Primary Protection for Transformer by Fuses

07/31/2013 1:46 PM

Hi All,

Can we use Fuse on primary side of transformer and CB on secondary side.

My query is upto what rating we can use Fuses for transformer protection.

can we use CB with solid state trip on primary and secondary side.

I have seen in IEEE C57 that fuses can be used upto 5MVA XFRM for primary / secondary side.

Am I getting it correctly or should we use Fuse on primary and CB on secondary regardless of MVA or Voltage.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Primary protection for transformer by fuses

07/31/2013 2:22 PM

Please consult your local regulations. Nobody here knows yet what they are.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Primary protection for transformer by fuses

07/31/2013 2:47 PM

As per IEC / IEEE what is the maximum rating of Transformer we can use the fuses as primary and secondary side protection.

Reply
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Primary protection for transformer by fuses

07/31/2013 2:54 PM

Then look here: International Program IEC - The IEEE Standards Association

If you are working to a standard you should have a copy, and use it.

Someone's life may depend on what you are doing!

Get the standard, or hire a PAID consultant.

Reply Good Answer (Score 3)
Active Contributor

Join Date: Jun 2013
Posts: 14
#4

Re: Primary protection for transformer by fuses

07/31/2013 3:00 PM

Hi there is one very good guide from Schneider Electric Protection guide

For 1-2 MVA HV / LV low density loads Fuse / CB combination

for > 2 MVA HV / HV you will need all protections

there are Gurus here who can advise better.

Reply
3
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#5

Re: Primary Protection for Transformer by Fuses

08/01/2013 4:41 AM

Selection of HRC fuse (providing short circuit protection only) or Circuit Breaker (facility to provide various protection and control functions) as primary side protection of Transformers depends mainly on economics and criticality of application. For lower rated transformers, the cost of circuit breaker will be equal or more than the cost of transformer which it protects and hence does make economic sense. Typically transformers rated 1000 KVa and above will be provided with circuit breakers as primary protection as cost of breaker will be some percentage of cost of the transformer it is protecting. Also from 1000 KVA rating, provision of WTI, OTI, Bucholz, surge protection devices etc (mechanical protection devices) becomes mandatory. With these protections in place, you will need tripping mechanisms for isolation of transformer from source, which HRC fuses cannot provide. Breakers for smaller rated transformers are employed in case the transformer is used for some critical application (where transformer cannot be allowed to be shut down and all necessary protection to safe guard the transformer are incorporated in the breaker) and/or based on requirement of operation through remote switching. However these are exceptions rather than normal.

Present day breakers (both primary & secondary side) are provided with solid state (electronic) or numerical based (software driven) protections which are field proven and widely used.

Please note that if you are using breakers, you can build in all kinds of required protection schemes, like overcurrent, short circuit, over/under voltage, earth fault etc, which is not possible with HRC fuses which offer only current based short circuit protection. Also the breakers can be "built intelligent" for remote control, metering etc and this is simply not possible if HRC fuses are provided as incomer control.

Slowly as the cost of breakers are coming down, the requirement of both operation and control of primary and secondary equipment's are going up, the usage of breakers as both primary and secondary protection and control equipments is gaining popularity, irrespective of the capacity of the transformer.

Reply Good Answer (Score 3)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Primary Protection for Transformer by Fuses

08/04/2013 10:28 AM

Consult your local regulations.

Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); lyn (1); mik23 (1); Pattabhiraman (1); Tornado (1)

Previous in Forum: Recloser TCC Slow Curve Pickup For Overcurrent (Overload) Protection   Next in Forum: Electrical Design Question

Advertisement