Load Limit For 3 Inch Concrete Floor

10/23/2013 12:12 PM

I have a tenant that has asked about the load limit of the floors in our building. We have a multi-story office building with structural steel joists spaced 2 ft apart with 3 inch concrete floors re-enforced with 4 inch wire mesh on top of corrugated decking. I called the original engineer but he is pushing 100 years old and was not much help. He said 40 lbs per square foot, but, if that were the case, at 270 lbs I would go right through the floor if I stood on one foot. Our tenant wants to put in 5 drawer lateral file cabinets some 36 x 18 and some 42 x 19 filled with paper documents. I am thinking it should not be a problem, but since I am not and engineer and he specifically asked about load limit I though I should check in here before answering him.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Load limit for 3 inch concrete floor

10/23/2013 12:26 PM

A 4 drawer file cabinet weighs about 250-275 empty. A ream of paper weighs from 5-6 pounds. You can do the math.

So, the weight adds up very quickly.

The only smart way to do this is to commission a registered engineer to do the analysis.

That way your insurance company will be happy with you, and may even be able to raise your rates on the basis of the added loads you are imposing of the old structure.

They are in business to extract as much money as they can, legally, from you. Protecting you is just incidental.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2
In reply to #1

Re: Load limit for 3 inch concrete floor

10/23/2013 1:03 PM

Those must be some well built file cabinets you have there! I have some good sized 5 drawer units I got from the local air base that are way over built and I would say they don't weigh half that.

As far as the OP's engineers advice I think he is way off as well. 40# per sq foot for a 3 inch thick reinforced concrete slab with corrugated steel underlayment on 24" spaced structural members seems way low. To be honest my books say the 3" thick slab weighs around 35# per sq foot alone.

To be honest my shop roof is rated for over 3x that per sq foot and thats nothing but ribbed sheet steel on 2" x 4" cross members set on 30" spacing all held up by 2" x 6" trusses set on 48" centers over a 32' span and I can walk all over that with my 250#'s without kinking the sheets let alone falling falling through.

Register to Reply
Participant

Join Date: Oct 2013
Posts: 4
#3
In reply to #2

Re: Load limit for 3 inch concrete floor

10/23/2013 1:15 PM

The guy actually said 40# and then said maybe it was 140#, but he was referring to the live load, which excludes the dead load weight of the structure itself. 140 would actually be just about right as I figure the 42" 5 drawer stuffed full of paper would come in at 136/Sq Ft even in a fine heavy cabinet as described previously.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #2

Re: Load limit for 3 inch concrete floor

10/23/2013 1:44 PM
  • View larger
  • Two drawer
  • 28-3/8"H x 36"W x 19-1/4"D
  • Charcoal
  • Letter or legal size
  • This product is made from 30% post consumer materials
  • Each drawer provides 2.96 cubic feet of storage
  • Weight: 132 lbs
Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#12
In reply to #1

Re: Load limit for 3 inch concrete floor

10/23/2013 10:55 PM

you have got to be kidding.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply Off Topic (Score 8)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13
In reply to #12

Re: Load limit for 3 inch concrete floor

10/24/2013 12:28 AM

Do you ever add anything constructive?

Register to Reply
Guru

Join Date: Nov 2010
Location: Virginia, Georgia, Idaho
Posts: 1079
Good Answers: 30
#15
In reply to #13

Re: Load limit for 3 inch concrete floor

10/24/2013 6:46 AM

yes, infrequently. Precisely the point. Try it sometime.

We all know that if you have a question, call an engineer, if you bought something, call the manufacturer. For God's sake, don't try to learn about and understand the problem by reading, it can only lead to errors in judgement.

__________________
PFR Pressure busts pipes. Maybe you need better pipes.
Register to Reply Off Topic (Score 6)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#21
In reply to #15

Re: Load limit for 3 inch concrete floor

10/24/2013 9:56 AM

Try to say something intelligent, or try not to speak!

Surprise us all!

Register to Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4

Re: Load limit for 3 inch concrete floor

10/23/2013 1:25 PM

His 40 lbs a square foot sounds more like the floor load. I don't think you would have a problem unless he is going to fill the room with these file cabinets. You have to look more at the structural steel holding the slab up and what it can handle.

The 36 X 18 would have to weigh filled more then 180 lbs to exceed the given load limit.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: Load Limit For 3 Inch Concrete Floor

10/23/2013 1:43 PM

If he's talking about 140 psf live load, that should be ok if we are only talking a few of these files.....

http://www.eng-tips.com/viewthread.cfm?qid=17038

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7

Re: Load Limit For 3 Inch Concrete Floor

10/23/2013 2:02 PM

square foot or inch??

Register to Reply
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#8

Re: Load Limit For 3 Inch Concrete Floor

10/23/2013 2:20 PM

Whoa back. 40psf is an average for the floor and in some domains would be acceptable. This average includes the equipment and the unloaded spaces between. The information you supply is not sufficient, the deck could be composite or non-composite and several different weights, the wire size and specification is unknown as is the strength of the concrete.

More normal would be 50# plus 15# for partitions plus an allowance for MEP. If designated for library use, it should have been designed for the actual usage.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Load Limit For 3 Inch Concrete Floor

10/23/2013 3:54 PM

No-one here can see the installation.

No-one here is liable in the event of a structural failure due to inappropriate advice being followed.

So the best thing to do hire a local Structural Engineering Consultant to investigate and prepare a report. Yellow Pages?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
2
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#10

Re: Load Limit For 3 Inch Concrete Floor

10/23/2013 9:44 PM

I'm certainly no expert here. Could one not check local building codes at time of construction? Is there a city/municipal building inspector?

