Diesel Generator Issue

10/28/2013 4:30 PM

Hii everybody.. i have a problem with a dg..we have totally 4 sets of generator onboard. Removed the old pms system and installed new plc and dief ppm controller for all the sets.the problem is with no 2 dg.it is synchronising with the other dg but the value of kw doesnt increases i.e it is max to max shwin 45kw and reactive power increases very slowly.we swapped the controller with no 3 but still issue persist.wiring is confirmed as per the 3 dg which are runnin without prob..plzz help me out..rating is 2nd and 3rd dg are of 1000kw and 1st and 4th is of 750kw.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: urgent plzz need help

10/28/2013 5:24 PM

Of course you have real and reactive power droop settings correct on all machines, as well as ensuring that the CTs and PTs are correctly wired, and don't forget to have only one master and the rest set to slave for all governors and AVRs.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2
In reply to #1

Re: urgent plzz need help

10/28/2013 10:19 PM

You're assuming a hell of a lot, like the OP knows what he's doing.

OP Ask yourself, who do you trust, RAM who I know has good knowledge of generator sets but doesn't know your particular set up or the generator manufacturer?

Have you altered the sets without prior advice? More fool you if you have is all I can say.

RAM full respect to you. You always give good advice.

Sometimes it's an uphill struggle!

At least with moving a load uphill there's usually only gravity and friction to fight. Here there's a myriad of factors to try to account for. Nearly all going the wrong way!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Member

Join Date: Sep 2007
Location: Pune, India
Posts: 7
#3

Re: Diesel Generator Issue

10/29/2013 12:53 AM

Good answer by RAM. If you follow guide lines, you should be out of problem.

Few things to add. Check controller fitted on Genset. Does it have capability to have good communication with PLC.

__________________
-Pratap Chavan
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Diesel Generator Issue

10/29/2013 2:04 AM

Who designed and supervised the retrofit? They should be able to sort this out... per RAM's suggestions for starters...

If you are the one wearing the can and need some help then calm down and explain your setup and observed problems more clearly. I can't model what you described in my head other than you have a load sharing issue.

Start with a sketch perhaps?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#5

Re: Diesel Generator Issue

10/29/2013 10:47 AM

If you have swapped controllers, verified wiring, and CT/PT polarity is correct, the only remaining root cause would logically be a master programming fault or PLC I/O card fault.

If possible I would exchange the #2 machine program position in the system with the #3 machine program position and see if the issue follows the program machine postion assignment.

If the issue follows the assignment:

I would exchange the associated PLC I/O card and see if there is a change then react accordingly by replacing the card.

If exchanging the I/O card postion does not affect the issue location, I would go online with the program and look for a math register error such as an "overflow" or "wrapping" of real time DATA values in the program that is specific to the system excitation control. This error is common due to programmers failing to set the upper and lower DATA value limits.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PSC (1); RAMConsult (1); SHOCKHISCAN (1); TonyS (1); Wal (1)