HVAC/R - Recovering Liquid Refrigerant

09/24/2013 3:05 PM

Hello, I am new to the forum but have read many posts and found a lot of useful information. I recently had to recover approximately 600lbs of refrigerant from a Trane water-cooled screw chiller and was curious about different recovery methods that technicians use.

While on this particular job I used the standard "push-pull" method to recover the liquid in the system (About 150lbs) and then proceeded to recover the remaining (~450lbs) vapor using the standard vapor recovery method. This took nearly 8 hours, even with two recovery machines.

My question is, since the chiller had an operational compressor, would it be possible to set up a liquid recovery as such:

Attach liquid port of recovery cylinder to liquid line service port of chiller.

Attach vapor port of recovery cylinder to suction service port of chiller.

Run compressor and recover liquid from circuit (of course monitoring amount recovered with scales and gauges, and having ensured proper water flow through chiller) Basically I want to run the compressor so I know where the liquid in the circuit is, and can recover a large percentage of refrigerant as a liquid, rather than waiting hours and hours to pull out the vapor.

Would recovering refrigerant in this manner pose a threat to the oil flow while compressor was running because of any problems with the differential that the oil needs to move? I have been told that you can recover up to about 80% of the unit's charge as liquid in this manner before low differential pressure poses a threat.

Thanks!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#1

Re: HVAC/R - Recovering Liquid Refrigerant

09/24/2013 3:22 PM

To my knowledge most compressors rely on the lubricant in the coolant, so as you deplete the coolant you may reach the point at which the compressor fails - but if you are draining the coolant because the unit is being disposed or replaced, and there is no future use for it, then it doesn't matter.

__________________
Smart as a post and twice as fast.
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#2

Re: HVAC/R - Recovering Liquid Refrigerant

09/24/2013 3:31 PM

I'm not an HVAC guy, but it sounds feasible if you were somehow able to create pressure on the back side, to push the vapor into the compressor at the same pressure that it normally runs at.

Maybe just a separate air compressor to keep the system pressurized, cutting off the AC compressor before the air hits it.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: HVAC/R - Recovering Liquid Refrigerant

09/24/2013 4:16 PM

It would seem to be plausible that the pressure differential is maintained to a certain point of somewhere in that neighborhood....but I wouldn't roll the dice without an endorsement by Trane that this is an accepted practice....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4

Re: HVAC/R - Recovering Liquid Refrigerant

09/24/2013 6:09 PM

Sounds like you're talking about using a pulldown mode, except you would be putting the refrigerant into a temporary recovery tank instead of a permanent receiver. I don't see any problem as long as you limit the time (probably 3 to 5 minutes max.) and get any oil back into the system when you recharge it.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#5

Re: HVAC/R - Recovering Liquid Refrigerant

09/24/2013 7:19 PM

I would have put it in the reciever

Register to Reply Score 1 for Good Answer
Participant

Join Date: Sep 2013
Posts: 3
#6

Re: HVAC/R - Recovering Liquid Refrigerant

09/24/2013 10:46 PM

Thanks for the feedback. Will be trying this method later this week and will post results.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: HVAC/R - Recovering Liquid Refrigerant

09/28/2013 6:26 PM

first off, a compressor is NOT a liquid pump, it is a vapor pump that works by compressing gas (vapor), if you attempt to pump liquid with it you will grenade it. if you introduce liquid refrigerant into the suction side of the compressor you will also wash out the bearings. I understand what you're trying to do and I strongly advise against it. put as much of the refrigerant as possible into the receiver and condenser coil. if it takes 2-3 recovery machines to evacuate it.......charge the customer, its part of the deal.

Register to Reply
Participant

Join Date: Aug 2014
Posts: 2
#9
In reply to #7

Re: HVAC/R - Recovering Liquid Refrigerant

08/10/2014 8:14 PM
Register to Reply
Participant

Join Date: Sep 2013
Posts: 3
#8

Re: HVAC/R - Recovering Liquid Refrigerant

09/28/2013 7:06 PM

Thanks for the feedback. Will be trying this method later this week and will post results.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers: