grid and Power Plant got islanded from the grid resulting into tripping of Loads. During this period, it was observed that there was a high current (1893 Amp) and high Megawatt (32.4 MW) had gone into the system for a moment. We synchronized the grid again with PP and we were in the process to take load . After one hour, there was a flash over observed in LAPT /CT (lightening arrestor potential transformer panel) and Turbine got tripped and at the same time resulting into tripping of 11 KV breaker of 31.5 MVA transformer which resulted into total black-out of the plant. It was found that CT (current transformer) of R phase in LAPT/ CT Panel got burst. Immediately the replacement work of the same was taken up and CT was replaced . After replacement of CT, IR (MEGGER VALUE) of generator Stator winding up to LAPT /CT panel was measured as 100 Mega Ohm at 5 KV. ALSO IR (MEGGER VALUE) From LAPT /CT panel UPTO generator bus was measured as 3 Mega Ohm at 5 KV voltage. Since IR value OF LAPT/CT PANEL was very low against the minimum requirement of 15 mega ohm, so external heating of panel was started and achieved 25 MEGA OHM .
This CT was checked along with the total circuit of the generator and LAPT /CT panel during last shutdown in February-March, 2013 and combined values of total system were observed at 26 mega ohm. i wanted to know whether there is any procedure to check these CTs in isolation mode during shutdown or during any opportunity, The above CT is in operation since 1996 i.e. from the starting of the plant.
Kindly advise in this issue to avoid such failure.