Harmonic Filter - Cost, Size?

08/27/2013 9:21 AM

Hi there,

I'm working a ship where we have a 6.6 kV 50Hz system that feeds 12-puls converter for propulsion, the same 6.6 kV is also transformed down to 400V for general use. This 400V is also used for feeding a 400V/400V transformer (500kVA) that is used to give power to refrigerator containers. When we only running two diesel generators connected to 6.6 kV net, we get problem with the harmonics created by the converters on this 400V. From the measurement that I have done, we have a voltage THD on the 400 V about 7 to 8 % and it is mostly, due to the 12 - puls converter, the 11th and 13th harmonic that causes us problem.

Now, I'm not wondering about the theory behind as I'm a bit familiar with it but I'm wondering about the hardware. How big would it have to be as there is a space issue onboard and what would an estimated cost for such filter be? It's easier to talk to the management if one has some idea as they will ask.

When searching for harmonic filters they usually is also used for power factor correction and therefore comes with larger capacitor banks. My only goal here is to remove the harmonics and from my own modest calculation by removing the 11th and 13th harmonic it would bring us down between 5% or 6 %.

Thx in advance for any idea

Lars

Register to Reply
Pathfinder Tags: Harmonic filter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Harmonic Filter - Cost, Size?

08/27/2013 10:02 AM

Only 7 to 8% THD gives your generators problems? What kind of problems? How can you be sure that by filtering you will clear up the problem? Maybe all you need is a set of line reactors between the generators.... And, how much overall current are your talking about?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Member

Join Date: Aug 2013
Posts: 6
#2
In reply to #1

Re: Harmonic Filter - Cost, Size?

08/27/2013 10:22 AM

Hi, thx for the comment.

We dont have any problem with the generators, i might have been a bit unclear with the problem :)

The problem is that the refrigerator containers that we feed power for driving the compressor, switches off from electric power and starts up on diesel instead when THD goes above about 5.5 %. The THD vaule goes up as we increases the load on the propulsion motor.

/Lars

Register to Reply
Member

Join Date: Aug 2013
Posts: 6
#3
In reply to #2

Re: Harmonic Filter - Cost, Size?

08/27/2013 10:44 AM

Some more explanation. My idea would be to put in detuned filters on the downside of the transformer that feed the containers.

The maximum current to the containers is 800A.

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#4
In reply to #2

Re: Harmonic Filter - Cost, Size?

08/27/2013 12:23 PM

So the problem is that the refrigerated containers are supposed to use your power but instead they are starting their own diesel powered cooling units?

And the container coolers are sensative to the THD? Thus refusing to allow external power to be used?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Member

Join Date: Aug 2013
Posts: 6
#5
In reply to #4

Re: Harmonic Filter - Cost, Size?

08/27/2013 1:20 PM

yes, that is our problem.

Register to Reply
2
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#6
In reply to #5

Re: Harmonic Filter - Cost, Size?

08/27/2013 11:54 PM

It may not be a problem with compressors of refrigerator container. Most probably it can be problem with relay which is sensing supply fitted in control circuit of refrigerator unit and giving starting command to DG Set.

For this you shall arrange a low pass filter, which shall only pass fundamental frequency component of voltage to the sensing relay. This is a small piece of size 200mm x 100mm x 100mm (length x width x height) with just 6 terminals (3 input and 3 output) and shall not cost more than $250.00. This is basically a Pi or T or simple L filter with air core choke in series and capacitors in parallel. This can be easily located in DG Control Panel.

I have one available with me. I keep this in stock for isolating harmonics entering sensing circuit of AVR of 3 phase generator.

Other way to reduce harmonics is to increase the size of 3 phase alternator coupled to the Engine. Higher the rating, higher is Sub-transient reactance Xd" and lower is the distortion. It is very easy to calculate and estimate distortion for standard IEEE limits of harmonics of 6 pulse or 12 pulse rectifier circuit and select the 3 phase synchronous alternator of correct size. Higher rating of alternator also improves its life against overheating of core due to harmonics (hysteresis and eddy losses).

One way to increase rating is to calculate the correct rating of additonal alternator, couple it with pony motor and synchronise with existing DG Set. But this will be more complicated than adding capacitor filters.

One disadvantage of Filters will be that when propulsion is not running, the capacitors will result in Leading Power Factor on DG set, resultant overvoltage (Armature Reaction of Capacitive load is Re-magnetising) , which will require cutting off of filters. And once 6.6kV capacitor is switched off it takes 3 to 4 minutes to discharge of residual voltage before it can be switched on in service. Hence using Capacitors can be nuisance with varying propulsion load.

Generally 7% to 8% distortion at terminal of Generator is not bad and acceptable for safe operation of power set up - This fact you can check with Standards to which the ship is built/certified (Lloyeds or ABS or BV etc.). When calcualting distortion at the time of proposal and closing order for 3 phase alternators for SCR applications, I used to aim at 8 to 9% and inform designer to ensure that Xd" of final built is standard rated less tollerance (IEC allow +/-20% tollerance in Xd" and if the designer is cautioned before hand he can ensure that we do not exceed in this particular application.

Hence in my opinion best option, out of 3 above, for you shall be to use Low Pass Filter in sensing circuit of relay which is triggering start of DG Set.

