Bm Value in Transformer Design

10/17/2013 4:06 AM

how to choose flux density value while transformer designing.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Bm value in transformer design

10/17/2013 4:09 AM

Well, these things should be in the organisation's design procedures manual, so that is the best place to look.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#2

Re: BH value in transformer design

10/17/2013 8:00 AM

At the upper limit of rated voltage core should remain well below magnetic saturation.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Bm Value in Transformer Design

10/17/2013 8:58 AM

sreerampkj

Have you ever considered doing your own homework?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Bm Value in Transformer Design

10/17/2013 7:33 PM

If you're going to copy something at least do it in the right order. First you figure out how much power you want transfer through the transformer, then you figure out the size of the conductors for the windings based upon the voltages; when you know the impedance characteristics, then you determine the reluctance of the core to achieve this, THEN you size the core. Otherwise it's like building a vehicle by choosing the tire size first without knowing whether it's going to be a Hummer or a Smart Car...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Bm Value in Transformer Design

10/18/2013 11:16 AM

First, understand what it is. Flux - Wikipedia, the free encyclopedia

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#6

Re: Bm Value in Transformer Design

10/20/2013 1:27 AM

Flux density is selected by the following:
Customer's specification for maximum core loss.
Core and or transformer temperature rise must not be excessive.
Transformer maximum inrush current must not be excessive.
Transformer maximum audible noise must meet customer's specification and not be excessive
For some transformers near electronic components, flux leakage may be a problem
For transformers using silicon steel, a good flux density to start a design is 15 kilogauss at 60 hertz, 4 kilogauss at 400 hertz.

Register to Reply
2
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#7

Re: Bm Value in Transformer Design

10/20/2013 6:43 AM

Sree Ram,

for all commercially available core plates for transformers, in data sheets we get value of ...Watt loss per kg at a give flux density and corresponding magnetising curve.

So either simply you can select that value of flux density of data sheet, or in case you would like to economise on cost of production, refer to the magnetising curve and select the value of density 10% more than start of saturation (where the straight line of flux density vs magnetising current curve starts becoming non-linear).

If we design a transformer at flux density beyond this point will result in increased core loss, distortion in sine wave and harmonics in magnetising current.

Pl ignore comments of RAMConsult Probably he has not designed a transformer. Neither I had for long but still remember how we designed and build in 3rd year engineering and later 42years back when I made first attempt for self employment. The design of transformer begins with

Selecting flux density

Then value of flux based on voltage

Then widow area based on number of turns and current loading, voltages etc. Now a days software is available, but in our time, Design Engineer used to work forward and backward, modifying window area, depending upon disc type coils or cylindrical coils or number of cooling oil ducts and minimum clearance required between coils of different voltages. And design was finally frozen when we achieve the required efficiency and percent impedance (voltage regulation).

Regulation could be achieved by changing disc to cylindrical coils or vice versa. Efficiency could be achieved by selecting lower loss steel or reducing current density or both.

I remember even in 1974-5 firms like Crompton Greaves in Bombay had their own developed software for designing of transformers. (I used to represent as a client). What I want to emphasise that designing transformer is the simplest or easiest of all electrical machines.

Register to Reply Good Answer (Score 2)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#8
In reply to #7

Re: Bm Value in Transformer Design

10/21/2013 3:39 PM

You said it right .Only I like to add that distribution transformers are designed with lower flux densities and cosidered value of 1.1 to 1.35 wbs./ sq mt depending up on the core meterial .

Register to Reply
Member

Join Date: Sep 2013
Posts: 8
#9
In reply to #8

Re: Bm Value in Transformer Design

10/22/2013 2:13 AM

Thanks for your valuable answer.

I had one more doubt please clarify this. In vendor catalogue they mentioned

For CRNGO steel -(35H210) = 0.9W/kg@ 1.0T,50hz / 2.1W/kg @1.5T,50Hz

then how I can choose value between 1.1 to 1.35T can you clear this.

Is this standard practice.

My friend was a design engineer he also choosing value between 1.1 to 1.3T, I prepared the same design in excel sheet I had doubt in that design excel sheet can you guide me if I submit that to you.

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#10
In reply to #9

Re: Bm Value in Transformer Design

10/22/2013 5:14 AM

For Transformer core the type of steel used is CRGO (Coled Rolled Grain Orientated) AND Not CRNGO (Coled Rolled Grain Non-Orientated).