Here's a perfect case of not enough information from the OP. Is this building in San Francisco or, perhaps, Bangladesh?

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply Good Answer (Score 2)
Participant

Join Date: Oct 2013
Posts: 4
#22
In reply to #10

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 10:31 AM

Good point but no one ever answers at the city inspector's office here in Austin TX

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#11

Re: Load Limit For 3 Inch Concrete Floor

10/23/2013 10:02 PM

Dear Steven,

All you write makes no sense.

Give us the kind of joists - and span and we get somewhere. Not the concrete but the joists are determinant.

If you do not know, measure them and make a sketch for us.

__________________
Plenty of room here
Register to Reply Score 1 for Good Answer
Participant

Join Date: Oct 2013
Posts: 4
#23
In reply to #11

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 11:04 AM

36 ft span, 20 inches top to bottom, 3-58 across the bottom and 9/16 thick cros braces

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#24
In reply to #23

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 11:27 AM

nice shot but it really isn't the most critical one you could have taken, those trusses are transferring the floor load to a column or a wall, how they are attached to them is where the rubber meets the road! but we love pics here, good job. have the truss rating by chance? all kidding aside if you have your plans especially the "as builts" you should be able to read the notes and specs to find out what you need to know. you really want info on "dead, as well as live loads" good luck but I doubt you'll be shocked to find out you have several tons of play left

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#25
In reply to #23

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 11:43 AM

Check google for

load steel joists

span steel joists

The Newmill catalog that shows has it all. Just check the channels used, especially the bottom one, so that it is fat enough, compared with the catalog ones.

The load tabels:

Deduct the weight of the joist

Deduct the weight of the sheet

Deduct the weight of the concrete

Deduct the weight of the mesh

In your case the load per square foot is less important, more the total weight on the joists. Check further and come back if you need more help.

__________________
Plenty of room here
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#28
In reply to #23

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 10:17 PM

You will certainly find a joist that is similar to yours qua dimensions. In case of doubt use a size smaller before you check the span load tables and a size bigger for the joists own weight table. Determine how big your floor is in sq. feet and count the joists and girders. One detail: I asked to check that the lower channel is fat enough.

Modern joists have L channels below. Yours seems to be a Omega or something. The section of this in particular is under most stress and the section needs to be sufficient to make a comparison with 2 L channels' section.

When you go to the load section, you play pretty safe taking the dynamic values. (These are significantly lower than the static load) I always use them, calculating flat roofs where I live (because of the hurricanes)

As Fredski says, the joists' connection with walls (or girders and pillars - but I guess you'll have none since 36 feet is a short span) need to be checked too. Cracks close to the seats in the walls are a bad sign.

Other than that you might have plenty of extra load capacity. (contradictory to what Fredski says)

But again, check the tables first and once you have the results, come back and then, with the gathered knowledge let an "official" or registered structural engineer state it.

This way you'll sleep tight.

__________________
Plenty of room here
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 3:08 AM

Better still, get that hired Structural Engineering Consultant [#9↑] to measure them instead.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#16

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 6:47 AM

I've never seen or heard of a building being damaged by file cabinets. Has anyone? Think

__________________
High Tolerance is Beautiful
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #16

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 7:42 AM

Yep. These people have:

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#26
In reply to #18

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 2:12 PM

an assemblage of matter a building constitutes does not.

__________________
High Tolerance is Beautiful
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#20
In reply to #16

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 7:47 AM

I have not but the point is still the same, assuming this place was designed and constructed correctly it will certainly have a square inch or foot rating for loading. regardless of how much steel and concrete it contains it will have a design limit that shouldn't be exceeded. by the way the concrete aspect of the floor is more about sound attenuation and vibration control.

I echo the sentiment about consulting a professional because no one here has access to this building or any of the plans used in its construction, there is no "rule of thumb" that applies here. weight is weight regardless if that weight is paper, lead or feathers. a file cabinet is no different.

Register to Reply Score 1 for Good Answer
Power-User
Fans of Old Computers - PDP 11 - New Member

Join Date: Mar 2007
Location: In a mushroom field somewhere in Canada. Kept in the dark and fed sh--, well you know.
Posts: 312
#17

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 7:42 AM

To elaborate along the lines of Bricktop's reasoning, you should be able to go to the town/city hall and pull the submitted dwgs for the building permit and the load limits will be listed on the concrete structural dwg which should include the structural steel beams in the calculation. The builders would also have to submit engineering calculations to verify these dwgs which should be available from the town/city hall.

UFG

__________________
Dirt is for vegetables. Pavement is for racing.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 7:45 AM

...and if the drawings are unavailable, get that Consultant [#9↑] to produce them in the Structural Report. Remember that what was "as built" when the building was constructed isn't necessarily the case now.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
United States - Member - New Member Safety - Hazmat - New Member

Join Date: Apr 2012
Location: in the desert near ground zero
Posts: 207
Good Answers: 7
#27

Re: Load Limit For 3 Inch Concrete Floor

10/24/2013 9:25 PM

I would contact the concrete supplier as they are the ones that have to mix the concrete to specifications. Your question as to the load should be easily answered by the supplier.

__________________
Dont squat with your spurs on, and always drink upstream from the herd.
Register to Reply
Register to Reply 28 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bricktop (1); dvmdsc (3); Fredski (3); JE in Chicago (2); lyn (4); ozzb (1); passingtongreen (1); PFR (2); PWSlack (4); SolarEagle (1); spaceracer (1); StevenW (3); tcmtech (1); unclefastguy (1)