Dear All,
Recently I have discussed about our problem N-E voltage at 300V in my previous discussion. We identified the problem it was reverse voltage from the phase and phase to earth shorting in Air conditioning distribution board.We rectified the same but now we are randomly facing same problem with different Air conditioner (3 phase) where phase short with body will be reflected as phase suppression, neutral at 230V and incomer FP MCB not failing at same time. Because of which all facility N-E voltage rises to 230V.
We have 3P UPS which accepts only 3P and generates 3P only. We connected mains Neutral at UPS bypass which is used in UPS output circuit for single phase load. Our electrical consultant recommended for removal of input Neutral and connection of separate Earth pit at UPS output Neutral so that Neutral will be isolated from facility. Please let me know technically it is ok or not?
I have got reply from UPS engineer that It is not recommended as whenever Earth connection at Neutral open in future there will be major failure at UPS output load. Is this right? Only isolation transformer will suffice the purpose.
We are using chemical earth at our facility which has longer life. Our consultant says there will not be any effect on ups output load. Please comment.