The Machine: Vibrating Screen having two unbalanced motor, one motor rotate CW another CCW
Motor Details: Make-INVICTA, Model-BLZ/75-150/6, RPM-990, KW=10, V=415, A=17.8, Phase=3, Hz=50, connection-Star, rating-continuous, Class-F, T=130 deg C
Issue: out of two one particular motor burnt out three times since commissioned last July. other motor having no problem at all. We have another identical Vibrating Screen in another plant which is running without any trouble.
Operating Data as recorded at Site: Current reading: in the range of 8 to 10 amps, Temperature recorded 72 deg C, ambient 30 deg C.
Circuit details: Direct On Line connection having common fuse of rating 100A (3NA7830-SIEMENS), Individual Contactor 40A (3RT10 35-1AL20-SIEMENS) and Individual Over Load Relay 14-20A (3RU11-36-4BB0, SIEMENS). Over Load Relay is set at 80% i.e. 14A
Report: While Overload Relay is tripped, electrician went to the equipment for investigation and found motor is already burnt. He came back to switchboard and checked fuse and power contactor is intact.
Problem: As with same arrangement other equipment is running trouble free, all the running data also normal so why particular one motor is burning frequently we could not able to sorted out? Experts, please examine the root cause and please help us with what could be the preventive measures ?
If any other information required please let us know.