High Voltage Circuit Breaker Recovery Voltage

10/07/2013 5:29 AM

Fellows, I have to know. HV CBs are said to have transient recovery voltage (TRV). When interrupting a fault the contacts will separate as a result an arc will form. But as the contacts separate the dielectric strength between the contacts increases. There will then be a race between the increase rate of the dielectric strength and that of the TRV between the contacts. if the dielectric strength is faster then the CB is good. I would like to know what causes the TRV to increase. I know the rate of increase depends on the systems connected on the terminals (contacts) of the CB. There is also small currents that are caused by capacitive or inducitve loads which the circuit breaker must interrupt. How are these currents generated and what magnitudes are we looking at?

__________________
cout<<"Hello world"<< endl; classic isn't?
Register to Reply
Pathfinder Tags: AC Primary Circuit Breakers
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#1

Re: High Voltage Circuit Breaker Recovery Voltage

10/07/2013 9:46 AM

TRV is a direct result of the collapsing ambient magnetic field back into the circuit conductors when/as the circuit is being opened/disconnected.

All electrically energized conductors create an ambient/surrounding magnetic field in the air as well as in any ferrous metal object in the near vicinity.

Equipment such as motors and transformers store very high magnetic fields in their laminations and therefore interrupting these types of circuits results in higher TRV values.

Length of supply conductors is a contributing factor. (The greater the line length, the higher the magnatic field, and the higher the TRV value during fault interruption.)

The higher that the current in the interrupted circuit is at the time of the fault, the stronger the magnetic field is surrounding the conductors, and the higher the TRV will be.

Also: The steeper the angle (up to 90 degrees) the greater the magnitude of voltage induced back into the circuit. (Transformer design takes advantage of this law for improving efficiency.)

This is a very simple explanation and for a better, more "in-depth" understanding you need to obtain and thoroughly review any of the readily available information on circuit breaker operation during fault conditions from multiple vendors.

There are standard fault calculation formulae available to apply for identifying the TRV.

I would suggest a visit to Engineering Toolbox and subscribing to the site.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Good Answer (Score 2)
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#2
In reply to #1

Re: High Voltage Circuit Breaker Recovery Voltage

10/07/2013 10:43 PM

SHOCKHISCAN:
Good amount of information and with lots of clarity.
Shielding magnetic field has always been a problem. Even though u-metal shields shields do some good, coupling of AC signals due to magnetic field tend to take place very often.
I am trying to see if any DC source +/-5V 100mA can be made with 100uV peak to peak noise? I am unable to reach below +/-2mV.
Another thing that matters is the choice of shielding material for RF LNA. Among common metals that are available, Copper, Aluminum, Iron or combination of these, which one to be used. I have low current, low charge but fast nano-seconds signals formed by just few thousands of electrons.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Aug 2008
Posts: 82
#4
In reply to #2

Re: High Voltage Circuit Breaker Recovery Voltage

10/08/2013 2:19 PM

For RF - LNA ;

Extra casing with Al or copper alongwith inner insulation { Double insulation in power tools type } could be of use .

Register to Reply Off Topic (Score 5)
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#5
In reply to #4

Re: High Voltage Circuit Breaker Recovery Voltage

10/09/2013 6:41 PM

I use 3mm Aluminum casing. Perhaps Copper with inner insulation can also be tried.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply Off Topic (Score 5)
Participant

Join Date: Oct 2013
Posts: 1
#3

Re: High Voltage Circuit Breaker Recovery Voltage

10/08/2013 7:07 AM

CR4 Admin: Spam: This post was modified because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#6

Re: High Voltage Circuit Breaker Recovery Voltage

10/16/2013 8:26 AM

On top of what has been explained, TRV is described by its rate of rise, and also by the initial rate of rise , as it is progressive . For CB arc interruption as the first microseconds after the zero current are of importance, the initial TRV delay (named Td in standards) is important) . Of course, all this applies to purely inductive loads, or short circuits . As soon as there is some resistance, as cable or busbars lenghts, downstream of the CB between the CB and the short circuit itself, arc quenching becomes a piece of cake ..

Do not forget that the dielectric strenght between contacts is due of course to contact separation, but also to the speed of dielectric recovery of the gazeouos medium that is between the contacts just after the zero of current. Indeed, it may seem strange, but arc quenching at 50Hz is a race that is won or lost in fractions of microseconds ....

Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#7
In reply to #6

Re: High Voltage Circuit Breaker Recovery Voltage

10/18/2013 3:59 PM

obouill:
"arc quenching at 50Hz is a race that is won or lost in fractions of microseconds".
50Hz is 20ms period so what is happening in microseconds here?

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply