Anonymous Poster #1

Transformer with High Voltage Ratio

07/28/2013 4:25 PM

Is it recommended to use transformer having high voltage ratio for example 275 KV/400 V? Any restriction on the max voltage ratio of a substation transformer?

Any comment or link for information is appreciated

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Transformer with High Voltage Ratio

07/28/2013 6:06 PM

If you have to ask, I don't think you need the answer.

Tips for Posting on CR4:

  • Look for answers before you post. Search CR4 or use a search engine to see if you can find the answer to your question.

  • Get an education and become qualified to know find the answer.
Reply Off Topic (Score 6)
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Transformer with High Voltage Ratio

07/28/2013 6:09 PM

No. Theoretically there's no limit, but there are some practical limits. A transformer with a 687.5:1 turns ratio is going to pass some really huge short circuit currents to the low side so that the money you think you're saving by not doing this properly is going to cost you big time when you try and get low voltage switchgear that is braced for that type of duty. Your voltage regulation on the low side is going to be problematic also. And who is going to build such a beast. Do it properly through multiple transformers.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#3

Re: Transformer with High Voltage Ratio

07/28/2013 9:31 PM

Short circuit current is not a more serious problem for high ratio transformers than for low ratio transformers. You can design a high ratio transformer to have any secondary short circuit current desired.

The problem is the same insulation clearance is require for a 1 kVA high voltage transformer as for a 5000 kVA high transformer. So small kVA high voltage transformer cost is the same for insulation and bushings as a large kVA high voltage transformer.
This means that the cost/kVA for small high voltage transformers are (usually much) higher than the cost/kVA for large high voltage transformers.

Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#4

Re: Transformer with High Voltage Ratio

07/29/2013 1:04 AM

For DC VSD drives I personally prefer Drive Type isolation transformers with a shield between windings. However, primary voltages are usually 2300 or 4600 volt.

Your ratio seems a bit extreme, but I suppose in the correct environment it could be reasoable - I just can't think of the situation.

Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#5

Re: Transformer with High Voltage Ratio

07/29/2013 4:41 AM

Voltages above 33 kv are used in transmission of high power because of lower losses. 400 volts are at the lowest level of distribution setup. The application are totally different. In theory while it is possible to build transformers with such voltage ratios (overcoming big technology challenges), the sheer cost involved will make it a non starter.

Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#6

Re: Transformer with High Voltage Ratio

07/29/2013 10:16 AM

The primary restriction would be economic, as transformers rated for that primary voltage are very expensive compared to a typical distribution-grade unit. Metering potential transformers for transmission circuits can have very high ratios, but they have very little capacity (usually 2 kVA or less).

However, high ratio power transformers are sometimes used to provide auxiliary power at remote transmission switching stations. There are places where you don't have a medium voltage circuit handy and getting one to the site would cost more than a special-design transformer.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Transformer with High Voltage Ratio

07/29/2013 3:29 PM

No it is not recommended, in your example you are trying to take a very high voltage transmission level supply and feed it directly into a low voltage distribution supply (you don't mention the transformer size, so I will keep the examples generic). The power grid is not designed and set up for this, that's one reason we have substations all over the place and smaller 11kV to 400V (for example) distribution transformers to actually step down the voltage for the consumer.

For a near-by dedicated very large factory load, perhaps, but even then large loads are likely to be operated on high or medium voltage (standard specific) rather than 400V low voltage so a single high voltage ratio transformer doesn't make sense.

With regards to high voltage distribution transformers outside of a substation, how do you even connect up to the 275kV line way up on those tall transmission pylons or buried under the ground, their are no easy branch access points to allow connection except at each end when they connect to either a power station or a substation.

Is this homework, because it sounds like it is?

Jack - In the middle of designing a real substation.

__________________
jack of all trades
Reply Score 1 for Good Answer
Anonymous Poster #1
#8
In reply to #7

Re: Transformer with High Voltage Ratio

07/29/2013 6:44 PM

It is not homework, it is rather hearing from electrical engineers, especially who are in the middle of designing real substation

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10
In reply to #8

Re: Transformer with High Voltage Ratio

07/30/2013 3:24 PM

Just about anything is potentially possible but customer requirements, protection equipment, economics, industry standards, safety and common sense will limit the options.

Have you looked at different transformer manufacturer websites to get a bit of an idea what is commonly used?

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Transformer with High Voltage Ratio

07/30/2013 4:55 AM

Selecting such a large voltage ratio significantly reduces the options for system expansion and alteration in the future, and might be described in some quarters as "myopic".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Aug 2013
Posts: 12
#11

Re: Transformer with High Voltage Ratio

08/01/2013 11:48 AM

I think that you should re-visit that voltage ratio because it appears to be very extreme. Typically, 11kv, 6kv are transmitted from the sub-station to private industries which will break it down to 415v/230v for workshop, office buildings etc. Typical transformer ratings are: 100kVA, 4kv/415v or 100kVA, 4kV/230v to domestic residence. May I suggest that you should check out the rating of the transformer and get the full load primary current and full load secondary current as follows: 100kVA/4kv = Ip and 100kvVA/415 = Is and then see if the load fits into this for whatever you want to do. What you have there is too extreme.

Reply
Member
India - Member - New Member

Join Date: Jan 2008
Posts: 7
#12

Re: Transformer with High Voltage Ratio

08/02/2013 11:51 PM

Apart from technical issues cost would be prohibitive. Nobody wants to connect their tv and microwave directly to the transmission network.

Reply
Reply to Forum Thread 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: