Anonymous Poster

Transformer Help

06/06/2007 9:20 AM

I have to test a couple of tranformers at various voltages and frequencies with a particular amperage setting. Can I connect a rheostat across the output windings both full and switchable to half and use it to vary the current? i.e. input of 120VAC 60Hz/output 20VAC - rheostat set at 10ohms to get 2 amps.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#1

Re: transformer help

06/06/2007 10:40 AM

That may work at 120 V AC ip, however, you said that you had to do various frequencies. A rheostat is a variable coil. Its properties will change with frequency. At DC (0hz) it is a short. If you stay with this option I would not rely on the settings of the rheostat for your amperage. The resistance of the rheostat will change with frequency. You should put an ammeter in series or use another measurement technique for your current.

Best setup is a resistor that limits your currrent for the highest current setting plus a Switch to switch in variable resistors for changing the settings. These variable resistors will be used to calibrate each setting. As well use accurate test equipment to measure both the input and output. An oscilloscope is important to ensure clean signals and accurate measurements.

__________________
Perfection is a subjective and abstract concept.
Reply
Anonymous Poster
#2
In reply to #1

Re: transformer help

06/06/2007 12:35 PM

I have to test 100VAC 50/60Hz, 120VAC 50/60HZ, 200VAC 50/60Hz, 208VAC 50/60HZ, 220VAC 50/60Hz, 240VAC 50/60Hz, 250VAC 50/60Hz. Some will be fully loaded at 2.1A and others at 1.6A. As you can see, the frequency won't vary too much. I currently have it set up with an ammeter in series on one leg after the rheostat. Wouldn't the other resistor just be redundant?

Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#3
In reply to #2

Re: transformer help

06/07/2007 9:32 AM

The resistor is there for protection to limit the maximum current. If you dial the rheostat too far one way you could drive the current beyond the limit of the transformer coil and damage it. Without knowing the limit of the transformer, I would set the resistor at 20% over your highest current potential. Doing the math:

250VAC RMS X 1.414 = 353.5V Peak

2.1A X 120% = 2.5A

353.5V / 2.5 A ~= 140 Ohms

__________________
Perfection is a subjective and abstract concept.
Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#4
In reply to #1

Re: transformer help

06/07/2007 10:15 PM

<A rheostat is a variable coil. Its properties will change with frequency. At DC (0hz) it is a short>

Sorry Mate ! We learnt always that rheostat is a Resistor wound on an Insulated tube ready to slide and vary the tap.

Hence at DC it is 100 OHMs(say). At 50Hz it may be Impedance= 100.05 Ohm. At 60 Hz may be 100.06Ω!

You go ahead-OK

Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#6
In reply to #4

Re: transformer help

06/08/2007 11:38 AM

I stand corrected.

I did not know the frequency range or accuracy required. (wire wound = coil)

If The minimum resistance (rheostat adjusted all the way one way) is approximately 140 ohms it would be safe, however, if it is 0 ohms; a current limiting resistor would be prudent.

__________________
Perfection is a subjective and abstract concept.
Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#7
In reply to #6

Re: transformer help

06/08/2007 11:54 AM

He better be prudent--

Always begin midway(slider to rear terminal shorting) -go a little left-watch Ammeter-correct the direction-- >>> till test current is there.

Don't rush-spend 2 minutes in 1 test!

Better Late than a burnt TRX winding or a smoked Rheostat!

Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#8
In reply to #7

Re: transformer help

06/08/2007 12:05 PM

Unless........ you want to have a little fun

__________________
Perfection is a subjective and abstract concept.
Reply
Power-User
United States - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: May 2006
Location: Pittsburgh PA
Posts: 121
#5

Re: Transformer Help

06/08/2007 8:20 AM

What are you trying to test? Putting a resistor at the output is only loading the XFMR.

There are several standard tests for XFMRs

Resistance Measuremnets, Ratio Test, Polarity and Phase relation(3 Phase), Impedance and load loss, Excitation Loss and Excitation Current and Dielectric tests-Low Frequency (IMPULSE, AKA the BOOM BOOM Test).

Depends on what you want to do.

__________________
“There's a sucker born every minute, and I happen to be one of them”
Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#9

Re: Transformer Help

06/20/2007 6:07 AM

In stead of using a rheostat and always varying & monitoring all at once may have risk of erroneous accident or atleast burning your test gadget or transformer under test: 1. You should make Fool-Proof Simple Test Loads for each Test & mark properly. 2. It will be safe for you & your assisstants /co-workers and will save your supervision. 3. It will look more professional & will earn dignity of your job to your Clients/ managers. 4. It will be your skill to expand your job & knowledge. Wish you best of luck

Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#10

Re: Transformer Help

06/27/2007 6:46 PM

In stead of using a rheostat and always varying & monitoring all at once may have risk of erroneous accident or atleast burning your test gadget or transformer under test:

1. You should make Fool-Proof Simple Test Loads for each Test & mark properly.

2. It will be safe for you & your assisstants /co-workers and will save your supervision.

3. It will look more professional & will earn dignity of your job to your Clients/ managers.

4. It will be your skill to expand your job & knowledge.

Wish you best of luck

Reply