Neutral to be Earthed at 3 Phase UPS Output OK or Not?

08/02/2013 4:15 AM

Dear All,

Recently I have discussed about our problem N-E voltage at 300V in my previous discussion. We identified the problem it was reverse voltage from the phase and phase to earth shorting in Air conditioning distribution board.We rectified the same but now we are randomly facing same problem with different Air conditioner (3 phase) where phase short with body will be reflected as phase suppression, neutral at 230V and incomer FP MCB not failing at same time. Because of which all facility N-E voltage rises to 230V.

We have 3P UPS which accepts only 3P and generates 3P only. We connected mains Neutral at UPS bypass which is used in UPS output circuit for single phase load. Our electrical consultant recommended for removal of input Neutral and connection of separate Earth pit at UPS output Neutral so that Neutral will be isolated from facility. Please let me know technically it is ok or not?

I have got reply from UPS engineer that It is not recommended as whenever Earth connection at Neutral open in future there will be major failure at UPS output load. Is this right? Only isolation transformer will suffice the purpose.

We are using chemical earth at our facility which has longer life. Our consultant says there will not be any effect on ups output load. Please comment.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Neutral to be earthed at 3 phase UPS output ok or not?

08/02/2013 4:31 AM

Earthing the neutral of the UPS separately is OK until someone opens the connection and grabs hold of the neutral thereby forming the earth path through that individual's body, at which point one hopes that the facility's indemnity insurance policies are fully subscribed as the prospect is that individual having half-a-day-out with the Undertaker. Were the equipment to continue to operate while the 230V-N were connected to earth, then there is something seriously adrift with the circuit protective equipment further upstream, a major safety problem, and the prospect of it causing fire if left unchecked. Sort this problem out and the N-E voltage problem at the UPS will go away.

Don't piddle about any longer. Hire an experienced Electrical Engineer today/this morning/right now. Get this individual to chase through the upstream connections and eliminate the fault. Have this individual review and confirm the settings of the circuit protective equipment having removed the fault. Make sure the investigation and its outcome are recorded for future reference, just in case the problem arises again.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Neutral to be earthed at 3 phase UPS output ok or not?

08/02/2013 4:57 AM

If you have a 3 phase UPS and uses only 3 phase voltage, then, the neutral should not be grounded to earth. The UPS itself provide its own neutral point for 230V. Only the body of the UPS is connected to earth.

If neutral of the UPS is connected to earth, then there will be a reverse flow of voltage to your UPS if there is a faults in the power distribution system where the leakage voltage will flow back to your UPS by the earth wire.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Neutral to be earthed at 3 phase UPS output ok or not?

08/02/2013 5:10 AM

...if, indeed, the upstream circuit protection equipment failed to operate...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jul 2013
Posts: 1
#4

Re: Neutral to be Earthed at 3 Phase UPS Output OK or Not?

08/02/2013 3:12 PM

Hi,

There are many types of UPS out there. You need to know wether your UPS has a Bypass or output isolation transformer (Not the small rectifier transformer).

In UPS systems with bypass option, without output IT, you will not have a new neutral at the output, and the bypass neutral is taken as it is. Input neutral is not used. Hence we usually have a by-pass Isolation transformer / AVR ( delta-star) with newly derived neutral connected to UPS bypass. In any case, earthing the neutral again is not advisable, without additional IT.

Plz see this doc for exact implementations

http://www.apcmedia.com/salestools/COCR-8SYKH8_R0_EN.pdf

https://www.insight.com/content/dam/insight/en_US/pdfs/apc/apc-role-of-isolation-transformaers-in-data-center-ups-systems.pdf

Register to Reply
Active Contributor

Join Date: Jul 2011
Posts: 20
#5

Re: Neutral to be Earthed at 3 Phase UPS Output OK or Not?

08/03/2013 3:44 AM

Your electrical consultant takes a risk for safety. Technically it can be done but not safe. If you have earth fault protection / RCBO it will triggered by the current that flow through earth.

Register to Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#6

Re: Neutral to be Earthed at 3 Phase UPS Output OK or Not?

08/04/2013 11:18 AM

This is a repeat post.

In OP's UPS, the output is 3 Phase delta connected. However single phase loads needs to be connected to the output. The OP has connected single phase loads, supposedly balanced, in a floating neutral arrangement, which is very dangerous. OP was advised to provide 3 phase delta to star double wound isolation transformer with dedicated star point neutral earth connections. With this arrangement single phase loads can safely be connected to UPS.

".....Because of which all facility N-E voltage rises to 230V."

This is a dangerous situation with potentially disastrous consequences. You are living with a time bomb. Without wasting time, immediately arrange to provide the isolation transformer to mitigate the problem.

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#7
In reply to #6

Re: Neutral to be Earthed at 3 Phase UPS Output OK or Not?

08/10/2013 1:21 AM

Pattahiraman is right, this is EXTREMEly Dangerous. must b fixed ASAP = immediately !!!

__________________
BSEE but always learning
Register to Reply
Active Contributor

Join Date: Aug 2013
Posts: 21
#8

Re: Neutral to be Earthed at 3 Phase UPS Output OK or Not?

08/19/2013 2:12 PM

This is true as when the 4 pole upstream tripped all the UPS suppled RCBO tripped

so the IT is a must ......that soves my rpoblem and will consult with APC on this

thanks

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); febriansasi (1); fidel (1); hareeshravi (1); Pattabhiraman (1); PWSlack (2); Simon Wan (1)