Calculate Stabilizing Resistor

08/12/2013 9:39 PM

hello engineers, please help me to calculate stabilizing resistor for earth fault relay. as i know,

Rstab = V/I

i know how to find v, but i am confused about I value. whether i use CT secondary current (i.e) 5A or relay setting current. looking for your help..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Calculate Stabilizing Resistor

08/12/2013 10:34 PM

You should take relay setting current. Supposing your CT secondary current is 5 amps and setting value is say 10 %, then you should take 0.5 Amps.

If the CT secondary is 1 amps and setting value is say 40 %, then you should take o.4 amps.

Hope this is clear.

I have developed an APP for calculating the Stabilising voltage and Stabilising resistance. This App will be uploaded to ITunes Stores /App stores shortly

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Anonymous Poster #1
#2
In reply to #1

Re: Calculate Stabilizing Resistor

08/13/2013 8:10 AM

dear sir,

Can u tell that why stabilising resistor to be used in protection relays. is it for voltage drop?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Calculate Stabilizing Resistor

08/15/2013 11:24 AM

Your understanding is grossly incorrect. You may please note that a stabilising resistor is added to an REF Relay circuit, to prevent a mal-operation of the relay for an external earth fault, in case one of the CTs involved in the fault saturates. Under such a condition, the saturated CT would act as a short circuit and would not pump any compensating current to the relay. Whereas, the unsaturated CT in the fault circuit would develop a voltage proportional to the fault current and the design Knee Point Voltage of the CT. This voltage developed by the CT shall not circulate a current so as to operate the relay.

So, the value of the stabilising resistor shall be: {R (total) - R (relay at the setting)}

R (total) = Relay operating voltage at the actual fault current / Relay set current

R (relay) = {VA Burden of the relay at the setting made / (set current)2}

Register to Reply