Tan Delta Test

10/07/2013 5:36 AM

1. What will be the difference of tan delta values when the test is conducted between Live- Tan delta point(UST Mode) & Live - Earth(GST Mode). If there is no difference what is the use of providing Tan delta terminal seperately?

2. Is it required to do Tan delta test for SF6 Gas filled current Transformers?

Register to Reply
Pathfinder Tags: tan delta
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Tan Delta Test

10/07/2013 1:42 PM

1. UST mode ("Ungrounded Specimen Test") is used for testing between 2 points that normally are both insulated from ground, such as across the open contacts of a circuit breaker pole. The GST mode ("Grounded Specimen Test") is for testing of a portion of apparatus that normally is operating phase to ground, such as a circuit breaker or transformer bushing from the conductor to the case or tank (which is grounded in service). GST tests can be done in the UST mode of the test set. However, UST tests cannot be made in GST mode, because the contribution of the insulation to ground element cannot be eliminated. Having both modes allows speedy testing of the various elements of the insulation in a transformer or circuit breaker without having to move the test leads around many times, just by changing the mode switch.

2. What does the project's test specification or the current transformer instruction manual say? I would normally expect "Yes," but that might not always be the case.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 2)
Participant

Join Date: Oct 2013
Posts: 2
#2
In reply to #1

Re: Tan Delta Test

10/08/2013 5:16 AM

Thanks for reply.Based on your points i understood that the test can be performed with out Tan delta point (i.e.,In GST mode) also but the need of providing tan delta point specially for Instrument transformers & Bushings is unanswered.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#3
In reply to #2

Re: Tan Delta Test

10/08/2013 7:45 AM

It is obvious that you are very new to insulation testing otherwise you would know that it is a pain to conduct GST tests, especially in or near energized equipment. The GST test always involves interference and thus makes it very difficult to get stable and reliable test results.

On the other hand, the UST test can always be conducted in a manner that minimizes interference and provides accurate and stable numbers.

When testing SF6 insulated equipment such as CTs, you have to do a test to determine the insulation qualities of the support structure - which is NOT gas, and you have to test a sample of the SF6 separately for moisture and other contaminants. It is most convenient to have a "Test Tap" on such assemblies.

Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

krishna57 (1); olehwi (1); PeterT (1)

Previous in Forum: High Voltage Circuit Breaker Recovery Voltage   Next in Forum: Conductance Calculation

Advertisement