Register to Reply Good Answer (Score 2)
Member

Join Date: Aug 2013
Posts: 6
#7
In reply to #6

Re: Harmonic Filter - Cost, Size?

08/28/2013 2:25 AM

Thx for your fine answer but the problem with the containers, which I should have been clearer about, is that they are on trucks and they are not ours as we just transport them as I work on a ferry. So for us to do any kind of modification on the containers is not doable.

Is the idea about putting in detuned band pass filter on the downside of the 400V transformer not so good?

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#8
In reply to #7

Re: Harmonic Filter - Cost, Size?

08/28/2013 5:58 AM

Connecting Filter downstream of Auxiliary transformer which is feeding in to Freezer Container will not help.

Reason being that the distortion is in 6.6kV output voltage generated by 3 phase synchronous alternator due to Harmonics Current fed from inverter. This is further being reflected in the 400V side of Transformer. The filter removes the harmonic currents. Hence any filter has to be at 6.6kV bus.

The picture of connection of Freezer Containers and Diesel Generator is not clear to me. What I understood earlier that each container has AC electric motor driven compressor + condenser unit. Individual freezer is normally supplied from common ship power and in case of problem with ship power there is a 400V, 3 Ph DG Set with AMF and changeover on the deck, common to all containers. The AMF relay of DG is malfunctioning due to harmonics. Please clarify connection between containers and Ship.

Register to Reply
Member

Join Date: Aug 2013
Posts: 6
#10
In reply to #8

Re: Harmonic Filter - Cost, Size?

08/29/2013 2:44 AM

The ships power comes from four diesel generators with a voltage of 6.6 kV. This 6.6 kV is used the propulsion converters. It is also transformed down to 400V for different three phase loads and among them a 400v/400V transformer that feeds all the power outlets for the freezer containers. The reason for the second transformer is to separate possible earth faults from the ships system.

There is no common DG set that will be switched over to incase of problem with the ships normal power. Every freezer container/truck can switch between using its own diesel set or an electric powered set. This switching is automatically.

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#11
In reply to #10

Re: Harmonic Filter - Cost, Size?

08/29/2013 4:52 AM

Noted that there are two Distribution Transformers between DG sets and Container Freezer units. First 6.6kV: 400V for main ship bus and second 400:400 isolating transformer between 400V Bus of Ship and Freezer units. The isolating transformer is probably used to convert ship floating neutral to grounded neutral for freezer units.

When designing core of Transformer, for economy, the designer selects operating flux density of at slight saturation 10% to 15% above linear range of magnetising curve. Because of this saturation there is slight harmonics in secondary winding. Which has no problem in case of normal supply. In your case the supply is already distorted and possibly the harmonic contents at 400V supply to freezer bus shall get worsened due to saturation in the core.

We cannot do anything to 6.6kV to 400V Transformer. Hence the harmonics at this bus is accepted.

We can definitely do something to 400:400V isolating transformer so that any distortion by virtue of this is eliminated. So as a first step, disconnect supply to containers from Secondary of Isolating transformer and connect directly to primary input of isolating Transformer. Try out Freezer containers at different load of inverter - if no problem is experienced order special isolating transformer and replace existing with new. The replacement transformer will have relatively higher cross section area of core and of material of better quality.

If above trial does not work - means the harmonics at ship 400V are of sufficient magnitude and required to be filtered. In this case suggest to install Harmonic filters at 6.6kV Bus.

Keep me posted of progress.

Best of luck.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#9

Re: Harmonic Filter - Cost, Size?

08/28/2013 10:22 AM

This problem can be mitigated with a passive harmonics filter but its design will be difficult if not impossible as the impedance of the source is not so low and changes drastically with the number of generators operating. You will need to use many smaller banks in parallel to adapt to the rapidly changing load. A fast controller (single cycle) with its corresponding fast semiconductor switches will be needed. The load also varies drastically when you are in a storm. This makes the phase and the amplitude of the harmonics change every time you hit a wave. The reefers load variation is probably negligible in this setup but this type of load is known to be highly variable as they turn on and off almost randomly.

In these applications, you are better off with an active harmonics filter that will not be susceptible to the resonance problems of the passive alternative. The cost will be higher though.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#12

Re: Harmonic Filter - Cost, Size?

08/29/2013 7:57 AM

How about using a set of 1:1 isolation transformers? The harmonics would have a hard time penetrating due to the iron core of the isolation transformer. You can buy phase shifted windings such that they actually eliminate certain harmonics. What I mean by phase shifted windings is a technique where a number of turns from the adjacent transformer are placed on the first transformer and so on.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#13
In reply to #12

Re: Harmonic Filter - Cost, Size?

08/29/2013 9:26 AM

Most lower harmonics (up to 30-40) pass through the standard isolation transformers with little attenuation. The main exception are the multiple of 3 that are blocked.

This will not solve the OP problems with 11 and 13.

The OP could use a specially designed mitigation transformer to attenuate the 11 and 13. This transformer could be used only on the 415V feeder to minimize its size. The net can list plenty of suppliers.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Lars (5); marcot (2); NotUrOrdinaryJoe (3); powersolutionsFBD (3)

Previous in Forum: Brazilian Industrial Single Phase   Next in Forum: Grounding of Painted Towers

Advertisement