Transformer Exitation

09/20/2013 3:19 PM

exitation test [power factor]was carried out on a 34.5 Kv power transformer, with 10 kv injected on high side on only the B and C phase.The current reading were 34.9 mA and 35.7mA respectively .could not inject 10 Kv 0n A phase because intrument[delta 2000] kept tripping out at 6 Kv , so 5 Kv was injected and current reading was 309.1mA. Are these readings normal or is there something wrong with winding?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster #1
#1

Re: transformer exitation

09/20/2013 4:36 PM

Help--I'm stuck in this transformer, and I want to get out!

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: transformer exitation

09/20/2013 7:52 PM

Could I ask, are you competent to be working with 10KV? The thought of you anywhere near 35KV fills me with dread.

Did you ever sort out the problems with the generators?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#3

Re: transformer exitation

09/20/2013 10:49 PM

HMMM!! Let me think?? Ummmm!! Yes!! You have a problem wih the "A" windings. Have it repaired or buy a new transformer.

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
2
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#4

Re: transformer excitation

09/21/2013 3:25 AM

By excitation we can detect two types of faults.

1. Shorted turns in any limb.

2. Any short in the core. By short in the core, I mean we have insulation sleeve and insulating washers in core clamping bolts so that the clamping or tightening bolt does not short circuit the core.

The batter way to check above is by not simultaneously energising all limbs and measuring magnetising current, but just excite any one core and measure induced voltage in other two. This Test is called CORE BALANCE TEST and is a good diagnostic tool in hands of Maintenance Engineers. I had also used this to find which limb of transformer winding has a short circuit.

That means energise, say phase A alone, connect voltmeters via PTs across other two phases and measure induced voltage.

Under healthy condition of winding and core, you shall have practically same induced voltage if both Phase B and C and in magnitude 50% of applied voltage on phase A. (B will have negligibly higher induced voltage due to shorter magnetic path in case of core type transformer. In case of shell type construction of core both will have same voltage).

If you find that Voltage induced in B phase is less than C phase, the B phase has either inter turn short or the insulation of bolt is damaged on this limb. shorted bolt is also equivalent of singe turn short around core.

You can further verify results by exciting other limbs, one at a time and measuring induced voltage in remaining two.

Otherwise, if you have excited the core with 10kV or 5kV 50HZ AC supply, and want to know whether the current is within limit - Just open the Factory test report in which you will find Open Circuit curve of the transformer and compare the results.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5

Re: transformer exitation

09/21/2013 5:39 AM

Response #4 is good answer. Certainly fault in winding A. But why did you not give transfo kVA rating? No-one can compare magnetising current with own experience without size.

Register to Reply
Register to Reply 5 comments