As suggested earlier please get the magnetization curve of 35H210 CRGO from the vendor (I could not find on net) and check point from where the curve tends to be Non-linear. You can maximum increase the designed flux density by 15% above value at this point.

We can not exchange e mail address on this site hence you can not send us the excel file.

Register to Reply
Member

Join Date: Sep 2013
Posts: 8
#11
In reply to #10

Re: Bm Value in Transformer Design

10/22/2013 8:13 AM

If you give me your mail id, so that i can mail my excel sheet to you for that mail id.,

So kindly help me to correct my design excel sheet.

and also can you tell me how to choose the conductor area. Wether this depends upon current density or flux density. if it is depends upon current density means what value i should choose for current density (i.e between J=1 to 3A/mm^2)

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#12
In reply to #11

Re: Bm Value in Transformer Design

10/22/2013 8:44 AM

Pl advise following:

1. Rating

2. Primary Voltage

3. Secondary Voltage

4. Any preference of vector group.

One of my friend has rewinding shop and carries out rewinding of Large size transformers, 3 phase HT motors and generators. I shall get you data of transformer close to your rating and parameters. That shall give you fare idea of current loading. The Selection of cross section area of Cu, its insulation and clearance between coils is a function of above 4 parameters. Are you a freshers and designing transformer as part of your curriculum (major project)? It is my endeavour to assist Young budding engineers to guide them in the right direction to best of my ability. I am an old man of 65. With Grace of God I have clear concepts in all fields of engineering and from these basics develop the system and won't mind also assisting you.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#13
In reply to #9

Re: Bm Value in Transformer Design

10/22/2013 8:54 AM

With flux densities higher than 1.35 wb./sq m the 5th or 7th harmonics become pronounced . For oil cooled transformers 150 to 500 kVA output 1.38 wb /sq m is recommended.For transformers above 500 kVA 1.4 wb./sq m is maximum permissible.

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#14
In reply to #13

Re: Bm Value in Transformer Design

10/22/2013 9:26 AM

Mr. Abraham,

Sree Ram is coming back on forum with information regarding kVA rating, voltage levels and application of the transformer.

In case you have the date available for kVA rating, voltage levels and application, then please provide him following information:

1. Flux loading for CRGO steel he intends to use.

2. Current loading of primary (considering cylindrical coil)

3. Current loading of secondary windings (for cylindrical as well as disc type coils)

4. Desirable clearance between primary and secondary for the voltage rating.

5. Desirable clearance between cylinders of windings for circulation of cooling oil.

6. Desirable clearance between adjacent discs.

7. Preferable length to dia ratio of coils (Limb) to achieve hotspot temperature within 10°C of average temperature.

8. Details of tapering of insulation of HT coil of line side conductor to absorb surge in case the application is for outdoor transformers of Receiving Station.

To me it appears that Sree Ram is doing h.is Major Project of Third/final year Engineering and needs support of members from CR4 Forum in Design and Manufacturing of transformers

Thanks in anticipation

Register to Reply
Member

Join Date: Sep 2013
Posts: 8
#15
In reply to #14

Re: Bm Value in Transformer Design

10/22/2013 11:11 PM

Dear Abraham & others,

Thanks for giving me those information.As powersolutionFBD said i am a beginer in transformer design.So intially i want to develop in single phase EI type transformer.So guide me for that later you guide me to 150KVA high rated transformer.

Customer Specification for transformer

Rating,pri vt,Sec Vt & eff

From these data i will calculate Pri& sec Ct

but my problem was with calculating core area(i.e stack & tongue width),which EI type to choose,lamination grade,& turns

can u tell listed below formulas are correct for those calculation

1) core area = 1.15*sqrt(rating) (from this core area how can i seperate core width & stack)

2) Pri Turns=(1/(4.44*f*core area*Bm))*pri vt

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#16
In reply to #15

Re: Bm Value in Transformer Design

10/23/2013 9:53 AM

Please read the following link which gives some basic concept about transformer design

http://ecee.colorado.edu/copec/book/slides/Ch15slides.pdf

http://www.gobookee.org/transformer-design-calculations/

Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Carl Pugh (1); lyn (1); powersolutionsFBD (4); PWSlack (1); rakesh_semwal (1); RAMConsult (1); sreerampkj (3); TonyS (1); V.I.Abraham (3)

Previous in Forum: Temp Rise of Transformer   Next in Forum: Current

Advertisement