Surge Arrester Rating Selection

10/29/2013 2:26 AM

I'd like to know how to select ratings for SA.

Drawing is not so clear.

So I'm adding some more design factors.

- MV SWGR nominal system voltage : 6.9kV, 3P 3W system.

- Unit Transformer is grounded via NGR : 100A, 30sec

Also LA for the primary of Step-up Transformer.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Surge Arrester rating selection

10/29/2013 4:04 AM

The posted drawing is practically unreadable here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Surge Arrester Rating Selection

10/29/2013 2:32 PM

You need an expert, or at least someone with a cursory knowledge of electricity and local codes, to do this for you.

Lightning arrester - Wikipedia, the free encyclopedia

Register to Reply
Active Contributor

Join Date: Oct 2013
Posts: 12
#3

Re: Surge Arrester Rating Selection

10/29/2013 9:05 PM

http://bayimg.com/IAbAIAAfK

You can see clear image here!!

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: Surge Arrester Rating Selection

10/29/2013 10:50 PM
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #3

Re: Surge Arrester Rating Selection

10/30/2013 7:03 AM

That image is practically unreadable as well.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Oct 2013
Posts: 12
#9
In reply to #6

Re: Surge Arrester Rating Selection

10/31/2013 8:13 AM

By clicking, you can see original size of drawing.(readable)

The reason why I ask for this is as below;

In the project that I am in, Surge arrester(S.A) for 6.9kV(L-L Voltage) Switchgear was selected as 9kV, 5kA.(PDV-65) for feeder and incomer both.

As far as I know, in 4.0kV(Line-Ground Voltage of 6.9kV L-L Voltage) system, S.A rating of 9kV cannot guarantee surge/overvoltage,

because residual voltage(discharge voltage) Ures is 30kV, which is 7.5 times of 4.0kV.

Here is what I sketched for S.A discharge characteristic.

Of course I know, S.A will discharge from 9kV point, but 9kV is fairly high voltage for the equipment, I guess.

Please advise if this S.A rating selection is correct or not?

(overvoltage protection for between 4.0kV and 30kV area)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #9

Re: Surge Arrester Rating Selection

04/11/2024 10:23 AM

Please identify the local standard against which the <...Surge Arrestor...> in question was selected. The rest of it is second-person-check; is there only one person at the facility who can do that? How peculiar.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: Surge Arrester Rating Selection

10/29/2013 11:56 PM

Dear Mr.posity,

Pl. open the following links one by one and read. I am sure, Definitely you will get you what you are looking for.

In addition to this there is a Han-Book published by IEEE, COMPRISING 1024 pages, the link could not be located, in my system. I will try to get it and post here.

These details are available in the ELECTRICAL ENGINEERS PORTAL and get registered there and you will get mails regularly LIKE CR4 which is ENRICHING OUR KNOWLEDGE and our CR4 MEMBERS share their knowledge, expertise and advise.

http://electrical-engineering-portal.com/download-center/books-and-guides/siemens-basics-of-energy/basics-of-surge-protection

http://electrical-engineering-portal.com/surge-protective-categories-defined-by-ansi-ieee-c62-41

http://electrical-engineering-portal.com/download-center/books-and-guides/siemens-basics-of-energy/basics-of-surge-protection

http://www.lightningsafety.com/nlsi_lhm/IEEE_Guide.pdf

http://electrical-engineering-portal.com/surge-protection-of-electronic-equipment

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Surge Arrester Rating Selection

10/30/2013 12:13 PM

The LA Rated voltage is: Highest System Voltage x Ground Fault Factor

The ground fault factor depends upon the type of system grounding and on the ratio R0/X1 & X0/X1.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8
In reply to #7

Re: Surge Arrester Rating Selection

10/30/2013 11:49 PM

Thank you Mr.electricalexpert65 for your response. You have mentioned " the ratio R0/X1 & X0/X1.

I request you to Pl.explain the ratio R0/X1 & X0/X1.the ratio R0/X1 & X0/X1.

DHAYANADHAN.S

Register to Reply
Active Contributor

Join Date: Oct 2013
Posts: 12
#10
In reply to #7

Re: Surge Arrester Rating Selection

10/31/2013 10:10 PM

Thank you for your idea sharing.

I think as below;

- Highest System Voltage : peak voltage (√2 x Us /√3 = 5.63kV)

- Ground Fault Factor : According to IEC 60099-5, 1.73 for Impedance Grounding system.

=> LA rated voltage = 5.63kv X 1.73 = 9.75kV ??

Am I correct?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#11
In reply to #10

Re: Surge Arrester Rating Selection

10/31/2013 10:38 PM

LA Rated Voltage is HSV (rms) x GFF

GFF will be 0.8 for effectively grounded systems and 1.732 for ungrounded systems. For impedance grounded systems, GFF will float between these two values of 0.8 & 1.732, depending upon the ratios R0/X1 & Xo/X1 as mentioned by me earlier.

Now, assuming solid earthing in a 11kV system; the HSV for 11kV is 12kV; GFF is 0.8; thus, LA rated voltage is: 12 x 0.8 = 9.6kV; the nearest standard LA one could get in the market is 9kV. Thus, it is 9kV.

But, the case under study is a Low Resistance grounded 6.9kV System. Here, the LA has to be selected duly considering the R0/X1 & X0/X1 ratios only.

Appendix B of IEC 60071-2 throws more light on this. Suggest to go thro the same.

I think, with this I have answered Mr. Dhayanandan (posting 8) too.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12
In reply to #11

Re: Surge Arrester Rating Selection

11/02/2013 10:29 AM

THANK YOU Mr.Electrical Expert for yor reply.

DHAYANANDHAN.S

Register to Reply
Active Contributor

Join Date: Oct 2013
Posts: 12
#13
In reply to #11

Re: Surge Arrester Rating Selection

11/04/2013 2:15 AM

Thank you very much for your further explaination, electricalexpert65

May I ask one more question?

In IEC 60099-5, Figure 23b, it is saying that " Three-wire impedance earthed systems. Earth Fault Factor 1,73"

So, I thought Maximum voltage between phase and earth would be 1.73 x Us / √3 = 6.89kV.

Once again, I really appreciate your comment.